[TRNSYS-users] PID controller in TRNSYS developer (URGENCY, PLEASE)

王洋 wanghongyang1767 at gmail.com
Tue Nov 22 02:51:52 PST 2011


Dear all,

These days I try to all kinds of methods to make PID controller/OF sense.
E.g. I set a Shedule from 9 am as 1(since at 9 am CO2 concentration just
reaches set point 1000 ppm) linked with PID controller. It seems it should
make sense. However, if I set P (Gain Constant) as 12.89648895941, OF will
not control CO2 concentration i.e. CO2 concentration will increase later
on; if I set P as 12.89648895942, OF can control CO2%, however at this time
OF will change into maximal value 1, so  CO2 concentration will decrease
later on, BUT I need CO2% keeps at 1000 ppm, PID controller can't get
it!Furthermore, from the above, we can see PID controller in TRNSYS
INDEED
should use an internal ITERATIVE algorithm! Since I tried millions times P
value until 0.0000000000x, it still can't reach my set point 1000 ppm.
Hence PLEASE give me some advices or experiences about this problem.
 (URGENCY, PLEASE)

Millions thanks in advance!

br

wang

2011/11/22 <trnsys-users-request at cae.wisc.edu>

> Send TRNSYS-users mailing list submissions to
>        trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
>        https://mailman.cae.wisc.edu/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
>        trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
>        trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
>   1. Re: NType 904 -what's going on with equation (Marion Hiller)
>   2. PID controller in TRNSYS developer (URGENCY, PLEASE) (??)
>
>
> ---------- 已转发邮件 ----------
> From: "Marion Hiller" <hiller at transsolar.com>
> To: "karol.bandurski" <karol.bandurski at put.poznan.pl>, trnsys-users <
> trnsys-users at cae.wisc.edu>
> Date: Tue, 22 Nov 2011 09:17:40 +0100
> Subject: Re: [TRNSYS-users] NType 904 -what's going on with equation
> ********
>
> Karol,****
>
> ** **
>
> you use the wrong signs fort he terms in your balance.****
>
> Pease check the SIGNs  + and – given in the equation for the balance (also
> see 05-MultizoneBuilding.pdf)****
>
> ** **
>
> Marion****
>
> ** **
>
> *Dipl.-Ing. Marion Hiller **
> **TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes
> Bauen und Nutzerkomfort in Gebäude **
> Munich - New York - Stuttgart + 49.711.67976.0
>
> **Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
> Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
> DE152272639*****
>
> *Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
> Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher *
>
>  ****
>
> ** **
>  ------------------------------
>
>
> *Von:* Karol Bandurski [mailto:karol.bandurski at put.poznan.pl]
> *Gesendet:* Montag, 21. November 2011 13:02
> *An:* **trnsys-users at cae.wisc.edu**
> *Betreff:* [TRNSYS-users] NType 904 -what's going on with equation****
>
> ** **
>
> Hi,****
>
> ** **
>
> Could somebody explain me how it is possible:****
>
> ** **
>
> I get file SUMMARY.BAL (enclosed) as a result of NType 904, and there is
> such equation:****
>
> BAL_ENERGY= -DQAIRdt  +QHEAT     -QCOOL    +QINF      +QVENT
> +QCOUPL    -QTRANS  +QGAININT  +QWGAIN    +QSOLGAIN****
>
> ** **
>
> But I calculate BAL_ENERGY in excel (enclosed), the same way, for each
> zone, and result are completely different!!!???****
>
> ** **
>
> How it is possible?****
>
> ** **
>
> Have I done something wrong?****
>
> ** **
>
> Regards,****
>
> ** **
>
> Karol****
>
> ------------------------------------------------****
>
> Karol Bandurski MSc.****
>
> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/>****
>
> ****Poznan** **University**** of Technology****
>
> www.ee.put.poznan.pl****
>
> www.put.poznan.pl****
>
> ** **
>
>
> ---------- 已转发邮件 ----------
> From: 王洋 <wanghongyang1767 at gmail.com>
> To: Marcus <jones.0bj3 at gmail.com>,
> marcello.caciolo at aximaseitha-gdfsuez.com, trnsys-users at cae.wisc.edu,
> hotline at transsolar.com
> Date: Tue, 22 Nov 2011 09:46:53 +0100
> Subject: [TRNSYS-users] PID controller in TRNSYS developer (URGENCY,
> PLEASE)
> Dear Marcello and Marcus,
>
> Many thanks for your quick and patient reply!
