[TRNSYS-users] WG: Re: Simulation of false ceiling: influence on	inertia
    Joke De Beuckelaer 
    joke.d at vkgroup.be
       
    Wed Oct 19 02:40:42 PDT 2011
    
    
  
Marion,
As an answer to your questions:
Indeed, I will not use the detailed radiation modes. I think it’s not necessary here, because indeed I have an external shading device..
But to resume:
It’s best to model two zones: one part the false ceiling and the other the room. The ceiling exists of two parts: one part with a high conductivity (= air – air contact), and the other part with the resistance of the false ceiling (= the false ceiling itself)?
Thanks a lot for the information!
Greetings,
Joke De Beuckelaer
project engineer mep
VK     HEALTHCARE      |      BUILDINGS      |      INDUSTRY      |      INFRA
Value by design
VK ENGINEERING  Avenue Clemenceaulaan 87, 1070 Bruxelles Brussel, Belgium
t   +32 2 414 07 77   f  +32 2 414 04 98   m  +32 473 97 01 50   e   joke.d at vkgroup.be   w   www.vkgroup.be
From: trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] On Behalf Of Marion Hiller
Sent: woensdag 19 oktober 2011 9:13
To: trnsys-users
Subject: [TRNSYS-users] WG: Re: Simulation of false ceiling: influence on inertia
David and Joke,
the coupling airflows between two airnodes belonging two different zones are defined by adjacent surfaces (walls/windows).
Coupling airflows between two airnodes of the same thermal zone can be defined in the regime. A new button coupling becomes active.
[cid:image001.jpg at 01CC8E53.2E9D9210]
Concerning the false ceiling problem of Joke, do you use the detailed radiation modes?
I assume not because you do have a shading and the distribution isn’t that important anymore, right?
If you use standard radiation mode I suggest that your airnode “false ceiling” doesn’t cover the whole
Ceiling area, but only 70 %. The remaining separating vertical surface between the airnode false ceiling and room
could be defined as a resistance wall with a high conductivity.
Virtual surfaces are defined in Trnsys3D, but they don’t exist in the thermal model. Thus no heat transfer through the virtual surface
can be calculated. Virtual surfaces are defined for creating closed volumes for airnodes such that the volume calculation of the airnode
is performed correctly.
Best,
Marion
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.: DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer, Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
________________________________
Von: David BRADLEY [mailto:d.bradley at tess-inc.com]
Gesendet: Dienstag, 18. Oktober 2011 19:28
An: Joke De Beuckelaer
Cc: TRNSYS-users
Betreff: Re: [TRNSYS-users] Simulation of false ceiling: influence on inertia
Joke,
 This came up yesterday as well (how to make a coupling air flow across a virtual surface) and I unfortunately don't know the answer. I am looking into it and will let you know what I learn.
Best,
 David
On 10/18/2011 11:23, Joke De Beuckelaer wrote:
David,
Thanks for the answer. But the problem is that it isn't a 100% false ceiling but about 70%.
So what do I do with the "air - air contact" between the two zones.
Does Trnsys takes this into account when I model it with a virtual surface in google sketchup or do the airnodes then have to belong to the same thermal zone?
Greetings,
Joke
________________________________
Van: David BRADLEY [d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>]
Verzonden: maandag 17 oktober 2011 18:38
Aan: Joke De Beuckelaer
CC: TRNSYS-users
Onderwerp: Re: [TRNSYS-users] Simulation of false ceiling: influence on inertia
Joke,
 I like to simulate this situation as two thermal zones; the conditioned zone below and the plenum zone above. Because the suspended ceiling basically has no mass to it, I simulate it as a wall made up of a single purely resistive (ie massless) layer.
best,
 David
On 10/14/2011 03:44, Joke De Beuckelaer wrote:
Dear all,
Can anyone help me what’s the best way to simulate a suspended false ceiling?
The goal is to simulate a class room where the comfort is assured by using night ventilation. However for acoustic reasons we need a false ceiling.
I want to know the percentage of suspended false ceiling is possible in order to have still enough inertia from the concrete ceiling.
Is the best way just to define two different types of ceiling (1. A concrete ceiling and 2.a false ceiling (concrete + air layer + false ceiling)) or has anyone another idea?
Is it possible to draw for example some obstructions in Google sketch up and then to define 3 air nodes in trnsys. One air node above the suspended false ceiling; one air node in the middle of the room and one air node representing the opening window?
Will it take into account the less availability of the inertia of the concrete ceiling?
Hoping for an answer,
Joke De Beuckelaer
project engineer mep
VK     HEALTHCARE      |      BUILDINGS      |      INDUSTRY      |      INFRA
Value by design
VK ENGINEERING  Avenue Clemenceaulaan 87, 1070 Bruxelles Brussel, Belgium
t   +32 2 414 07 77   f  +32 2 414 04 98   m  +32 473 97 01 50   e   joke.d at vkgroup.be<mailto:joke.d at vkgroup.be>   w   www.vkgroup.be<http://www.vkgroup.be>
 ALWAYS LOOKING FOR GREAT PEOPLE
****DISCLAIMER****
This communication is confidential and for the sole useof the addressee. If you are not the intended recipient,
please immediately notify the sender by e-mail at the address shown and then delete it from your system
without copying, disclosing or forwarding its contents. Thank you.
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu<mailto:TRNSYS-users at cae.wisc.edu>
https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
 ALWAYS LOOKING FOR GREAT PEOPLE
****DISCLAIMER****
This communication is confidential and for the sole useof the addressee. If you are not the intended recipient,
please immediately notify the sender by e-mail at the address shown and then delete it from your system
without copying, disclosing or forwarding its contents. Thank you.
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
 ALWAYS LOOKING FOR GREAT PEOPLE
****DISCLAIMER****
This communication is confidential and for the sole useof the addressee. If you are not the intended recipient,
please immediately notify the sender by e-mail at the address shown and then delete it from your system
without copying, disclosing or forwarding its contents. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111019/d0f6e09c/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 14276 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111019/d0f6e09c/attachment-0005.jpg>
    
    
More information about the TRNSYS-users
mailing list