[TRNSYS-users] TR: longwave radiation mode with 2 airnodes
Antoine Gautier
antoine.gautier at solamen.fr
Thu Jun 16 10:07:18 PDT 2011
.inf file was deleted from my previous sending.
De : Antoine Gautier [mailto:antoine.gautier at solamen.fr]
Envoyé : jeudi 16 juin 2011 18:39
À : 'trnsys-users at cae.wisc.edu'
Objet : TR: longwave radiation mode with 2 airnodes
On the same topic
I am trying to model a fully glazed wall with fully transparent window
between the 2 airnodes to account for radiative transfers.
When I save the building file I get the message: .inf etc. generated
successfully.
However when I launch the simulation I get the message in attachment which
appears in TRNEXE window.
If you check the .inf file you will notice that adjacency is well defined
for surfaces 9, 11, 12 and 13 despite the previous message error.
Eventually the simulation goes on but the results tend to convince me that
radiative transfers are not correctly calculated between the 2 airnodes.
Do you have any idea to solve this problem?
Thanks a lot.
Regards
--
Antoine Gautier
Solamen
+33 6 98 78 56 46
antoine.gautier at solamen.fr
De : Antoine Gautier [mailto:antoine.gautier at solamen.fr]
Envoyé : jeudi 16 juin 2011 14:27
À : 'trnsys-users at cae.wisc.edu'
Objet : longwave radiation mode with 2 airnodes
Dear all
I understand from the user manual §5 that longwave radiation exchange is not
taken into account between 2 airnodes of the same zone under standard
(starnet) or one node radiation mode.
Could you please confirm my understanding?
Then what is the best strategy to transfer internal gains and radiative
heating flux (e.g. from active layer) to the other airnode of the same zone
when not using 3D data?
Thanks a lot for your help.
Best regards
--
Antoine Gautier
Solamen
+33 6 98 78 56 46
antoine.gautier at solamen.fr
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110616/3a779334/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Capture.PNG
Type: image/png
Size: 5696 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110616/3a779334/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Project10.inf
Type: application/octet-stream
Size: 59769 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110616/3a779334/attachment-0005.obj>
-------------- next part --------------
*********************************************************************************************************************************************************************************************************
* TRNBuild 2.0.167
*********************************************************************************************************************************************************************************************************
* BUILDING DESCRIPTIONS FILE TRNSYS
* FOR BUILDING: C:\Users\solamen\Documents\My Dropbox\1_presta\2_etudes_en_cours\201105_axima_cdg\jdd\0_wip\Project10.inf
* GET BY WORKING WITH TRNBuild 1.0 for Windows
*********************************************************************************************************************************************************************************************************
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m m e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o j e c t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*+++ PROJECT
*+++ TITLE=ADP S4
*+++ DESCRIPTION=AILE N FILES 60-70
*+++ CREATED=SOLAMEN
*+++ ADDRESS=
*+++ CITY=
*+++ SWITCH=UNDEFINED
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o p e r t i e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
DENSITY=1.204 : CAPACITY=1.012 : PRESSURE=101325.000 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
*--- alpha calculation -------------------
KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
KVERTICAL=5.76 : EVERTICAL=0.3
