[TRNSYS-users] Low flow collector operation with immersed heat exchanger in Type60
David BRADLEY
d.bradley at tess-inc.com
Thu Nov 10 09:59:32 PST 2011
William,
I would be very careful in using the Type60 with an internal heat
exchanger and low flow rates, particularly if you are anywhere close to
laminar flow. I have run into some problems with its internal
calculation of the heat exchanger UA as well. If possible, I would
recommend that you use Type534 from the TESS Storage Libary. In my
experience, the UA calculation for that tank model's internal heat
exchanger is more robust.
Best,
David
On 11/10/2011 04:32, William.Logie at solarenergy.ch wrote:
>
> Dear TRNSYS folk,
>
> I was wondering if anyone can shed some light on Type60, in particular
> low flow operation of the immersed heat exchanger model (IHX). I'm
> using the 16.01.0003 edition of TRNSYS and 2005-01-31 -- Mku version
> of Type60.
>
> I've been happily simulating high-flows (>40kg/hr per m^2 collector
> area) but run into non-convergence warnings (and infinite loops) with,
> for example, a specific collector flow of 10kg/hr; storage volume 400
> litres with 25 nodes and a simulation time step between 3 and 6 mins;
> http://sel.me.wisc.edu/trnsys/mailinglist/archive2004/msg00640.html. I
> have tried reducing the flow rate to a minute and even less but
> non-convergence persists (for an annual simulation that doesn't abort
> I get between 2 and 5 thousand warnings). Some exemplary energy
> balances (measured with Type60) are as follows;
>
> 10kg/hr:
>
> Q_coll + Q_aux = 13934081.86 kJ
>
> Q_losses + Q_dhw = 13920759.15 kJ
>
> Q_coll + Q_aux -- Q_losses -- Q_dhw = Q_err = 13322.71 kJ
>
> 50kg/hr:
>
> Q_coll + Q_aux = 13961476.57 kJ
>
> Q_losses + Q_dhw = 13947209.16 kJ
>
> Q_coll + Q_aux -- Q_losses -- Q_dhw = Q_err = 14267.41 kJ
>
> Is this all within reason? If not, any tips?
>
> Kind regards,
>
> ------------------------------------------------------------------------
>
> *William Logie*
> Forschung / Research
>
> Institut für Solartechnik SPF: Adresse
> <http://www.solarenergy.ch/spf.php?lang=de&fam=44&tab=3> / Website
> <http://www.solarenergy.ch/spf.php?lang=de&fam=41&tab=1>
> Hochschule für Technik Rapperswil HSR
> Tel. +41 55 222 48 34
> Fax +41 55 222 48 44
>
> ------------------------------------------------------------------------
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111110/b06a28b5/attachment-0001.htm>
More information about the TRNSYS-users
mailing list