[TRNSYS-users] Error: generating shading/insolation matrix

Marion Hiller hiller at transsolar.com
Wed May 18 23:38:42 PDT 2011


Dear Joke,

in Trnsys3d the surfaces (walls, window and shaders) have arbitrary 
names composed by numbers and characters. The import converts them to 
unique surface ID numbers without changing existing already converted 
surface IDs. In Version 17.00.0018 the import had a bug when there where 
no characters in the automatic generated name of trnsys3D.
This bug is fixed in the current version 17.00.0019. in order to solve 
your problem, please contact your distributor for a free update.

Kind Regards,

Marion 

P.S. I received two emails with attachments but the original IDF file    
    doesn't seem to be included.


 
Dipl.-Ing. Marion Hiller 
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen 
und Nutzerkomfort in Gebäude 
Munich - New York - Stuttgart + 49.711.67976.0 

Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart 
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.: 
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer, 
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher 

 

-----Ursprüngliche Nachricht-----
Von: Joke De Beuckelaer [mailto:joke.d at vkgroup.be] 
Gesendet: Donnerstag, 19. Mai 2011 08:09
An: Marion Hiller
Cc: TRNSYS-users
Betreff: RE: Re: [TRNSYS-users] Error: generating shading/insolation 
matrix

Dear Marion,


It's strange that the error occurs because the surface number>999. When 
I deleted all the shading except 1 rectangle, the same error occurred. 
Or is this number (999) with the surfaces of the model included?

In attachment you can find the original idf file. Normally I've send all 
my files already, didn't you receive them?

I'm working with Trnsys version 17.00.0018.



Thanks a lot already for all your help and I hope you can find the 
problem,
Kind regards,

Joke De Beuckelaer
project engineer mep


VK     HEALTHCARE      |      BUILDINGS      |      INDUSTRY      |      
INFRA

Value by design

VK ENGINEERING  Avenue Clemenceaulaan 87, 1070 Bruxelles Brussel, 
Belgium
t   +32 2 414 07 77   f  +32 2 414 04 98   m  +32 473 97 01 50   e   
joke.d at vkgroup.be   w   www.vkgroup.be

-----Oorspronkelijk bericht-----
Van: Marion Hiller [mailto:hiller at transsolar.com]
Verzonden: dinsdag 17 mei 2011 13:27
Aan: Joke De Beuckelaer
CC: TRNSYS-users
Onderwerp: AW: Re: [TRNSYS-users] Error: generating shading/insolation 
matrix

Joke,

the error message is due to too surface numbers > 999. The surface
number can't be written in the log file (artsmetiers7_shd.log) and ***
are written instead.

*** Notice at time        :         0.000000
 Orientation of wall   SURF=***: azimuth angle= 180.00°, slope=  90.00°
 Orientation of wall   SURF=***: azimuth angle=   0.00°, slope=   0.00°

In order to see why the surface numbers are so high (starting with
3993 instead of 1) I need to need the original *.idf and check the
import function.

With what version of TRNSYS17 are you working? I have in mind that we
fixed such a bug created by the import.

Kind regards,

Marion



-----Ursprüngliche Nachricht-----
Von: Joke De Beuckelaer [mailto:joke.d at vkgroup.be]
Gesendet: Donnerstag, 12. Mai 2011 08:58
An: duffy at tess-inc.com; trnsys-users at cae.wisc.edu
Betreff: Re: [TRNSYS-users] Error: generating shading/insolation matrix

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users



 VISIT US AT REALTY   SUBSCRIBE FOR THE VK-COCKTAIL AT REALTY
<mailto:marketing at vkgroup.be?SUBJECT=vk-cocktail>
****DISCLAIMER****
This communication is confidential and for the sole useof the addressee. 
If you are not the intended recipient,
please immediately notify the sender by e-mail at the address shown and 
then delete it from your system
without copying, disclosing or forwarding its contents. Thank you.







More information about the TRNSYS-users mailing list