Dear trnsys users,
I would like to simulate a SDHW System in which a 4 way valve is used to
discharge the
store (Type 340) with a fixed mixing temperature from 3 temperature zones.
Ive attached a project file Ive used to test the controller.
Ive tried to use two flow diverter and two tee pieces to realize the
system.
Double Port 3 is placed in the top of the storage
Double Port 2 between top and middle of the storage
Double Port 1 in the middle of the storage
Flow diverter 1 outlet flow rate 1 is connected to Double Port 1
Flow diverter 1 outlet flow rate 2 is connected to flow diverter 2 Inlet
flow rate
Flow diverter 2 outlet flow rate 1 is connected to Double Port 2
Flow diverter 2 outlet flow rate 2 is connected to Double Port 3
(in the complete system the temperatures are also connected, but in the
attached file
I have no system between Flow diverter and mixers
and the input
temperatures to the
tee pieces have fixed values to simulate an example for storage
temperatures)
The double ports outlet flow rates and temperatures are connected to two tee
pieces
Tee Piece 1 inlet temperature 1 and flow rate 1 is connected to Double Port
2
Tee Piece 1 inlet temperature 2 and flow rate 2 is connected to Double Port
3
Tee Piece 2 inlet temperature 1 and flow rate 1 is connected to Double Port
1
Tee Piece 2 inlet temperature 2 and flow rate 2 is connected to outlet
temperature and outlet flow
rate of tee piece 1
In the attached file the outlets of the flow diverters are connected to the
inlets of the tee pieces.
Ive tried to control the outlet flow rates from the flow diverters with
iterative feedback controllers
to reach the set point temperature as mixing temperature of tee piece 1 and
2.
The first flow diverter is controlled by an iterative feedback controller
monitoring the
outlet temperature of tee piece 2 (setpoint 40°C)
the second flow diverter is controlled by a second iterative feedback
controller monitoring
the outlet temperature of tee piece 1 (setpoint also 40°C)
the inlet flow rate of flow diverter 1 is fixed
inlet temperature 1 of tee piece 1 is 50°C
inlet temperature 2 of tee piece 1 is 70°C
inlet temperature 1 of tee piece 1 is 30°C
To reach the setpoint the control function of flow diverter 1 has to be zero
and
the control function of flow diverter 2 has to be 0.5.
The first iterative feedback controller works fine, control function is set
to zero, but the second iterative
Feedback controller doesnt work, but I dont know why.
I hope someone can help me or can tell me an easier way to realize the
system.
Thanks
Danny
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110309/6ced4624/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Project43.tpf
Type: application/octet-stream
Size: 101358 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110309/6ced4624/attachment-0005.obj>
More information about the TRNSYS-users
mailing list