I found some problem in Type 66: Calling EES, TRNSYS17. I tried to run the
example that comes with the program but the solver cannot start, the error
message in the list file show that
*** Fatal Error at time : 3648.000000
Generated by Unit : 5
Generated by Type : 66
TRNSYS Message 103 : The TRNSYS TYPE checking routine has found an
inconsistency in the specified component between the input file and the
information expected by the Type
Reported information : An illegal number of PARAMETERS has been
specified for this component. Please check the component configuration. 0
PARAMETERS are required and 4 were specified.
I use the EES professional version, all the paths should be correct. I tried
to create a new simple file or even use the file that used to be able to run
for TRNSYS 16 but the same message always show up. I also attach the list
file with this mail. Please kindly check, there might be something wrong in
this component, or some setting parameters are wrong.
Thank you very much and looking forward to hearing from you.
Best Regards,
Wimolsiri
Wimolsiri Pridasawas
Dept. of Chemical Engineering
King Mongkut's University of Technology Thonburi
126 Pracha U-thit Rd.
Bangmod, Tungkru
Bangkok 10140
Tel. +66 (0)04709222 ext 211
Fax. +66(0)2 4283534
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110330/7da099fc/attachment-0005.htm>
-------------- next part --------------
TRNSYS - the TRaNsient SYstem Simulation program
The Solar Energy Lab at the University of Wisconsin - Madison, USA
Le Centre Scientifique et Technique du Batiment, Sophia Antipolis, France
Transsolar Energietechnik GmBH, Stuttgart, Germany
Thermal Energy System Specialists, LLC, Madison Wisconsin, USA
Release 17.00.0012
Listing file for: "C:\Trnsys17\Examples\Calling_EES\Calling EES.dck"
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : The TRNSYS Executable (TRNExe.exe) and main DLL (TRNDll.dll) are located in "C:\Trnsys17\Exe"
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : 208
TRNSYS Message 75 : The Type referenced below requires descriptors instead of initial values.
Reported information : Type 208
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : 535
TRNSYS Message 75 : The Type referenced below requires descriptors instead of initial values.
Reported information : Type 535
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : 580
TRNSYS Message 76 : The following Type has been identified as allowing the unit specifications (kg/h for example) after the input specifications and intial values for the inputs. The critical parameter number, and the value of this critical parameter that indicates that the units will be supplied is also listed. This information was retrieved from the VarUnits.dat file loacted in the \Exe directory of your TRNSYS 16 installation.
Reported information : Type 580, Critical Parameter 11, Parameter Value 1
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : 580
TRNSYS Message 88 : The following Type has been identified as allowing FORMAT statements. This information was retrieved from the Formats.dat file loacted in the \Exe directory of your TRNSYS 16 installation.
Reported information : Type 580
*** Pre-Processing the TRNSYS EQUATIONs and CONSTANTs to check for fatal errors.
*** Pre-Processing of EQUATIONs and CONSTANTs completed with no fatal errors found.
*** Evaluating the EQUATIONs and CONSTANTs to determine their initial values.
*** Finished evaluating the EQUATIONs and CONSTANTs and ready to begin processing the remainder of the TRNSYS input file.
