[TRNSYS-users] Condensation problem
Jean Marais
jeannieboef at googlemail.com
Tue Apr 24 08:42:55 PDT 2012
The freezing of the air will also be a problem. Ice formation will also
release energy (latent heat of freezing). The latent gains refered to by
the buillding model refers to the part of the total energy that is in water
vapour form. In the industry this is refered to as latent heat gain. It is
not the heat released into the air by the forming water when condensation
occurs, as far as I know. A building this cold with just infiltration must
be similar to my deepfreeze section at home. The latent heat of
condensation and freezing may be small enough to ignor. See this wiki
article http://en.wikipedia.org/wiki/Latent_heat and try out the formula in
it
The latent heat of condensation of water in the temperature range from -40
°C to 40 °C is approximated by the following empirical cubic function:
[image: L_{water}(T)=-0.0000614342 T^3+0.00158927 T^2-2.36418
T+2500.79][7]<http://en.wikipedia.org/wiki/Latent_heat#cite_note-6>[J
/ g]
with a determination
coefficient<http://en.wikipedia.org/wiki/Coefficient_of_determination>of
[image:
R^2=0.999988], where [image: T] is in °C
On 24 April 2012 16:32, Alexis Fabre (3E) <Alexis.Fabre at 3e.eu> wrote:
> Dear all,****
>
> ** **
>
> I'm working on a fish factory project located in Nigeria.****
>
> I need to simulate the building based on the outside temperature (around
> 30°C) and the required temperature inside the factory (the temperature
> level depends on the room but will vary between 13°C and -40°C).****
>
> I set the internal gains (lightings, fish, workers, water cleaning),
> insulation thickness...there is no ventilation and I considered an
> infiltration factor for each room.****
>
> I simulated the building and got the energy needs of the building to
> provide all the cooling demand.****
>
> ** **
>
> I realized that I considered as main output the sensible cooling demand
> for the building.****
>
> Problem: The relative humidity of the outside air (entering the building
> when fish load goes in or out) is high in Nigeria (between 60 and 90%).
> Therefore when fresh air enter the building, the temperature decrease and
> the relative humidity reach 100% really quickly. There is condensation and
> thus heat release (latent heat). This amount of heat is high specially when
> the outside air (around 30°C) has to reach a temperature of -40°C!****
>
> ** **
>
> I decided to analyse the TRNSYS output: QLATG (latent energy gains
> including ventilation, infiltration...). Then I've compared it with the
> sensible heat and I noticed the following:****
>
> Sensible heat =10000 x Latent heat.****
>
> I was expected that the latent heat would have been about the same as the
> sensible heat (calculation done with a mollier diagram).****
>
> I decided to check the relative humidity inside the rooms: the relative
> humidity is almost always at 100%.****
>
> ** **
>
> Question: I'm wondering if TRNSYS considers the heat released during
> condensation. The impact is probably huge on the energy demand of the
> building.****
>
> Does anybody know if TRNSYS can give me the energy which is released when
> the humidity inside the air is condensated? ****
>
> I did not fix any humidity level inside the rooms.****
>
> ** **
>
> Thanks a lot for your help****
>
> ** **
>
> Best regards****
>
> ** **
>
> Alexis Fabre****
>
> ** **
>
> ** **
>
> [image: Description: Description: http://www.3e.eu/img/3E_mail.gif]<http://www.3e.eu/>
> ****
>
> Alexis Fabre ****
>
> Project engineer****
>
> Kalkkaai 6
> Quai à la Chaux
> B-1000 Brussels****
>
> T +32 2 229 15 29
> G +32 489 77 14 96****
>
> F +32 2 219 79 89****
>
> ** **
>
> ** **
>
> [image: Description: cid:image004.jpg at 01CD0EA2.ABE1B880]****
>
> ** **
>
> 3E sa/nv Headquarters (Invoicing Address)****
>
> Vaartstraat 61 Rue du Canal, B-1000 Brussels****
>
> ** **
>
> Visit us at www.3E.eu <http://www.3e.eu/>****
>
> Not facing but shaping the changes****
>
> ** **
>
> ** **
>
> ** **
>
> SAVE PAPER: THINK TWICE BEFORE PRINTING!****
>
> ** **
>
> This email is strictly confidential and intended solely for the use of the
> individual to whom it is addressed. Any views or opinions presented are
> solely those of the author and do not necessarily represent those of 3E. If
> you are not the intended recipient, be advised that you have received this
> email in error and that any use, dissemination, forwarding, printing or
> copying of this email is strictly prohibited.****
>
> ** **
>
> ** **
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120424/6e4bda75/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2111 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120424/6e4bda75/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1077 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120424/6e4bda75/attachment-0001.gif>
More information about the TRNSYS-users
mailing list