>
> 1.   For Concentration unit: Indeed I used kg/kg as the CO2 concentration
> since the unit is kg/kg in TRNFlow. In my previous email I said ppm in
> order to make you understand well. Maybe I also need clarify another thing:
> as you know, 1000 ppm is about 0.00164 kg/kg, whether or not for PID
> controller its tolerance is too small? Therefore, PID controller can't
> control well for smaller set point 0.00164 kg/kg?
>
> 2. For Input 11 : I indeed set it as 1.
>
> 3. For  Output 2 should be equal to set-point concentration minus actual
> concentration: Indeed it is right which I observed.
> For output 4 to output 2 multiplied by kp.****: Output 4 is about from
> 10^-6 to 10^-8, maybe since Kp is too small 0.0064 and output 2 ia also too
> small. So I think it is right.
>
> 4. Maybe I need describe this simulation situation in detail:
> From 0 to 8 am: there is no occupant in this office zone,
> From 8 am to 6 pm: there are 2 workers working in this office and begin to
> produce CO2.
>
> In truth, OF activates before 8 am based on PID controller.  So it is
> further *WEIRD*!(I didn't mentioned it previously) Since it is very *
> unreasonable!* So I forced to set OF as 0 before 8 am. PLEASE see the
> ATTACHED figure. Although CO2 concentration can be kept at set point 0.0016
> kg/kg (1000 ppm), however, there is still that problem:
>  when indoor CO2 concentration is less than set point 1000 ppm, PID
> begins to activate OF i.e. windows are open. Based on PID principle, control
> signal should be set to zero. BUT it is not like this. As we know, if CO2
> concentration is not getting to set point 1000 ppm, at this time windows
> are open will result in the ERROR (between the set point and actual indoor
> CO2 concentration) increasing. So I'm puzzled!
>
>
> Now, I only would like a solution for this problem as I said in recent
> emails and the adequate explanations for this OF_CO2 concentration_PID
> control issue in TRNSYS .****
>
>  ****
>
>  ****
>
> Many thanks in advance!****
>
>  ****
>
> br****
>
>  ****
>
> wang****
>
>
> ---------- Forwarded message ----------
> From: 王洋 <wanghongyang1767 at gmail.com>
> Date: 2011/11/19
> Subject: Fwd: [TRNSYS-users] TR: PID controller in TRNSYS developer
> To: Marcus <jones.0bj3 at gmail.com>,
> marcello.caciolo at aximaseitha-gdfsuez.com, trnsys-users at cae.wisc.edu
>
>
>  Dear Marcello and Marcus,
>
> Many thanks for your quick and patient reply!
>
> 1.   For Concentration unit: Indeed I used kg/kg as the CO2 concentration
> since the unit is kg/kg in TRNFlow. In my previous email I said ppm in
> order to make you understand well. Maybe I also need clarify another thing:
> as you know, 1000 ppm is about 0.00164 kg/kg, whether or not for PID
> controller its tolerance is too small? Therefore, PID controller can't
> control well for smaller set point 0.00164 kg/kg?
>
> 2. For Input 11 : I indeed set it as 1.
>
> 3. For  Output 2 should be equal to set-point concentration minus actual
> concentration: Indeed it is right which I observed.
> For output 4 to output 2 multiplied by kp.****: Output 4 is about from
> 10^-6 to 10^-8, maybe since Kp is too small 0.0064 and output 2 ia also too
> small. So I think it is right.
>
> 4. Maybe I need describe this simulation situation in detail:
> From 0 to 8 am: there is no occupant in this office zone,
> From 8 am to 6 pm: there are 2 workers working in this office and begin to
> produce CO2.
>
> In truth, OF activates before 8 am based on PID controller.  So it is
> further *WEIRD*!(I didn't mentioned it previously) Since it is very *
> unreasonable!* So I forced to set OF as 0 before 8 am. PLEASE see the
> ATTACHED figure. Although CO2 concentration can be kept at set point 0.0016
> kg/kg (1000 ppm), however, there is still that problem:
>  when indoor CO2 concentration is less than set point 1000 ppm, PID
> begins to activate OF i.e. windows are open. Based on PID principle, control
> signal should be set to zero. BUT it is not like this. As we know, if CO2
> concentration is not getting to set point 1000 ppm, at this time windows
> are open will result in the ERROR (between the set point and actual indoor
> CO2 concentration) increasing. So I'm puzzled!
