David BRADLEY d.bradley at tess-inc.com
Mon Nov 14 10:31:11 PST 2011


Walif,
   I think it is the "Line X>" text that is causing the problem. You 
should have a file with only numbers in it. If you are using Trnsys17, 
there is an example file in:

..\Trnsys17\Examples\DataFiles\Type51-CoolingTower.dat

Alternatively, you can look in the Type51 section of the 
04-MathematicalReference manual (for both Trnsys16 and Trnsys17) to see 
an example data file.
Kind regards,
  David


On 11/12/2011 08:13, Walif M'kacher wrote:
>
> Dear TRNSys Users,
>
> I have a problem with external file of type 51a (cooling tower with an 
> external performance File):
>
>
> That the simulation with this type causes error and this can't read 
> this external file (.txt)
>
>
>
> Would you please help me how to correct the file joined or send me a 
> truth format of this .txt file
>
>
> Many thanks in advance
>
> _Mkacher Walif_
>
>
>