[TRNSYS-users] simulating a humidity controlled ventilation
David BRADLEY
d.bradley at tess-inc.com
Wed Jan 4 11:21:18 PST 2012
Dear Younness,
I would not worry about switching to the detailed humidity model in
Type56; the simple one is quite adequate. Make sure that the humidity
multiplier is set to a value between about 5 and 15. This indicates that
the zone has between 5 and 15 times the moisture capacitance of the air
in the zone. If you only consider the moisture capacitance of the air
(by setting the multiplier to 1) then you are discounting the fact that
the furnishings and the wall materials in the zone can absorb (and
desorb) moisture.
I think also that you are modeling the variation in RH correctly, its
just that based on your system, there isn't a very good way to dry out
the space. Look carefully at the RH of the ventilation air that you are
putting into the space. If its RH is high and if there are any latent
gains in your space (from occupants or from cooking, for example) then
the moist air in the residence has no way of drying out. Try changing
the conditions of the air that you are putting into the space by means
of a VENTILATION type; set the RH (arbitrarily) to 30% and make sure
that the RH in the zone drops to something close to that level.
Kind regards,
David
On 12/29/2011 10:38, youness EL FOUIH wrote:
> Dear TRNSYS users,
> I'm trying to simulate a humidity controlled ventilation system for a
> flat. As you know in this system the air flow rate is given as
> function of the relative humidity. the problem that I'm facing now is
> that the relative humidity within the kitchen (which has no external
> walls, only adjacent) does not vary it's almost fix around 98%.
> I cheked the humidity parameter for the considered zone and I changed
> the model from "Simple Humidity Model" to "Moisture capacitance
> Moisture" but i really don't know how we could use this model and does
> every parameter mean.
>
> I would be pleased if anyone who know how can I model the variation of
> the internal relative humidity show me how to do it.
>
> Thanks for your help in advance.
>
> --
> *EL Fouih Younness
> *Ingénieur Process - ENIM - Rabat- Promo 2010
> Master Stratégies Énergétiques - Mines Paristech - Paris
> Tel : +33 6 48 81 01 13 <tel:%2B33%206%2048%2081%2001%2013>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120104/3d19878d/attachment-0001.htm>
More information about the TRNSYS-users
mailing list