>
>
> Now, I only would like a solution for this problem as I said in recent
> emails and the adequate explanations for this OF_CO2 concentration_PID
> control issue in TRNSYS .****
>
>  ****
>
>  ****
>
> Many thanks in advance!****
>
>  ****
>
> br****
>
>  ****
>
> wang****
>
>
>   ---------- Forwarded message ----------
> From: 王洋 <wanghongyang1767 at gmail.com>
> Date: 2011/11/17
> Subject: Re: [TRNSYS-users] TR: PID controller in TRNSYS developer
> To: Marcus <jones.0bj3 at gmail.com>,
> marcello.caciolo at aximaseitha-gdfsuez.com
> Cc: trnsys-users at cae.wisc.edu
>
>
> Dear Marcello and Marcus,
>
> Many thanks for your quick and patient reply!
>
> 1.   For Concentration unit: Indeed I used kg/kg as the CO2 concentration
> since the unit is kg/kg in TRNFlow. In my previous email I said ppm in
> order to make you understand well. Maybe I also need clarify another thing:
> as you know, 1000 ppm is about 0.00164 kg/kg, whether or not for PID
> controller its tolerance is too small? Therefore, PID controller can't
> control well for smaller set point 0.00164 kg/kg?
>
> 2. For Input 11 : I indeed set it as 1.
>
> 3. For  Output 2 should be equal to set-point concentration minus actual
> concentration: Indeed it is right which I observed.
> For output 4 to output 2 multiplied by kp.****: Output 4 is about from
> 10^-6 to 10^-8, maybe since Kp is too small 0.0064 and output 2 ia also too
> small. So I think it is right.
>
> 4. Maybe I need describe this simulation situation in detail:
> From 0 to 8 am: there is no occupant in this office zone,
> From 8 am to 6 pm: there are 2 workers working in this office and begin to
> produce CO2.
>
> In truth, OF activates before 8 am based on PID controller.  So it is
> further *WEIRD*!(I didn't mentioned it previously) Since it is very *
> unreasonable!* So I forced to set OF as 0 before 8 am. PLEASE see the
> ATTACHED figure. Although CO2 concentration can be kept at set point 0.0016
> kg/kg (1000 ppm), however, there is still that problem:
>  when indoor CO2 concentration is less than set point 1000 ppm, PID
> begins to activate OF i.e. windows are open. Based on PID principle, control
> signal should be set to zero. BUT it is not like this. As we know, if CO2
> concentration is not getting to set point 1000 ppm, at this time windows
> are open will result in the ERROR (between the set point and actual indoor
> CO2 concentration) increasing. So I'm puzzled!
>
>
> Now, I only would like a solution for this problem as I said in recent
> emails and the adequate explanations for this OF_CO2 concentration_PID
> control issue in TRNSYS .****
>
>  ****
>
>  ****
>
> Many thanks in advance!****
>
>  ****
>
> br****
>
>  ****
>
> wang****
>
>
>
>
>
> 2011/11/16 Marcus <jones.0bj3 at gmail.com>
>
>> I just wanted to quickly mention that from my experience with PID control
>> in TRNSYS, you should start with Kp  ~ 0, Ki = timestep, and Kd = 0.
>> Furthermore, give the simulation a very short timestep. So I typically
>> start with Kp = 0.00001 and timestep = 30 seconds, and then slowly increase
>> Kp. As I guess you realize now, this is to first eliminate any oscillatory
>> effect due to high gains over large discrete timesteps.
>>
>> Cheers,
>>
>> Marcus
>> --
>> Marcus Jones,  M.Sc., LEED®AP BD+C
>> *Freelance energy consultant*
>> *Vienna, Austria*
>>
>>
>>
>>
>>
>> On Wed, Nov 16, 2011 at 4:17 PM, <
>> marcello.caciolo at aximaseitha-gdfsuez.com> wrote:
>>
>>>  Sorry, in the point 2) you should read “Input 11 (Fraction of ySet for
>>> proportional effect) should be set to *one*”****
>>>
>>> ** **
>>>
>>> *De :* trnsys-users-bounces at cae.wisc.edu [mailto:
>>> trnsys-users-bounces at cae.wisc.edu] *De la part de*
>>> marcello.caciolo at aximaseitha-gdfsuez.com
>>> *Envoyé :* mercredi 16 novembre 2011 16:14
>>> *À :* yang.wang at unibw.de; trnsys-users at cae.wisc.edu
>>> *Objet :* [SUSPECTED IDENTITY THEFT] Re: [TRNSYS-users] PID controller
>>> in TRNSYS developer****
>>>
>>> ** **
>>>
>>> Dear Wang,****
>>>
>>> ** **
>>>
>>> As I used the PID control many times, I am sure that there is no problem
>>> with the code…I suggest you to check the following two points:****
>>>
>>> ** **
>>>
>>> **1)      **Concentration unit: it happened to me to make trivial
>>> errors because of the expression of concentration: check if the output of
