[TRNSYS-users] WG: Re: Simulation of false ceiling: influence	on inertia
    Marion Hiller 
    hiller at transsolar.com
       
    Wed Oct 19 00:51:43 PDT 2011
    
    
  
Karol,
 
a virtual surface is NOT a heat transfer surface!! It doesn’t exist in
the thermal model. 
If you open the B17 file you don’t find the surface.
 
Best,
 
Marion
 
 
 
Dipl.-Ing. Marion Hiller 
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude 
Munich - New York - Stuttgart + 49.711.67976.0 
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart 
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher 
 
 
  _____  
Von: Karol Bandurski [mailto:karol.bandurski at put.poznan.pl] 
Gesendet: Mittwoch, 19. Oktober 2011 09:46
An: Marion Hiller; 'trnsys-users'
Betreff: RE: [TRNSYS-users] WG: Re: Simulation of false ceiling:
influence on inertia
 
Marion,
 
Could you explain what kind of heat or mass transfer exist  by Virtual
surface:
 
1.      Radiation?
2.      Convection?
3.      Mass transfer?
4.      Neither? – virtual surface is perfect insulator
 
If 1-3  :  how values of these magnitude are calculated?
 
Regards
------------------------------------------------
Karol Bandurski MSc.
Institute of Environmental Engineering
Poznan University of Technology
www.ee.put.poznan.pl
www.put.poznan.pl
 
 
 
From: Marion Hiller [mailto:hiller at transsolar.com] 
Sent: Wednesday, October 19, 2011 9:00 AM
To: trnsys-users
Subject: [TRNSYS-users] WG: Re: Simulation of false ceiling: influence
on inertia
 
David and Joke, 
 
the coupling airflows between two airnodes belonging two different zones
are defined by adjacent surfaces (walls/windows). 
Coupling airflows between two airnodes of the same thermal zone can be
defined in the regime. A new button coupling becomes active. 
 
 
Concerning the false ceiling problem of Joke, do you use the detailed
radiation modes? 
I assume not because you do have a shading and the distribution isn’t
that important anymore, right? 
 
If you use standard radiation mode I suggest that your airnode “false
ceiling” doesn’t cover the whole 
Ceiling area, but only 70 %. The remaining separating vertical surface
between the airnode false ceiling and room 
could be defined as a resistance wall with a high conductivity. 
 
Virtual surfaces are defined in Trnsys3D, but they don’t exist in the
thermal model. Thus no heat transfer through the virtual surface 
can be calculated. Virtual surfaces are defined for creating closed
volumes for airnodes such that the volume calculation of the airnode 
is performed correctly. 
 
Best, 
 
Marion 
 
Dipl.-Ing. Marion Hiller 
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude 
Munich - New York - Stuttgart + 49.711.67976.0 
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart 
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639 
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher  
  
 
  _____  
                                     
Von: David BRADLEY [mailto:d.bradley at tess-inc.com] 
Gesendet: Dienstag, 18. Oktober 2011 19:28
An: Joke De Beuckelaer
Cc: TRNSYS-users
Betreff: Re: [TRNSYS-users] Simulation of false ceiling: influence on
inertia 
 
Joke,
 This came up yesterday as well (how to make a coupling air flow across
a virtual surface) and I unfortunately don't know the answer. I am
looking into it and will let you know what I learn.
Best,
 David
On 10/18/2011 11:23, Joke De Beuckelaer wrote: 
David, 
  
Thanks for the answer. But the problem is that it isn't a 100% false
ceiling but about 70%. 
So what do I do with the "air - air contact" between the two zones. 
Does Trnsys takes this into account when I model it with a virtual
surface in google sketchup or do the airnodes then have to belong to the
same thermal zone? 
  
Greetings, 
Joke 
  
  _____  
                                     
Van: David BRADLEY [d.bradley at tess-inc.com]
Verzonden: maandag 17 oktober 2011 18:38
Aan: Joke De Beuckelaer
CC: TRNSYS-users
Onderwerp: Re: [TRNSYS-users] Simulation of false ceiling: influence on
inertia 
Joke,
 I like to simulate this situation as two thermal zones; the conditioned
zone below and the plenum zone above. Because the suspended ceiling
basically has no mass to it, I simulate it as a wall made up of a single
purely resistive (ie massless) layer.
best,
 David
On 10/14/2011 03:44, Joke De Beuckelaer wrote: 
Dear all, 
  
Can anyone help me what’s the best way to simulate a suspended false
ceiling? 
  
The goal is to simulate a class room where the comfort is assured by
using night ventilation. However for acoustic reasons we need a false
ceiling. 
I want to know the percentage of suspended false ceiling is possible in
order to have still enough inertia from the concrete ceiling. 
  
Is the best way just to define two different types of ceiling (1. A
concrete ceiling and 2.a false ceiling (concrete + air layer + false
ceiling)) or has anyone another idea? 
  
Is it possible to draw for example some obstructions in Google sketch up
and then to define 3 air nodes in trnsys. One air node above the
suspended false ceiling; one air node in the middle of the room and one
air node representing the opening window? 
Will it take into account the less availability of the inertia of the
concrete ceiling? 
  
  
Hoping for an answer, 
  
  
Joke De Beuckelaer 
project engineer mep 
  
  
VK     HEALTHCARE      |      BUILDINGS      |      INDUSTRY      |     
INFRA 
  
Value by design 
  
VK ENGINEERING  Avenue Clemenceaulaan 87, 1070 Bruxelles Brussel,
Belgium   
t   +32 2 414 07 77   f  +32 2 414 04 98   m  +32 473 97 01 50   e
joke.d at vkgroup.be   w   www.vkgroup.be 
  
  
 ALWAYS LOOKING FOR GREAT PEOPLE      
****DISCLAIMER****
This communication is confidential and for the sole useof the addressee.
If you are not the intended recipient,
please immediately notify the sender by e-mail at the address shown and
then delete it from your system 
without copying, disclosing or forwarding its contents. Thank you. 
  
  
 
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users
 
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
 
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
 
http://www.tess-inc.com
http://www.trnsys.com
  
 ALWAYS LOOKING FOR GREAT PEOPLE      
****DISCLAIMER****
This communication is confidential and for the sole useof the addressee.
If you are not the intended recipient,
please immediately notify the sender by e-mail at the address shown and
then delete it from your system 
without copying, disclosing or forwarding its contents. Thank you. 
  
  
 
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
 
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
 
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111019/280bbdc5/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 14276 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111019/280bbdc5/attachment-0005.jpg>
    
    
More information about the TRNSYS-users
mailing list