VERSION 17
*******************************************************************************
*** TRNSYS input file (deck) generated by TrnsysStudio
*** on Monday, March 28, 2011 at 16:27
*** from TrnsysStudio project: C:\Trnsys17\Examples\Calling_EES\Calling EES.tpf
***
*** If you edit this file, use the File/Import TRNSYS Input File function in
*** TrnsysStudio to update the project.
***
*** If you have problems, questions or suggestions please contact your local
*** TRNSYS distributor or mailto:software at cstb.fr
***
*******************************************************************************
*******************************************************************************
*** Units
*******************************************************************************
*******************************************************************************
*** Control cards
*******************************************************************************
* START, STOP and STEP
CONSTANTS 3
START=3648
STOP=3720
STEP=1
* User defined CONSTANTS
! Start time End time Time step
SIMULATION 3.6480000000000000E+03 3.7200000000000000E+03 1.0000000000000000E+00
! Integration Convergence
TOLERANCES 1.0000000000000002E-03 1.0000000000000002E-03
! Max iterations Max warnings Trace limit
LIMITS 30 30 31
! TRNSYS numerical integration solver method
DFQ 1
! TRNSYS output file width, number of characters
WIDTH 80
! NOLIST statement
LIST
! MAP statement
! Solver statement Minimum relaxation factor Maximum relaxation factor
SOLVER 0
1.000000000000000
1.000000000000000
! Nan DEBUG statement
NAN_CHECK 0
! Overwrite DEBUG statement
OVERWRITE_CHECK 0
! disable time report
TIME_REPORT 0
! EQUATION SOLVER statement
EQUATION SOLVING METHOD 0
* Model "Ambient Conditions" (Type 15)
*
UNIT 2 TYPE 15 Conditions
*$UNIT_NAME Ambient Conditions
*$MODEL .\Weather Data Reading and Processing\Standard Format\TMY2\Type15-2.tmf
*$POSITION 69 496
*$LAYER Main #
PARAMETERS 9
! 1 File Type
! 2 Logical unit
! 3 Tilted Surface Radiation Mode
! 4 Ground reflectance - no snow
! 5 Ground reflectance - snow cover
! 6 Number of surfaces
! 7 Tracking mode
! 8 Slope of surface
! 9 Azimuth of surface
2.0000000000000000E+00 3.2000000000000000E+01 3.0000000000000000E+00 2.0000000000000001E-01 7.0000000000000007E-01
1.0000000000000000E+00 1.0000000000000000E+00 0.0000000000000000E+00 0.0000000000000000E+00
*** External files
ASSIGN ..\..\Weather\US-TMY2\US-WI-Madison-14837.tm2 32
*|? Which file contains the TMY-2 weather data? |1000
*------------------------------------------------------------------------------
* Model "ON/OFF Function" (Type 14)
*
UNIT 3 TYPE 14 Function
*$UNIT_NAME ON/OFF Function
*$MODEL .\Utility\Forcing Functions\General\Type14h.tmf
*$POSITION 69 378
*$LAYER Main #
PARAMETERS 12
! 1 Initial value of time
! 2 Initial value of function
! 3 Time at point-1
! 4 Value at point -1
! 5 Time at point-2
! 6 Value at point -2
! 7 Time at point-3
! 8 Value at point -3
! 9 Time at point-4
! 10 Value at point -4
! 11 Time at point-5
! 12 Value at point -5
0.0000000000000000E+00 1.0000000000000000E+00 1.2000000000000000E+01 1.0000000000000000E+00 1.2000000000000000E+01
0.0000000000000000E+00 1.6000000000000000E+01 0.0000000000000000E+00 1.6000000000000000E+01 1.0000000000000000E+00
2.4000000000000000E+01 1.0000000000000000E+00
*------------------------------------------------------------------------------
* EQUATIONS "Equa"
*
EQUATIONS 4
P2 = 4
M_DOT_TRN = 360
R = 0.288
N = 1.3
*$UNIT_NAME Equa
*$LAYER Main
*$POSITION 241 272
*------------------------------------------------------------------------------
* Model "Always ON" (Type 66)
*
UNIT 5 TYPE 66 ON
*$UNIT_NAME Always ON
*$MODEL .\Utility\Calling External Programs\EES\Call EES EveryTime\Type66a.tmf
*$POSITION 461 321
*$LAYER Main #
PARAMETERS 4
! 1 Input mode
! 2 not used
! 3 Allowable wait
! 4 Number of ouputs
1.0000000000000000E+00 1.0000000000000000E+00 1.0000000000000000E+04 6.0000000000000000E+00
INPUTS 7
! Ambient Conditions:Atmospheric pressure ->Input-1
! Ambient Conditions:Dry bulb temperature ->Input-2
