[TRNSYS-users] Type 927, Number of specified flows
David BRADLEY
d.bradley at tess-inc.com
Tue Apr 10 12:18:47 PDT 2012
Richard,
It is important to clarify that the data file for Type927 required at
least two /values /of source and load flow rates in order for the TRNSYS
kernel routine that reads the data file to interpolate correctly. A
modification has been made to TRNSYS 17.1 that allows users to specify
only one value for any of the "independent variables" if they so choose.
The easiest thing to do in Trnsys17.0.x and earlier is simply to copy
the data for the flow rates that you do have and paste it for another
(arbitrary) flow rate. Essentially this just indicates in the data file
that there is no performance dependence on a changing flow rate.
Probably not a great assumption but at least the simulation would run.
Kind regards,
David
On 4/10/2012 04:12, Richard Thygesen wrote:
>
> Hi.
>
> Is it necessary to specify three load and source flows in the external
> file of type 927? Because it seems like it should be possible to only
> have two but when I try to simulate I get two errors
>
> /"The referenced Unit has a bad parameter value./
>
> /Reported information : Parameter # 11, Reported Problem: There must
> be at least two source flow rates." /
>
> //
>
> /"The referenced Unit has a bad parameter value./
>
> /Reported information : Parameter # 12, Reported Problem: There must
> be at least two load flow rates."/
>
> The problem is that I have specified two load and source flows.
>
> Has anyone encountered this problem?
>
> Best regards
>
> *Richard Thygesen*
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120410/9872e50f/attachment-0005.htm>
More information about the TRNSYS-users
mailing list