>>> your model is not expressed in percent or per mille instead of ppm;****
>>>
>>> **2)      **Input 11 (Fraction of ySet for proportional effect) should
>>> be set to zero and parameter 1 (mode) to zero.****
>>>
>>> ** **
>>>
>>> In addition, you should plot the output 2 and 4 in order to understand
>>> where the problem is. Output 2 should be equal to set-point concentration
>>> minus actual concentration, output 4 to output 2 multiplied by kp.****
>>>
>>> ** **
>>>
>>> Good luck!****
>>>
>>> ** **
>>>
>>> Best regards,****
>>>
>>> ** **
>>>
>>> Marcello****
>>>
>>> ** **
>>>
>>> *De :* wanghongyang1767 at gmail.com [mailto:wanghongyang1767 at gmail.com] *De
>>> la part de* wangyang
>>> *Envoyé :* mercredi 16 novembre 2011 13:00
>>> *À :* Caciolo Marcello (Axima Seitha);; hotline at transsolar.com
>>> *Objet :* Re: [TRNSYS-users] PID controller in TRNSYS developer****
>>>
>>> ** **
>>>
>>> Dear marcello.caciolo,****
>>>
>>>  ****
>>>
>>> Many thanks for your quick reply!****
>>>
>>>  ****
>>>
>>> I know and understand all what you explained. Since my profession for
>>> Bachelor and Master is Automation control. That is also the reason why I
>>> suspect the function of PID controller in TRNSYS. As you said, I tried many
>>> time the gain Kp and integral time Ki and small time step 1 min or smaller
>>> in order to avoid oscillations, a large difference between the set point
>>> 1000 ppm and actual CO2 concentration etc.****
>>>
>>>  ****
>>>
>>> I mentioned already as my first email about PID controller: I set the
>>> set point CO2 concentration 1000 ppm as PID controller's set point; its
>>> control signal links to Opening Factor (OF) of windows; indoor CO2
>>> concentration links to PID's controlled variable. However, when indoor CO2
>>> concentration is less than set point 1000 ppm, PID begins to activate OF
>>> i.e. windows are open. Based on PID principle, control signal should
>>> be set to zero. BUT it is not like this. As we know, if CO2
>>> concentration is not getting to set point 1000 ppm, at this time windows
>>> are open will result in the ERROR (between the set point and actual indoor
>>> CO2 concentration) increasing. So I'm puzzled! So I suspect the
>>> function of PID controller in TRNSYS.****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> Now, I only would like a solution for this problem as I said in recent
>>> emails and the adequate explanations for this OF_CO2 concentration_PID
>>> control issue in TRNSYS .****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> Many thanks in advance!****
>>>
>>>  ****
>>>
>>> br****
>>>
>>>  ****
>>>
>>> wang****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> ** **
>>>
>>> 2011/11/16 <marcello.caciolo at aximaseitha-gdfsuez.com>****
>>>
>>> Dear Wang,****
>>>
>>>  ****
>>>
>>> I find that your problem description is not very clear, but I try anyway
>>> to guess what you want to do.****
>>>
>>>  ****
>>>
>>> In my understanding, if you want CO2 concentration to be less than 1000
>>> ppm, you should use a PID control with a positive gain and an output signal
>>> between 0 and 1, directly connected to the OF. In this way, if the CO2
>>> concentration is less than 1000 ppm, the error (and integral and derivative
>>> part of the signal, if present) of the PID control will be negative, so
>>> that control signal is set to zero. On the other hand, when CO2
>>> concentration is above 1000 ppm, the error is positive and the output
>>> signal will be more than 0, so opening the window. ****
>>>
>>>  ****
>>>
>>> Take care to the choice of the gain of the PID: a too high value could
>>> generate oscillations, while a value too low will lead to a large
>>> difference between actual and setpoint CO2 concentration. Also note that,
>>> without an integral part, the PID control is purely proportional and will
>>> always lead to a CO2 concentration higher than 1000 ppm. However, the
>>> integral time should be high enough to prevent oscillations. The time
>>> period should be also short enough in order to avoid instabilities in
>>> control.****
>>>
>>>  ****
>>>
>>> Guessing a good value of the gain and the integral time of a PID needs
>>> to wall understand the main principles of a proportional and integral
>>> controller. I suggest you to have a look to some textbooks about HVAC
>>> control in order to understand  these principles.****
>>>
>>>  ****
>>>
