Béatrice,
   The error message is indicating that the energy balance across one of 
the walls in your Type56 (I am guessing) building is not converging. 
Specifically, the outside surface temperature of the wall is not coming 
to a stable solution. If you are using an algorithm to set the 
convection coefficient on the outside surface of your wall, make sure 
that the algorithm cannot produce a result of 0; this would indicate 
that there is NO convective heat transfer on the outside surface of the 
wall and that only the radiation matters, which is unrealistic. The 
second thing to try is that if you have variable convective coefficients 
on either the inside or the outside surface of that wall, turn them off 
and use constant values.
Kind regards,
  David

On 11/4/2011 04:21, beatrice bernin wrote:
> Hello,
>
> I have a mistake during a simulation, an eror occured :outside 
> temperature of 11 wall in zone 3 at time 8718 not converged.
> I don't uderstand the mistake because I've two models:
> One with a building and convectors and it works, another with the same 
> buildind, convector and a wood poele ans it doesn't work
> Can you help me?
>
> Best regards
>
> Béatrice Bernin
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111107/d31df2e9/attachment-0005.htm>


More information about the TRNSYS-users mailing list