[TRNSYS-users] cold bridge
ITF - Adrien JEZEQUEL
a.jezequel at itf.biz
Wed Jul 4 05:25:16 PDT 2012
Dear Karol,
You can't modify geometry in trnbuild if detailed radiation model are
selected, that's why coldbridges can't be modified.
You can integrate coldbridges in wall u-value definition :
* Uvalue = (Uwall*Area + Coldbridge_1 x L_1 + Coldbridge_2 x L_2 + ...
+ Coldbridge_i x L_i)/Area
For windows, you can do the same and include coldbridges in Uw value
(modify c-value)
Best regards
------------------------------------------------------------------------
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz ou aj at itf.biz
/Afin de contribuer au respect de l'environnement, merci de n'imprimer
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/
Le 04/07/2012 11:34, Karol Bandurski a écrit :
> Dear All,
>
> Could somebody explain me how to model cold bridge effect?
>
> Building, which I model, have balcony. So, I go to zone which is directly
> connect with balcony, highlight exterior wall where balcony hangs and what
> data should I put?
>
> There is resistance of connection wall-balcony or whole wall taking into
> account this connection?
> The same question is to other parameters?
>
> After I accept cold bridge windows I cannot set cold bridge dimension
> because it is blocked (gray)... Why?
>
> Thank in advance for your time!!!
>
> Regards,
>
> ------------------------------------------------
> Karol Bandurski MSc.
> Institute of Environmental Engineering
> Poznan University of Technology
> www.ee.put.poznan.pl
> www.put.poznan.pl
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120704/f81d79b3/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_2010.jpg
Type: image/jpeg
Size: 2583 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120704/f81d79b3/attachment-0001.jpg>
More information about the TRNSYS-users
mailing list