>>> I hope that these explanation will help you.****
>>>
>>>  ****
>>>
>>> Best regards,****
>>>
>>> *Marcello CACIOLO*
>>> Responsable Outils et Méthodes d'Analyse Energétique
>>> ___________________________________________________
>>>
>>> *Erreur ! Nom du fichier non spécifié.*
>>> *
>>> Cellule Efficacité Energétique*****
>>>
>>> Direction Commerciale*
>>> *46 Boulevard de la Prairie au Duc BP 40119
>>> 44000 Nantes Cédex 2
>>> Tel. 02 40 41 06 57****
>>>
>>>
>>> mail: marcello.caciolo at aximaseitha-gdfsuez.com****
>>>
>>> *
>>> *www.aximaseitha-gdfsuez.com****
>>>
>>>  ****
>>>
>>> P *Pensez à l'environnement avant d'imprimer ce message*****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> *De :* trnsys-users-bounces at cae.wisc.edu [mailto:
>>> trnsys-users-bounces at cae.wisc.edu] *De la part de* wangyang
>>> *Envoyé :* mercredi 16 novembre 2011 10:53
>>> *À :* David BRADLEY; trnsys-users at cae.wisc.edu; hotline at transsolar.com
>>> *Objet :* Re: [TRNSYS-users] PID controller in TRNSYS developer****
>>>
>>>  ****
>>>
>>> Dear David,****
>>>
>>>  ****
>>>
>>> As I said yesterday, I linked PID's output Control Signal to a minus 1
>>> then to OF. The results are still very *WEIRD. *OF becomes minus value
>>> which is not reasonable very much i.e. the window is open towards abnormal
>>> direction; CO2 concentration is not decreasing as we hoped, however, it is
>>> becoming much more bigger e.g. 4000 ppm.****
>>>
>>>  ****
>>>
>>> Now, I only would like a solution for this problem as I said in last
>>> email and the adequate explanations for this OF_CO2 concentration_PID
>>> control issue.****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> Many thanks in advance!****
>>>
>>>  ****
>>>
>>> br****
>>>
>>>  ****
>>>
>>> wang****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> 2011/11/15 王洋 <wanghongyang1767 at gmail.com>****
>>>
>>> Dear David,****
>>>
>>>  ****
>>>
>>> Many thanks for your reply!****
>>>
>>>  ****
>>>
>>> I already saw both of them as you mentioned, however, they are not
>>> helpful for my simulation results i.e. they don't explain the things I
>>> wanted.****
>>>
>>>  ****
>>>
>>> Your heating/cooling example is very vivid. Do you mean I need add an
>>> equation after the PID i.e. link PID's output Control Signal to a minus 1
>>> then to OF? ****
>>>
>>>  ****
>>>
>>> Now, I only would like a solution for this problem as I said in last
>>> email and the adequate explanations for this OF_CO2 concentration_PID
>>> control issue.****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> Many thanks in advance!****
>>>
>>>  ****
>>>
>>> br****
>>>
>>>  ****
>>>
>>> wang****
>>>
>>>  ****
>>>
>>>
>>>  ****
>>>
>>> 2011/11/14 David BRADLEY <d.bradley at tess-inc.com>****
>>>
>>> Wang,
>>>   You should already have the source code for the PID controller in
>>> ..\TrnsysXX\SourceCode\Types\. I would also recommend reading the Type23
>>> section of the 04-MathematicalDescription manual.
>>>
>>>   PID controllers can operate in one of two ways: they can generate a
>>> greater signal value if the sampled input value is below the set point or
>>> they can generate a greater signal value if the sampled input is above the
>>> current set point. Imagine a heating application with a PID controller. As
>>> the zone temperature falls, you want the PID to give you a bigger and
>>> bigger signal. Now imagine a cooling application. As the zone temperature
>>> rises, you want the PID to give you a bigger and bigger signal. You may
>>> have to add an equation after the PID to invert its control signal if it is
>>> acting the opposite of the way that you want.
>>>
>>> David ****
>>>
>>>
>>>
>>> On 11/14/2011 04:28, wangyang wrote: ****
>>>
>>> Dear all,****
>>>
>>>  ****
>>>
>>>     I have a question about PID controller in TRNSYS for its developer.*
>>> ***
>>>
>>>  ****
>>>
>>>     Which expert knows PID controller in TRNSYS developer? Or Which
>>> expert could pass me the source code of PID controller or its internal
>>> algorithm etc.? I guess PID controller in TRNSYS is based on empirical
>>> equation or iterative algorithm. Since there is *very weird* simulation
>>> results i.e. I set the set point CO2 concentration 1000 ppm as PID
>>> controller's set point; its control signal links to Opening Factor (OF) of
>>> windows; indoor CO2 concentration links to PID's controlled variable.
