[TRNSYS-users] NType 904 -what's going on with equation
    Marion Hiller 
    hiller at transsolar.com
       
    Thu Nov 24 05:45:31 PST 2011
    
    
  
Karol,
 
in fact, it is accuracy problem that show the different error sum in
excel .
 
In your summary file the largest number is 1.693E+07  . 
The number is equal to 1693.E+04. 
Due to the fact that we do print values with accuracy of 1E+04 
you can’t expect the sum to be more accurate with in excel.
 
Therefore, you can’t recalculate the balance by excel.
 
 
Best, 
 
Marion
 
Dipl.-Ing. Marion Hiller 
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude 
Munich - New York - Stuttgart + 49.711.67976.0 
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart 
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher 
 
 
  _____  
Von: Karol Bandurski [mailto:karol.bandurski at put.poznan.pl] 
Gesendet: Donnerstag, 24. November 2011 09:48
An: Marion Hiller
Betreff: RE: RE: [TRNSYS-users] NType 904 -what's going on with equation
 
Thanks Marion, I am waiting.
 
It seems to me that the reason could be accuracy.
 
Karol
 
From: Marion Hiller [mailto:hiller at transsolar.com] 
Sent: Thursday, November 24, 2011 9:33 AM
To: karol.bandurski
Subject: AW: RE: [TRNSYS-users] NType 904 -what's going on with equation
 
Karol, 
 
I have to check it in more detail. 
I’ll try to get back to you today. 
 
Marion 
 
Dipl.-Ing. Marion Hiller 
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude 
Munich - New York - Stuttgart + 49.711.67976.0 
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart 
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639 
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher  
  
 
  _____  
                                     
Von: Karol Bandurski [mailto:karol.bandurski at put.poznan.pl] 
Gesendet: Dienstag, 22. November 2011 11:06
An: Marion Hiller
Betreff: RE: [TRNSYS-users] NType 904 -what's going on with equation 
 
Marion, 
 
Thank you for tip – there was mistake in file generate in TRNSYS –
SUMMARY.BAL: QTRANS is with ‘-‘ and should be without. 
 
But there is still something wrong: my sums and TRNSYS sums differ. 
 
Take a look pleas (enclose)! 
 
Karol 
 
From: Marion Hiller [mailto:hiller at transsolar.com] 
Sent: Tuesday, November 22, 2011 9:18 AM
To: karol.bandurski; trnsys-users
Subject: AW: [TRNSYS-users] NType 904 -what's going on with equation 
 
Karol, 
 
you use the wrong signs fort he terms in your balance. 
Pease check the SIGNs  + and – given in the equation for the balance
(also see 05-MultizoneBuilding.pdf) 
 
Marion 
 
Dipl.-Ing. Marion Hiller 
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude 
Munich - New York - Stuttgart + 49.711.67976.0 
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart 
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639 
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher  
  
 
  _____  
                                     
                                     
Von: Karol Bandurski [mailto:karol.bandurski at put.poznan.pl] 
Gesendet: Montag, 21. November 2011 13:02
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] NType 904 -what's going on with equation 
 
Hi, 
 
Could somebody explain me how it is possible: 
 
I get file SUMMARY.BAL (enclosed) as a result of NType 904, and there is
such equation: 
BAL_ENERGY= -DQAIRdt  +QHEAT     -QCOOL    +QINF      +QVENT
+QCOUPL    -QTRANS  +QGAININT  +QWGAIN    +QSOLGAIN 
 
But I calculate BAL_ENERGY in excel (enclosed), the same way, for each
zone, and result are completely different!!!??? 
 
How it is possible? 
 
Have I done something wrong? 
 
Regards, 
 
Karol 
------------------------------------------------ 
Karol Bandurski MSc. 
Institute of Environmental Engineering 
Poznan University of Technology 
www.ee.put.poznan.pl 
www.put.poznan.pl 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111124/b7a2a1f2/attachment-0005.htm>
    
    
More information about the TRNSYS-users
mailing list