[TRNSYS-users] Error of TRNSYS Message 103
David BRADLEY
d.bradley at tess-inc.com
Tue May 3 08:10:10 PDT 2011
Wang,
The error message should reference one of the Types in your simulation.
TRNSYS is telling you that it doesn't like the value of parameter 4 for
that Type. You might get this error if you entered a negative value for
the specific heat. You might also get this error in a 2-stage thermostat
if you entered a second stage setpoint temperature that was greater than
your first stage set point.
David
On 5/3/2011 09:56, 王洋 wrote:
> Dear all,
>
> I met the ERROR as follows:
>
> TRNSYS Message 103 : The TRNSYS TYPE checking routine has found an
> inconsistency in the specified component between the input file and
> the information expected by the Type
> Reported information : An illegal PARAMETER value has been reported by
> the model. The model has reported that Parameter 4 is the problem -
> but this may not be the case. Please check the component configuration.
>
> Thanks a lot in advance!
>
> Br.
>
> wang
>
> 2011/5/3 <trnsys-users-request at cae.wisc.edu
> <mailto:trnsys-users-request at cae.wisc.edu>>
>
> Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>
> To subscribe or unsubscribe via the World Wide Web, visit
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
> <mailto:trnsys-users-request at cae.wisc.edu>
>
> You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
> <mailto:trnsys-users-owner at cae.wisc.edu>
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
> 1. problem in debugging TRNSYS 16 (Jordi Cipriano)
>
>
> ---------- 已转发邮件 ----------
> From: Jordi Cipriano <cipriano at cimne.upc.edu
> <mailto:cipriano at cimne.upc.edu>>
> To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
> Date: Tue, 03 May 2011 12:49:02 +0200
> Subject: [TRNSYS-users] problem in debugging TRNSYS 16
> Dear all,
>
> Few years ago I made some new types with TRNSYS 16. Now I've made
> some modifications on them and I'm trying to check wether they
> work or not. I'm using a windows XP system and the Compaq Visual
> fortran 6.6.a as a compiler.
> When I use the debugging, the project crashes in the Exec.for
> kernel file, with the following error message:
>
>
> Does anybody knows what kind of problem do I have?
>
> Thanks,
>
> --
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110503/d450f292/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 20187 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110503/d450f292/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 12455 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110503/d450f292/attachment-0001.gif>
More information about the TRNSYS-users
mailing list