>>> However, when indoor CO2 concentration is less than set point 1000 ppm, PID
>>> begins to activate OF i.e. windows are open. But based on PID principle, as
>>> we know, if CO2 concentration is not getting to set point 1000 ppm, at this
>>> time windows are open will result in *the ERROR* (between the set point
>>> and actual indoor CO2 concentration)* increasing. *So I'm puzzled!
>>> Please PID controller in TRNSYS developer or other experts explain this
>>> weird phenomenon!****
>>>
>>>    Many thanks in advance!****
>>>
>>>  ****
>>>
>>>    br****
>>>
>>>  ****
>>>
>>>    wang****
>>>
>>>  ****
>>>
>>> 2011/11/12 <trnsys-users-request at cae.wisc.edu>****
>>>
>>> Send TRNSYS-users mailing list submissions to
>>>        trnsys-users at cae.wisc.edu
>>>
>>> To subscribe or unsubscribe via the World Wide Web, visit
>>>        https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>> or, via email, send a message with subject or body 'help' to
>>>        trnsys-users-request at cae.wisc.edu
>>>
>>> You can reach the person managing the list at
>>>        trnsys-users-owner at cae.wisc.edu
>>>
>>> When replying, please edit your Subject line so it is more specific
>>> than "Re: Contents of TRNSYS-users digest..."
>>>
>>> Today's Topics:
>>>
>>>   1. Re: (no subject) (David BRADLEY)
>>>   2. Re: TRNSYS3D Shading on Walls? (David BRADLEY)
>>>   3. Re: how to identify a wall that is adjacent two walls
>>>      (David BRADLEY)
>>>   4. Error in reading type 51 external performance File
>>>      (Walif M'kacher)
>>>
>>>
>>> ---------- 已转发邮件 ----------
>>> From: David BRADLEY <d.bradley at tess-inc.com>
>>> To: Erik Boschek <erikboschek at yahoo.com>
>>> Date: Fri, 11 Nov 2011 12:01:47 -0600
>>> Subject: Re: [TRNSYS-users] (no subject)****
>>>
>>> Erik,
>>>  You are right on with all three of your points. For reference, we
>>> discontinued use of Type109 in Trnsys17 in favor of option 2 (Type15),
>>> which is correct from an energy perspective even though it isn't a smooth
>>> curve. In gernal think that a control strategy that relies only on the
>>> instantaneous DNI as its input might run into trouble not only in
>>> simulation but also in the real world; clouds pass in front of the sun
>>> rapidly sometimes. While I won't pretend that the "spiky" profile that
>>> Type15 generates is totally realistic, I think it is a fairly accurate
>>> representation of DNI. Bear in mind that Type15 is trying to reconstruct a
>>> minute by minute radiation profile based only on 1 number and to do so
>>> correctly for all possible climate types. You might consider a control
>>> strategy that uses the output of Type15 but put through a running-average
>>> component so that your control decisions are based on a somewhat more
>>> stable (smoother) profile.
>>> Best,
>>>  David
>>>
>>>
>>> On 11/11/2011 00:32, Erik Boschek wrote: ****
>>>
>>>  ****
>>>
>>> Dear TRNSYS users,****
>>>
>>>  ****
>>>
>>> I have a simple question regarding weather reading and interpolating
>>> direct normal radiation (DNI) values for time steps less than an hour.**
>>> **
>>>
>>>  ****
>>>
>>> As long as I have been using TRNSYS (using TRNSYS 16.1) I have
>>> understood this can be done in a few ways as follows, including the
>>> consequence for an example TM2 file (see attached screen shot for
>>> clarification):****
>>>
>>>  ****
>>>
>>> 1.) Do not interpolate, using Type 15 with output DNR (not
>>> interpolated): you end up with a "steppy" profile****
>>>
>>> 2.) Using Type 15, but with 2-axis tracking and the output "Beam
>>> radiation for surface": you get a discontinuous "spikey" profile, but the
>>> integration of energy across the hour is respected****
>>>
>>> 3.) Same as 2, but using Type109-TMY2: You get a smooth profile, but
>>> often there appear inexplicable spikes at the beginning or end of the day.
