Ehsan,
There is a way of accomplishing this.
*1. create a new *.bui file for each parametric run that you want to do
each one varying whatever parameter(s) you want.*
*2. replace the line in your input file that assigns an integer logical
unit number to the *.bui file with a series of them, each having a
different value. For example, if the line in the input file is:*
ASSIGN c:\Trnsys17\MyProjects\EhsanBuilding\building.bui 31
then you might replace that line with:
ASSIGN c:\Trnsys17\MyProjects\EhsanBuilding\building_option1.bui 31
ASSIGN c:\Trnsys17\MyProjects\EhsanBuilding\building_option2.bui 32
ASSIGN c:\Trnsys17\MyProjects\EhsanBuilding\building_option3.bui 33
ASSIGN c:\Trnsys17\MyProjects\EhsanBuilding\building_option4.bui 34
ASSIGN c:\Trnsys17\MyProjects\EhsanBuilding\building_option5.bui 35
ASSIGN c:\Trnsys17\MyProjects\EhsanBuilding\building_option6.bui 36
*3. Define the following equation:*
CONSTANTS 1
LU_bui = 31
*4. Change the first parameter of Type56 from:*
31 ! 1 Logical unit for building description file (.bui)
to
LU_bui ! 1 Logical unit for building description file (.bui)
*5. finally, select LU_bui as your variable to change from one
parametric run to the next and enter the values 31 through 36 in the
parametric table.*
As a side note, this is a way of running the same system for a lot of
different weather files in a parametric table too!
Best,
David
On 9/26/2011 07:03, hotline wrote:
> Hi Ehsan,
> with TRNEDIT you can only adapt INPUTS of TRNBUILD, that are defined
> in the *.dck file.
> Regards
>
> Christian
>
> TRANSSOLAR Software Team
>
> hotline at transsolar.com <mailto:hotline at transsolar.com>
>
> www.trnsys.de <http://www.trnsys.de/>
>
> Transsolar KlimaEngineering - Technologien für energieeffizientes
> Bauen und Nutzerkomfort in Gebäuden
>
> Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart /
> Amtsgericht Stuttgart - HRB 23347 / UsSt.-Id: DE152272639
>
> Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
> Dipl.Phys. Stefan Holst, Prof. Volkmar Bleicher
>
>
> ------------------------------------------------------------------------
> *Von:* Ehsan Asadi [mailto:ehsan0asadi at yahoo.com]
> *Gesendet:* Samstag, 24. September 2011 17:21
> *An:* trnsys-users at engr.wisc.edu
> *Betreff:* [TRNSYS-users] Using TRNEdit and *.bui
>
> Hi,
>
> Can we use TRNEdit for parametric run of parameters specified in *.bui
> and not *.dck?
> Regards
> Ehsan
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110926/80bc37d1/attachment-0001.htm>
More information about the TRNSYS-users
mailing list