[TRNSYS-users] shading from balcony
David BRADLEY
d.bradley at tess-inc.com
Thu Jul 5 08:53:23 PDT 2012
Eva,
Either method will work. I would lean towards drawing the building in
Trnsys3D and drawing the balconies as shading surfaces. Once you get to
TRNBuild, make sure to tell it to generate the shading mask. Once you
do, the building form and the location of the balconies will be taken
into account as far as shading the windows goes.
For Type34, you would need one instance of Type34 for each shaded
surface that you want to consider. The surface can be either a wall or a
window but you must define a new orientation in TRNBuild for each
surface that is going to receive a different amount of solar radiation.
I think Type67 is not appropriate in this case; it was designed to
deal with objects that shade the building from nearby (like another
building across the street) and is not set up to deal with objects that
shade a surface from above (like a balcony does).
Kind regards,
David
On 7/3/2012 17:10, Eva gklezakou wrote:
> Dear Sirs,
>
> I model a two storey building with balconies in all elevations so the
> first floor is shaded by the balconies of the above floor. How can I
> model the balconies? If I model them in type 56 does the shading from
> taken into account? Do I have to use type 34 (shading from overhangs)?
> If yes do I have to use as many components of type 34 as the number of
> the openings (each component describe only one opening with
> overhangs)? Can I approach this case with type 67 (shading mask)?
> Thank you.
>
> Regards,
> Eva
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120705/6209a8fe/attachment-0001.htm>
More information about the TRNSYS-users
mailing list