Dear Ratnalee,
Thank you for the explanation. I believed so, but it was not clear from
TRNSYS documentation.

The type680 si located in HVAC TESS library under single-effect absorption
chiller hot-water fired.

Best regards,
Emilia Visek

On Wed, Sep 14, 2011 at 8:48 PM, Ratnalee Patil <
Ratnalee at innovativedesign.net> wrote:

>  Emilia,****
>
> ** **
>
> For the absorption chiller models I believe the rated COP to be supplied as
> a parameter is thermal COP (Qcooling output/Qheat input to generator). In
> the COP output from the chiller model however, the electricity consumed by
> the chiller for the operation (for pumps etc.) is taken into consideration
> based on the auxiliary electric power (Qaux) supplied as one of the
> parameters. Thus the output COP = Qcooling output/(Qheat input to
> generator + Qaux). ****
>
> ** **
>
> By the way, where is this Type 680 located? I am aware of Types 676 to 679,
> Type 681, and Type 107 for absorption chillers.****
>
> ** **
>
> Thanks.****
>
> ** **
>
> Regards,****
>
> Ratnalee Patil****
>
> B.Arch., M.A.Sc. Engineering****
>
> Sustainable Design Analyst****
>
> Innovative Design****
>
> 850 West Morgan St.****
>
> Raleigh, NC 27603****
>
> Ph: (919) 832-6303****
>
> Fax: (919) 832-3339****
>
> www.innovativedesign.net****
>
> ** **
>
> *From:* Emilia Visek [mailto:emilia.visek at mail.polimi.it]
> *Sent:* Tuesday, September 13, 2011 12:14 PM
> *To:* trnsys-users at cae.wisc.edu
> *Subject:* [TRNSYS-users] type680 COP_rated****
>
> ** **
>
> Dear all,****
>
> The COPrated from type680, is thermal or electrical COP?****
>
> Thank you,****
>
> EV****
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110914/750f254c/attachment-0005.htm>


More information about the TRNSYS-users mailing list