[TRNSYS-users] problem with control signal of type 668

David BRADLEY d.bradley at tess-inc.com
Tue Aug 21 12:16:08 PDT 2012


Eva,
  Quite a long time ago, there was a bug in Type668 that caused there to 
be a power output even when the device was off. However, this was fixed 
in 2005. You should contact your distributor and make sure that you have 
a more recent version. Also, Type668 has two control signals; one for 
heating and one for cooling. Make sure that both are switched to OFF.
Best,
  David

On 8/21/2012 10:56, Eva gklezakou wrote:
> Dear Sirs,
>
> I think that something going wrong with the control signal of the type 
> 668 because even though the signal from the controller is 0 and for 
> this reason both COP (output of type 668) of the heat pump and the 
> heat transfer to load (output of type 668) are 0 the heat pump power 
> is not 0.
> Thank you for your help.
>
> Regards,
> Eva
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120821/7a0d8afd/attachment-0001.htm>


More information about the TRNSYS-users mailing list