Dear Karol,
just a brief answer:
1.) The parameters of Type are defined in the Trnsys Studio at the
Tab parameter
2.) The two NTYPEs are the same if
- the thermal zone has one airnode only and
- longwave radiation mode = STANDARD
NTYPE 24: For being backwards compatible it is always calculated by
DO NS=N1,N2 ! all surfaces of airnode
OUT(IOUT)=OUT(IOUT)+AREA(NS)*TSI(NS)
TOTAREA=TOTAREA+AREA(NS)
ENDDO
OUT(IOUT)=OUT(IOUT)/TOTAREA
NTYPE 120:
a) Longwave radiation mode = STANDARD:
DO NS=N1,N2 !all surface of zone to which airnode belongs
TMSURF=TMSURF+AREA(NS)*TSI(NS)
TOTAREA=TOTAREA+AREA(NS)
ENDDO
OUT(IOUT)=TMSURF/TOTAREA !area weighted mean surface
temperature
b) Longwave radiation mode = DETAILED:
caluclation based Gebhart factors. The Gebhart
method involves the view factor from the comfort point to the surfaces
and the therewith the position in the room
with respect to the surrounding surfaces.
Best,
Marion
_____
Von: Karol Bandurski [mailto:karol.bandurski at put.poznan.pl]
Gesendet: Freitag, 30. März 2012 17:20
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] mean radiant and operative temperature
Dear All,
I have 2 question:
1) In manual vol. 5 (introduction) I have read:
The third parameter gives the WEIGHTING FACTOR between air and mean
surface temperature for the calculation of an operative room
temperature. The inputs and outputs of TYPE 56 depend upon the building
description and options within the TRNBUILD program. TRNBUILD generates
an information file describing the outputs and required inputs of TYPE
56.
Where can I found/ set this factor?
2) What is the exactly difference between:
NTYPE 24
TMSURF
weighted mean surface temperature of airnode
[°C]
and
NTYPE 120
TMRLW
Mean radiant temperature (longwave only)
[!C]
The first is calculate according to surface area, and second is
calculate according to surface area and distance from person?
Kind regards,
------------------------------------------------
Karol Bandurski MSc.
Institute of Environmental Engineering
Poznan University of Technology
www.ee.put.poznan.pl
www.put.poznan.pl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120402/c38a7555/attachment-0005.htm>
More information about the TRNSYS-users
mailing list