Nidal,
You have to be a little careful here. If you have a wall in zone 1,
half of which is adjacent to zone 2 and half of which is adjacent to
zone 3, you actually need to draw the wall as two walls in zone 1.
Trnsys3D requires the user to be quite vigilant about manually setting
adjacencies. You need to draw the ADJACENT wall in both zones and you
need to open the object window for each of them, set the construction to
ADJ_WALL, set the "outside boundary condition" to "Zone" and then
manually select the zone to which it is adjacent in the "outside
boundary object" field.
If you have been very careful about drawing your ADJACENT walls so
that they have exactly the same verticies in both zones to which they
belong, you can then select the menu item: Plugins: Trnsys3d: Surface
Matching and click the "match in entire model" button.
Kind regards,
David
On 11/11/2011 08:32, Nidal Abdalla wrote:
> I drew a house using Trnsys3d that consists of: 3 bed rooms, living
> room, guest room and bath . The house was divided into 6 zones.
> Wall_zone5, for example, is adjacent two walls for two different
> zones. I am wondering how to identify a wall (using Object Info) that
> is adjacent two or more walls of diff. zones.
> Best Regards
> Nidal Abdalla
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111111/e581f8b1/attachment-0001.htm>
More information about the TRNSYS-users
mailing list