[TRNSYS-users] Has someone worked with TYPE-53?
David BRADLEY
d.bradley at tess-inc.com
Mon Oct 3 08:52:35 PDT 2011
Javier,
Although Type53 does not use the standard TRNSYS external data file
format, some of the same rules still apply: the model can interpolate
performance inside the range of data given in the file but it cannot
extrapolate beyond the range given. In the case of Type53m you get an
error if your data file does not cover the range of your inlet
conditions. Take the second data variable for example. The values are
ratios of the temperature difference between the condenser water outlet
and the evaporator water outlet relative to a specified design
temperature difference. If the maximum temperature difference in the
data file is 10C and then during your simulation, the temperature
difference goes as high as 15C, you will get an error. If you aren't
able to find which of your input variables is going out of the range,
please send me the simulation that you are trying to run and I'll see if
I can find it.
Kind regards,
David
On 10/3/2011 03:15, Javier Galvan Villamarin wrote:
>
> Hi Everyone,
> I am having trouble with the TYPE-53 for vapor compression chillers.
> I am getting an error message which says "the chiller is operating
> outside of the range defined by the performance curve fit". However, I
> cannot see what the problem is. I have checked the data and everything
> look well.
> There is no examples with this type included in the provided
> information with the software.
>
> Has someone worked with this TYPE-53?.
> Does have someone an example using this TYPE-53?.
>
> Thanks,
> Javier Galvan
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111003/54c146aa/attachment-0005.htm>
More information about the TRNSYS-users
mailing list