>>> The one in the plot obviously is an extreme case.****
>>>
>>>  ****
>>>
>>> For reference: I just used the Daggett profile "US-CA-Daggett-23161.tm2"
>>> which came with TRNSYS, but the behavior is not specific to this file.**
>>> **
>>>
>>>  ****
>>>
>>> Generally, I have been using 2, but it can cause problems if there is,
>>> for example, some triggering function based on DNI and the DNI hovers
>>> around the threshold. Is there another option for getting a smoother
>>> profile or is it best just to not interpolate? Any opinions? Feel free to
>>> point me to an earlier post on this topic in case I missed it.****
>>>
>>>  ****
>>>
>>> Thanks,****
>>>
>>>  ****
>>>
>>> Erik Boschek****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> _______________________________________________****
>>>
>>> TRNSYS-users mailing list****
>>>
>>> TRNSYS-users at cae.wisc.edu****
>>>
>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users****
>>>
>>> ** **
>>>
>>> -- ****
>>>
>>> *******************************
>>>
>>> David BRADLEY****
>>>
>>> Principal****
>>>
>>> Thermal Energy Systems Specialists, LLC****
>>>
>>> 22 North Carroll Street - suite 370****
>>>
>>> Madison, WI  53703 USA****
>>>
>>>  ****
>>>
>>> P:+1.608.274.2577****
>>>
>>> F:+1.608.278.1475****
>>>
>>> d.bradley at tess-inc.com****
>>>
>>>  ****
>>>
>>> http://www.tess-inc.com****
>>>
>>> http://www.trnsys.com****
>>>
>>>
>>>
>>> ---------- 已转发邮件 ----------
>>> From: David BRADLEY <d.bradley at tess-inc.com>
>>> To: Marion Hiller <hiller at transsolar.com>
>>> Date: Fri, 11 Nov 2011 12:03:16 -0600
>>> Subject: Re: [TRNSYS-users] TRNSYS3D Shading on Walls?
>>> TRNSYS-users,
>>>  My apologies; my reply to Graham was incorrect; as Marion says, only
>>> the windows are affected.
>>> Kind regards,
>>>  David
>>>
>>>
>>> On 11/11/2011 01:33, Marion Hiller wrote:****
>>>
>>> Graham,
>>>
>>> the shading defined in Trnsys3D effects only windows.
>>>
>>> Marion
>>>
>>> Dipl.-Ing. Marion Hiller
>>> TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
>>> und Nutzerkomfort in Gebäude
>>> Munich - New York - Stuttgart + 49.711.67976.0
>>>
>>> Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
>>> Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
>>> DE152272639
>>> Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
>>> Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
>>>
>>>
>>>
>>> -----Ursprüngliche Nachricht-----
>>> Von: Graham Linn [mailto:grahamjlinn at gmail.com]
>>> Gesendet: Donnerstag, 10. November 2011 21:49
>>> An: trnsys-users at cae.wisc.edu
>>> Betreff: [TRNSYS-users] TRNSYS3D Shading on Walls?
>>>
>>> Hello TRNSYS users,
>>>
>>> I have a question about shading in TRNSYS3D. Does a shading object
>>> affect how much insolation hits the entire building or just the
>>> windows on the building?
>>>
>>> Thank you!
>>> Graham
>>> _______________________________________________
>>> TRNSYS-users mailing list
>>> TRNSYS-users at cae.wisc.edu
>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>
>>>
>>>
>>> _______________________________________________
>>> TRNSYS-users mailing list
>>> TRNSYS-users at cae.wisc.edu
>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users****
>>>
>>>
>>> --
>>> ***************************
>>> David BRADLEY
>>> Principal
>>> Thermal Energy Systems Specialists, LLC
>>> 22 North Carroll Street - suite 370
>>> Madison, WI  53703 USA
>>>
>>> P:+1.608.274.2577
>>> F:+1.608.278.1475
>>> d.bradley at tess-inc.com
>>>
>>> http://www.tess-inc.com
>>> http://www.trnsys.com
>>>
>>>
>>>
>>>
>>> ---------- 已转发邮件 ----------
>>> From: David BRADLEY <d.bradley at tess-inc.com>
>>> To: Nidal Abdalla <nidalabdalla at yahoo.com>
>>> Date: Fri, 11 Nov 2011 12:29:48 -0600
>>> Subject: Re: [TRNSYS-users] how to identify a wall that is adjacent two
>>> walls****
>>>
>>> Nidal,
>>>   You have to be a little careful here. If you have a wall in zone 1,
>>> half of which is adjacent to zone 2 and half of which is adjacent to zone
>>> 3, you actually need to draw the wall as two walls in zone 1. Trnsys3D
>>> requires the user to be quite vigilant about manually setting adjacencies.
>>> You need to draw the ADJACENT wall in both zones and you need to open the
>>> object window for each of them, set the construction to ADJ_WALL, set the
>>> "outside boundary condition" to "Zone" and then manually select the zone to
>>> which it is adjacent in the "outside boundary object" field.
