Dear Zhe,
In addition to Jean Marais' response, I thought that I would mention
that if you have precalculated loads, you can impose them either on an
air stream or on a water stream using components from the TESS Loads and
Structures Libraries (Type682 and 693). Jean is quite correct that it is
best to have the weather data for the same year for which the loads were
generated since the heat pump performance depends on ambient conditions.
As for the second part of your question. There are two ways of
modeling buildings and systems. The first way is that you calculate the
loads and then impose them on the HVAC equipment. When you do this,
however, you presuppose the zone temperatures. You no longer have any
control over when the heat pump turns on and when it turns off. If there
is a load (whether heating or cooling) it must be imposed on the heat
pump. All of the control algorithms are built in to determining the
space load.
The other way of modeling a building is to allow the building
temperature to float, to define a thermostat model that senses the room
temperature and which is then used to command equipment to turn on and
off to keep the space at its temperature. In this case there is no load.
The conditioned air or water stream from the heat pump is delivered to
the zone by whatever means are appropriate (a VENTILATION type in
Type56, an active layer in Type56, a fan coil model, the heat pump
itself...) and the zone temperature responds accordingly. The thermostat
senses the room temperature change and decides whether to keep the
equipment on or turn it off.
Kind regards,
david
On 7/2/2012 07:00, Zhe Li wrote:
>
> Dear all,
>
> I am having two problems.
>
> I have a measured hourly domestic heat loads for a year, I would like
> to implement it in TRNSYS simulation. Which component is best for this
> application? And how to actually implement it?
>
> Also, I would like to utilise air-water heat pump. However, I want to
> turn the heating mode on only, and completely turn off the cooling
> mode. How could I achieve this?
>
> I would like to set room temperature at 22oC. I would want to turn on
> the heat pump at temperature below 20oC and turn it off when room
> temperature arrives at 24oC. I notice there are a few controllers are
> capable to do this, however, which one is the easiest in controlling
> this function?
>
> Thank you very much in advance.
>
> Zhe Li
>
>
>
> Tá an teachtaireacht seo scanta ó thaobh ábhar agus víreas ag Seirbhís
> Scanta Ríomhphost de chuid Seirbhísí Faisnéise, ITBÁC agus meastar í a
> bheith slán. http://www.dit.ie
> This message has been scanned for content and viruses by the DIT
> Information Services E-Mail Scanning Service, and is believed to be
> clean. http://www.dit.ie
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120702/1251a248/attachment-0001.htm>
More information about the TRNSYS-users
mailing list