! Ambient Conditions:Humidity ratio ->Input-3
! Equa:P2 ->Input-4
! Equa:M_DOT_TRN ->Input-5
! Equa:R ->Input-6
! Equa:N ->Input-7
2,10 2,1 2,6 P2 M_DOT_TRN
R N
*** INITIAL INPUT VALUES
1.0500000000000000E+00 3.0200000000000000E+02 5.0000000000000010E-03 5.0000000000000000E+00 3.6000000000000000E+02
2.8800000000000003E-01 1.3000000000000000E+00
LABELS 2
c:\EES32\ees.exe
compressor.ees
*------------------------------------------------------------------------------
* Model "Last Calc" (Type 66)
*
UNIT 6 TYPE 66 Calc
*$UNIT_NAME Last Calc
*$MODEL .\Utility\Calling External Programs\EES\First Input is a Control Signal\Hold Last Calculated Values when OFF\Type66d.tmf
*$POSITION 465 394
*$LAYER Main #
PARAMETERS 4
! 1 Input mode
! 2 Output mode
! 3 Allowable wait
! 4 Number of ouputs
2.0000000000000000E+00 3.0000000000000000E+00 1.0000000000000000E+04 6.0000000000000000E+00
INPUTS 8
! ON/OFF Function:Average value of function ->Control signal
! Ambient Conditions:Atmospheric pressure ->Input-1
! Ambient Conditions:Dry bulb temperature ->Input-2
! Ambient Conditions:Humidity ratio ->Input-3
! Equa:P2 ->Input-4
! Equa:M_DOT_TRN ->Input-5
! Equa:R ->Input-6
! Equa:N ->Input-7
3,1 2,10 2,1 2,6 P2
M_DOT_TRN R N
*** INITIAL INPUT VALUES
1.0000000000000000E+00 1.0500000000000000E+00 3.0200000000000000E+02 5.0000000000000010E-03 5.0000000000000000E+00
3.6000000000000000E+02 2.8800000000000003E-01 1.3000000000000000E+00
LABELS 2
c:\EES32\ees.exe
compressor.ees
*------------------------------------------------------------------------------
* Model "Predefined" (Type 66)
*
UNIT 7 TYPE 66
*$UNIT_NAME Predefined
*$MODEL .\Utility\Calling External Programs\EES\First Input is a Control Signal\Set Outputs to Predefined Values when OFF\Type66c.tmf
*$POSITION 464 480
*$LAYER Main #
PARAMETERS 10
! 1 Input mode
! 2 Output mode
! 3 Allowable wait
! 4 Number of ouputs
! 5 Value when OFF for output-1
! 6 Value when OFF for output-2
! 7 Value when OFF for output-3
! 8 Value when OFF for output-4
! 9 Value when OFF for output-5
! 10 Value when OFF for output-6
2.0000000000000000E+00 2.0000000000000000E+00 1.0000000000000000E+04 6.0000000000000000E+00 2.0000000000000000E+00
1.0000000000000000E+02 8.0000000000000004E-01 -9.0000000000000000E+00 4.0000000000000000E+01 4.0000000000000000E+01
INPUTS 8
! ON/OFF Function:Average value of function ->Control signal
! Ambient Conditions:Atmospheric pressure ->Input-1
! Ambient Conditions:Dry bulb temperature ->Input-2
! Ambient Conditions:Humidity ratio ->Input-3
! Equa:P2 ->Input-4
! Equa:M_DOT_TRN ->Input-5
! Equa:R ->Input-6
! Equa:N ->Input-7
3,1 2,10 2,1 2,6 P2
M_DOT_TRN R N
*** INITIAL INPUT VALUES
1.0000000000000000E+00 1.0500000000000000E+00 3.0200000000000000E+02 5.0000000000000010E-03 5.0000000000000000E+00
3.6000000000000000E+02 2.8800000000000003E-01 1.3000000000000000E+00
LABELS 2
c:\EES32\ees.exe
compressor.ees
*------------------------------------------------------------------------------
* Model "Zeros" (Type 66)
*
UNIT 8 TYPE 66
*$UNIT_NAME Zeros
*$MODEL .\Utility\Calling External Programs\EES\First Input is a Control Signal\Set Outputs to Zero when OFF\Type66b.tmf
*$POSITION 465 545
*$LAYER Main #
PARAMETERS 4
! 1 Input mode
! 2 Output mode
! 3 Allowable wait
! 4 Number of ouputs
2.0000000000000000E+00 1.0000000000000000E+00 1.0000000000000000E+04 6.0000000000000000E+00
INPUTS 8
! ON/OFF Function:Average value of function ->Control signal
! Ambient Conditions:Atmospheric pressure ->Input-1
! Ambient Conditions:Dry bulb temperature ->Input-2
! Ambient Conditions:Humidity ratio ->Input-3
! Equa:P2 ->Input-4
! Equa:M_DOT_TRN ->Input-5
! Equa:R ->Input-6
! Equa:N ->Input-7
3,1 2,10 2,1 2,6 P2
M_DOT_TRN R N
*** INITIAL INPUT VALUES
1.0000000000000000E+00 1.0500000000000000E+00 3.0200000000000000E+02 5.0000000000000010E-03 5.0000000000000000E+00
3.6000000000000000E+02 2.8800000000000003E-01 1.3000000000000000E+00
LABELS 2
c:\EES32\ees.exe
Compressor.ees
*------------------------------------------------------------------------------
* Model "Temp." (Type 65)
*
UNIT 9 TYPE 65
*$UNIT_NAME Temp.
