[TRNSYS-users] PV powered air conditioning
David BRADLEY
d.bradley at tess-inc.com
Wed Sep 28 09:11:02 PDT 2011
Michael,
I think you would need to rewrite the heat pump model so that it takes
the available power as an input and returns the machine's available
capacity as an output. We had to do this with a pump model a few years
ago because we had the same situation; a pump that was directly
connected to a PV.
My impression is that variable speed compressor heat pumps are fairly
new to the market and that you find the performance files from a
manufacturer who makes one and see if you can turn their catalog data
around so that power and entering conditions are the independent (input)
variables and capacity is the dependent (output) variable. Normally,
heat pump performance files have the entering conditions as inputs and
both the power and capacity as outputs.
Kind regards,
David
On 9/28/2011 06:09, e0526036 at student.tuwien.ac.at wrote:
> Dear TRNSYS-users,
>
> I am trying to model a PV powered heat pump for cooling purpose
> (variable speed => no battery required, power from PV is used
> directly). I would like to try Type 94a (PV), 48a (inverter) and 665-8
> (heat pump) but I can't find a "power input" for the heat pump, there
> is only the required power as an output. In case, is there
> alternatives for the 665-8?
>
> Thank you very much for your suggestions!
> Kind regards
>
> Michael Mischkot
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
More information about the TRNSYS-users
mailing list