>>>
>>>   If you have been very careful about drawing your ADJACENT walls so
>>> that they have exactly the same verticies in both zones to which they
>>> belong, you can then select the menu item:  Plugins: Trnsys3d: Surface
>>> Matching and click the "match in entire model" button.
>>>
>>> Kind regards,
>>>  David
>>>
>>>
>>> On 11/11/2011 08:32, Nidal Abdalla wrote: ****
>>>
>>> I drew a house using Trnsys3d that consists of: 3 bed rooms, living
>>> room, guest room and bath . The house was divided into 6 zones. Wall_zone5,
>>> for example, is adjacent two walls for two different zones. I am wondering
>>> how to identify a wall (using Object Info) that is adjacent two or more
>>> walls of diff. zones.****
>>>
>>>  ****
>>>
>>> Best Regards****
>>>
>>>  ****
>>>
>>> Nidal Abdalla****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> _______________________________________________****
>>>
>>> TRNSYS-users mailing list****
>>>
>>> TRNSYS-users at cae.wisc.edu****
>>>
>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users****
>>>
>>> ** **
>>>
>>> -- ****
>>>
>>> *******************************
>>>
>>> David BRADLEY****
>>>
>>> Principal****
>>>
>>> Thermal Energy Systems Specialists, LLC****
>>>
>>> 22 North Carroll Street - suite 370****
>>>
>>> Madison, WI  53703 USA****
>>>
>>>  ****
>>>
>>> P:+1.608.274.2577****
>>>
>>> F:+1.608.278.1475****
>>>
>>> d.bradley at tess-inc.com****
>>>
>>>  ****
>>>
>>> http://www.tess-inc.com****
>>>
>>> http://www.trnsys.com****
>>>
>>>
>>>
>>> ---------- 已转发邮件 ----------
>>> From: "Walif M'kacher" <walif.mkacher at gmail.com>
>>> To: trnsys-users at cae.wisc.edu
>>> Date: Sat, 12 Nov 2011 15:13:05 +0100
>>> Subject: [TRNSYS-users] Error in reading type 51 external performance
>>> File****
>>>
>>> Dear TRNSys Users,****
>>>
>>>  ****
>>>
>>> I have a problem with external file of type 51a (cooling tower with an
>>> external performance File):****
>>>
>>>  ****
>>>
>>> That the simulation with this type causes error and this can't read this
>>> external file (.txt)****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> Would you please help me how to correct the file joined or send me a
>>> truth format of this .txt file****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>> Many thanks in advance****
>>>
>>>  ****
>>>
>>> *Mkacher Walif*****
>>>
>>>
>>> _______________________________________________
>>> TRNSYS-users mailing list
>>> TRNSYS-users at cae.wisc.edu
>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users****
>>>
>>> ** **
>>>
>>> _______________________________________________****
>>>
>>> TRNSYS-users mailing list****
>>>
>>> TRNSYS-users at cae.wisc.edu****
>>>
>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users****
>>>
>>> ** **
>>>
>>> -- ****
>>>
>>> *******************************
>>>
>>> David BRADLEY****
>>>
>>> Principal****
>>>
>>> Thermal Energy Systems Specialists, LLC****
>>>
>>> 22 North Carroll Street - suite 370****
>>>
>>> Madison, WI  53703 USA****
>>>
>>>  ****
>>>
>>> P:+1.608.274.2577****
>>>
>>> F:+1.608.278.1475****
>>>
>>> d.bradley at tess-inc.com****
>>>
>>>  ****
>>>
>>> http://www.tess-inc.com****
>>>
>>> http://www.trnsys.com****
>>>
>>>  ****
>>>
>>>  ****
>>>
>>>
>>> GDF SUEZ Mail Disclaimer:
>>> http://www.gdfsuez.com/disclaimer/disclaimer-fr.html****
>>>
>>> ** **
>>>
>>>
>>> GDF SUEZ Mail Disclaimer:
>>> http://www.gdfsuez.com/disclaimer/disclaimer-fr.html****
>>>
>>>
>>> GDF SUEZ Mail Disclaimer:
>>> http://www.gdfsuez.com/disclaimer/disclaimer-fr.html
>>>
>>>
>>> _______________________________________________
>>> TRNSYS-users mailing list
>>> TRNSYS-users at cae.wisc.edu
>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>
>>>
>>
>>
>>
>>
>>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111122/02e4000e/attachment-0005.htm>


More information about the TRNSYS-users mailing list