*$MODEL .\Output\Online Plotter\Online Plotter Without File\Type65d.tmf
*$POSITION 667 434
*$LAYER Main #
PARAMETERS 12
! 1 Nb. of left-axis variables
! 2 Nb. of right-axis variables
! 3 Left axis minimum
! 4 Left axis maximum
! 5 Right axis minimum
! 6 Right axis maximum
! 7 Number of plots per simulation
! 8 X-axis gridpoints
! 9 Shut off Online w/o removing
! 10 Logical unit for output file
! 11 Output file units
! 12 Output file delimiter
5.0000000000000000E+00 8.0000000000000000E+00 -2.0000000000000000E+02 2.0000000000000000E+02 0.0000000000000000E+00
2.0000000000000000E+02 1.0000000000000000E+00 1.2000000000000000E+01 0.0000000000000000E+00 -1.0000000000000000E+00
0.0000000000000000E+00 0.0000000000000000E+00
INPUTS 13
! Ambient Conditions:Dry bulb temperature ->Left axis variable-1
! Always ON:Output-2 ->Left axis variable-2
! Last Calc:Output-2 ->Left axis variable-3
! Predefined:Output-2 ->Left axis variable-4
! Zeros:Output-2 ->Left axis variable-5
! Always ON:Output-4 ->Right axis variable-1
! Always ON:Output-5 ->Right axis variable-2
! Last Calc:Output-4 ->Right axis variable-3
! Last Calc:Output-5 ->Right axis variable-4
! Predefined:Output-4 ->Right axis variable-5
! Predefined:Output-5 ->Right axis variable-6
! Zeros:Output-4 ->Right axis variable-7
! Zeros:Output-5 ->Right axis variable-8
2,1 5,2 6,2 7,2 8,2
5,4 5,5 6,4 6,5 7,4
7,5 8,4 8,5
*** INITIAL INPUT VALUES
T_in T_out1 T_out2 T_out 3 T_out4
Q1 W_actual1 Q2 W_act ual2 Q3
W_actual3 Q4 W_actual4
LABELS 3
Temperatures
Energy
TEMPS and ENERGY
*------------------------------------------------------------------------------
* Model "Pressure and Eff." (Type 65)
*
UNIT 10 TYPE 65 and Eff.
*$UNIT_NAME Pressure and Eff.
*$MODEL .\Output\Online Plotter\Online Plotter Without File\Type65d.tmf
*$POSITION 667 336
*$LAYER Main #
PARAMETERS 12
! 1 Nb. of left-axis variables
! 2 Nb. of right-axis variables
! 3 Left axis minimum
! 4 Left axis maximum
! 5 Right axis minimum
! 6 Right axis maximum
! 7 Number of plots per simulation
! 8 X-axis gridpoints
! 9 Shut off Online w/o removing
! 10 Logical unit for output file
! 11 Output file units
! 12 Output file delimiter
1.0000000000000000E+00 4.0000000000000000E+00 5.0000000000000000E-01 1.0000000000000000E+00 6.0000000000000009E-01
1.0000000000000000E+00 1.0000000000000000E+00 1.2000000000000000E+01 0.0000000000000000E+00 -1.0000000000000000E+00
0.0000000000000000E+00 0.0000000000000000E+00
INPUTS 5
! Ambient Conditions:Atmospheric pressure ->Left axis variable
! Always ON:Output-3 ->Right axis variable-1
! Last Calc:Output-3 ->Right axis variable-2
! Predefined:Output-3 ->Right axis variable-3
! Zeros:Output-3 ->Right axis variable-4
2,10 5,3 6,3 7,3 8,3
*** INITIAL INPUT VALUES
P_ATM Efficiency1 Efficiency 2 Effic iency3 Efficiency4
LABELS 3
Pressure
Efficiency
PRESS and EFF
*------------------------------------------------------------------------------
END
TRANSIENT SIMULATION STARTING AT TIME = 3.6480000000000000E+03
STOPPING AT TIME = 3.7200000000000000E+03
TIMESTEP = 1 / 1
DIFFERENTIAL EQUATION ERROR TOLERANCE = 1.0000000000000002E-03
ALGEBRAIC CONVERGENCE TOLERANCE = 1.0000000000000002E-03
DIFFERENTIAL EQUATIONS SOLVED BY MODIFIED EULER
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
TRNSYS Message 90 : TRNDll.dll is compiled in release mode. External DLLs will be loaded from the .\UserLib\ReleaseDLLs\ directory.
Reported information : Not available
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : The following Types were loaded from TRNDll.dll: Type15, Type14, Type66, Type65
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "FileReader.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "type127.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "Type157_demo_release.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "Type76Lib.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "Type82Lib.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
Message : "Type858-diffeqn.dll" was found but did not contain any components from the input file.
*** Notice at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
TRNSYS Message 199 : TRNSYS found at least one user DLL in the UserLib directory. (Note: Only DLL's including Types that are used in the simulation are loaded)
Reported information : 0 user DLLs were loaded after searching in "C:\Trnsys17\UserLib\ReleaseDLLs"
*** Fatal Error at time : 3648.000000
Generated by Unit : 5
Generated by Type : 66
TRNSYS Message 103 : The TRNSYS TYPE checking routine has found an inconsistency in the specified component between the input file and the information expected by the Type
Reported information : An illegal number of PARAMETERS has been specified for this component. Please check the component configuration. 0 PARAMETERS are required and 4 were specified.
*********************************************************************************************************
The Following UNIT Numbers, TYPE Numbers, and Logical Units Were Used in the Supplied TRNSYS Input File:
2 14 4
3 15 6
5 65 9
6 66 32
7