Tue Mar 22 01:21:38 PDT 2011
Dear Stefano,
one option is to place an “active layer” in the middle of your wall and
set the mass flow to 0.
Internally this will split your wall into two pieces.
Marion
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
_____
Von: Avesani Stefano [mailto:stefano.avesani at eurac.edu]
Gesendet: Montag, 21. März 2011 18:15
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] building with walls with big thermal mass
Dear all,
I need to simulate the behavior of a building with big thermal mass (old
church, circa 90 cm stone wall).
Unfortunately, this condition does not fulfill the stability criteria.
Which is the best way to simulate this case? Would it make sense to
create another adjacent thermal zone with no air mass capacitance and
with the external wall as half of the massive original wall?
Thanks for helping and suggestions
Stefano