<Sorry to make you misunderstanding. i intend to make the heating not
working, then i set the heating point as a low level instead of a normal
20 C. because i wanna see the comparison and differences between the case
with type 121 and without type 121, as i said i made the heating not
running, So i meaned the results for the two cases should be the same, the
type 121 which is added for heating doesnt running. However, cooling
consumption of the case with type 121(but i set it not work at all ) is
lower than the case wihout it, and the plot for the room temperature is
also different. >
The room temperature plot shouldn't be the same. In one case you are
keeping the building at a minimum of 20 C and cooling the building when it
hits the cooling setpoint temperature. In the second case, the building
can fall well below 20 C and must come up much farther before cooling
comes on. I'm guessing that there are quite a few days in the shoulder
seasons where the cooling is on with a heating setpoint of 20 C and not on
at all if the building wasn't being heated. Imagine your building is
heated on a cold night to 20 C and the next day is warm. The internal
gains and passive solar gains could raise the building temperature from 20
C to 25 C and the cooling system would turn on. Now imagine that same
cold night without heating. The zone could fall down to 5 C and the next
days passive solar and internal gains may raise it all the way up to 22
but cooling remains off.