Hi Rana,
You can:
- define your external shading factor as an input of type 56 (let's say
"ESF1")
- create an equation box in the simulation studio (Assembly > insert new
equation).
- define in the equation box an input (IB_X) linked to the beam radiation
value (weather data reader -> Type 99 or 109)
- define an output as : *ESF1_value = ge(IB_X,972)* (because 270 W/m² = 972
kJ/h.m²)
-> it is equivalent to say "*if IB_X >= 270 W/m² then ESF1_value =
1 else ESF1_value = 0*"
- link this output ("ESF1_value") to the type56 input ("ESF1")
Regards,
Damien.
On Wed, Nov 23, 2011 at 4:08 PM, Rana Mohsen <r.mohsen at live.com> wrote:
>  Hi all,
>
> i am having a building with internal and external shading system. the
> external shading system is on when it the irradiation on window reaches
> 270w/m2 or more, and  if it is less it went off. and i want to put this in
> the simulation by using a control function and connect it to my input,,, so
> which control function could be used is it type 2d or the PID controler
> type 23..
> and if it is in the 2d, how to put this number.
>
> *Best Regards*,
>   * **I*NG*.*| *R*ana Hanafy
>  Master Student
>  Hochschule für TechniK Stuttgart
>  Tübingerstraße 93,
>  70178 Stuttgart, Germany
>   0049-176-59730029
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111123/430586bc/attachment-0005.htm>
    
    
More information about the TRNSYS-users
mailing list