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
TYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* L a y e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
LAYER ALUMINIUM
CONDUCTIVITY= 730 : CAPACITY= 0.88 : DENSITY= 2700
LAYER PLASTERBOA
CONDUCTIVITY= 0.8 : CAPACITY= 0.84 : DENSITY= 800
LAYER FIBREGLASS
CONDUCTIVITY= 0.144 : CAPACITY= 0.84 : DENSITY= 12
LAYER HEAVYCONCR
CONDUCTIVITY= 6.12 : CAPACITY= 0.84 : DENSITY= 2200
LAYER ALUMINIUM_MASSLESS
RESISTANCE= 0.00065
LAYER MDFBOARD
CONDUCTIVITY= 0.432 : CAPACITY= 1.88 : DENSITY= 500
LAYER CLAY
CONDUCTIVITY= 5.4 : CAPACITY= 1.8 : DENSITY= 1500
LAYER BETON
CONDUCTIVITY= 8.28 : CAPACITY= 1 : DENSITY= 2400
LAYER AIR_FLUX_ASC_GE15MM
RESISTANCE= 0.044
LAYER AIR_FLUX_HOR_GE25MM
RESISTANCE= 0.05
LAYER COUCHE_ACTIVE
PSPACING= 0.35 : PDIAMETER= 0.02 : PWALLTHICKNESS= 0.0019 : PCONDUCTIVITY= 1.26 : CPFLUID= 4.18
LAYER CBR_MUR_PB
RESISTANCE= 0.73
LAYER CBR_MUR_PI
RESISTANCE= 0.48
LAYER CBR_MUR_PH
RESISTANCE= 0.46
LAYER EXPANSEDPO
CONDUCTIVITY= 0.119 : CAPACITY= 1.47 : DENSITY= 27
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INPUTS EQUIPEMENT_EMB ECLAIRAGE_EMB OCCUPATION_EMB OCCUPATION_DEB ECLAIRAGE_DEB EQUIPEMENT_DEB AIRE_EMB AIRE_DEB INFILTRATION_EMB INFILTRATION_DEB QM_AIR_DEB QM_AIR_EMB T_SOUF_DEB RH_SOUF_DEB ;
T_SOUF_EMB RH_SOUF_EMB QM_EAU_PBCH T_EAU_E_PBCH T_AIR_CONS_CH_DEB T_AIR_CONS_FR_DEB T_AIR_LT T_AIR_EXT INFILTRATION_EMBH QM_AIR_COUPHB QM_AIR_COUPBH
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* S c h e d u l e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W a l l s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WALL ME1
LAYERS = ALUMINIUM_MASSLESS
THICKNESS= 0
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL ME2
LAYERS = PLASTERBOA FIBREGLASS ALUMINIUM
THICKNESS= 0.013 0.1 0.005
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL MI2
LAYERS = CLAY AIR_FLUX_HOR_GE25MM MDFBOARD
THICKNESS= 0.05 0 0.03
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 11
WALL PH
LAYERS = PLASTERBOA AIR_FLUX_ASC_GE15MM FIBREGLASS ALUMINIUM
THICKNESS= 0.013 0 0.13 0.005
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL PI
LAYERS = BETON
THICKNESS= 0.2
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 11
WALL CBR_MUR_PB
LAYERS = CBR_MUR_PB
THICKNESS= 0
ABS-FRONT= 0.0001 : ABS-BACK= 0.0001
EPS-FRONT= 0.0001 : EPS-BACK= 0.0001
HFRONT = 0.002 : HBACK= 0.002
WALL CBR_MUR_PI
LAYERS = CBR_MUR_PI
THICKNESS= 0
ABS-FRONT= 0.0001 : ABS-BACK= 0.0001
EPS-FRONT= 0.0001 : EPS-BACK= 0.0001
HFRONT = 0.002 : HBACK= 0.002
WALL CBR_MUR_PH
LAYERS = CBR_MUR_PH
THICKNESS= 0
ABS-FRONT= 0.0001 : ABS-BACK= 0.0001
EPS-FRONT= 0.0001 : EPS-BACK= 0.0001
HFRONT = 0.002 : HBACK= 0.002
WALL PBCH
LAYERS = BETON COUCHE_ACTIVE BETON EXPANSEDPO BETON
THICKNESS= 0.105 0 0.01 0.068 0.2
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = FLOOR : HBACK= 11
WALL PB
LAYERS = BETON BETON EXPANSEDPO BETON
THICKNESS= 0.105 0.01 0.068 0.2
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 11
WALL PB_EXT
LAYERS = BETON BETON EXPANSEDPO BETON
THICKNESS= 0.105 0.01 0.068 0.2
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL PBCH_EXT
LAYERS = BETON COUCHE_ACTIVE BETON EXPANSEDPO BETON
THICKNESS= 0.105 0 0.01 0.068 0.2
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = FLOOR : HBACK= 64
WALL MI1
LAYERS = HEAVYCONCR FIBREGLASS
THICKNESS= 0.2 0.1
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 11
WALL MI4
LAYERS = FIBREGLASS
THICKNESS= 0.05
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 11
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W i n d o w s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WINDOW VE1
WINID=3002 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=0 : WWID=0 : WHEIG=0 : FFRAME=0.18 : UFRAME=100 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.1 : CCISHADE=0.5 : ;
EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW TRANSPARENT
WINID=10001 : HINSIDE=1 : HOUTSIDE=1 : SLOPE=0 : SPACID=5 : WWID=0 : WHEIG=0 : FFRAME=0 : UFRAME=8.17 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : CCISHADE=0.5 : ;
EPSFRAME=0.9 : EPSISHADE=0.9
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* D e f a u l t G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN PERS_ISO02
CONVECTIVE=156 : RADIATIVE=78 : HUMIDITY=0.081
GAIN PERS_ISO05
CONVECTIVE=216 : RADIATIVE=108 : HUMIDITY=0.139
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O t h e r G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN ECL_EMB
CONVECTIVE=INPUT 0.7*ECLAIRAGE_EMB : RADIATIVE=INPUT 0.3*ECLAIRAGE_EMB : HUMIDITY=0
GAIN EQ_EMB
CONVECTIVE=INPUT 0.8*EQUIPEMENT_EMB : RADIATIVE=INPUT 0.2*EQUIPEMENT_EMB : HUMIDITY=0
GAIN ECL_DEB
CONVECTIVE=INPUT 0.7*ECLAIRAGE_DEB : RADIATIVE=INPUT 0.3*ECLAIRAGE_DEB : HUMIDITY=0
GAIN EQ_DEB
CONVECTIVE=INPUT 0.8*EQUIPEMENT_DEB : RADIATIVE=INPUT 0.2*EQUIPEMENT_DEB : HUMIDITY=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m f o r t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n f i l t r a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INFILTRATION INF_EMB
AIRCHANGE=INPUT 1*INFILTRATION_EMB
INFILTRATION INF_DEB
AIRCHANGE=INPUT 1*INFILTRATION_DEB
INFILTRATION INF_EMBH
AIRCHANGE=INPUT 1*INFILTRATION_EMBH
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* V e n t i l a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
VENTILATION VENT_EMB
TEMPERATURE=INPUT 1*T_SOUF_EMB
AIRFLOW=INPUT 1*QM_AIR_EMB
HUMIDITY=INPUT 1*RH_SOUF_EMB
VENTILATION VENT_DEB
TEMPERATURE=INPUT 1*T_SOUF_DEB
AIRFLOW=INPUT 1*QM_AIR_DEB
HUMIDITY=INPUT 1*RH_SOUF_DEB
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o o l i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
COOLING PCL_FR
ON=INPUT 1*T_AIR_CONS_FR_DEB
POWER=999999999
HUMIDITY=100
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* H e a t i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
HEATING PCL_CH
ON=INPUT 1*T_AIR_CONS_CH_DEB
POWER=999999999
HUMIDITY=0
RRAD=0
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONES EMBARQUEMENT DEBARQUEMENT
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O r i e n t a t i o n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ORIENTATIONS N_180_90 S_0_90 E_270_90 W_90_90 E_270_7 H_0_0
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
BUILDING
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e EMBARQUEMENT / A i r n o d e EMBARQUEMENT
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE EMBARQUEMENT
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE EMBARQUEMENT
WALL =ME1 : SURF= 1 : AREA= 0.1 : EXTERNAL : ORI=W_90_90 : FSKY=0.5
WINDOW=VE1 : SURF= 3 : AREA= 116.5 : EXTERNAL : ORI=W_90_90 : FSKY=0.5
WALL =ME2 : SURF= 2 : AREA= 124.1 : EXTERNAL : ORI=W_90_90 : FSKY=0.5
WALL =MI1 : SURF= 4 : AREA= 119.1 : BOUNDARY=INPUT 1*T_AIR_LT
WALL =ME1 : SURF= 10 : AREA= 345.3 : EXTERNAL : ORI=E_270_90 : FSKY=0.5
WALL =PI : SURF= 25 : AREA= 569.6 : ADJACENT=DEBARQUEMENT : ADJ_SURF=24 : BACK
WALL =CBR_MUR_PB : SURF= 29 : LENGTH= 160 : EXTERNAL : ORI=W_90_90 : FSKY=0.5
WALL =CBR_MUR_PI : SURF= 30 : LENGTH= 80 : EXTERNAL : ORI=W_90_90 : FSKY=0.5
WALL =PB : SURF= 27 : AREA= 379 : BOUNDARY=IDENTICAL
WALL =PBCH : SURF= 28 : AREA= 454 : BOUNDARY=IDENTICAL : INTEMP = INPUT 1*T_EAU_E_PBCH : MFLOW = INPUT 0.48*QM_EAU_PBCH : NLOOP = 14 : MFLOWMIN = 2.9 : ASEGSURF = 28 ,36 ,
WALL =PB_EXT : SURF= 34 : AREA= 412 : EXTERNAL : ORI=H_0_0 : FSKY=0
WALL =PBCH_EXT : SURF= 35 : AREA= 494 : EXTERNAL : ORI=H_0_0 : FSKY=0 : INTEMP = INPUT 1*T_EAU_E_PBCH : MFLOW = INPUT 0.52*QM_EAU_PBCH : NLOOP = 14 : MFLOWMIN = 2.9 : ASEGSURF = 35 ,37 ,
WALL =PBCH : SURF= 36 : AREA= 454 : BOUNDARY=IDENTICAL : MFLOW = INPUT 0.48*QM_EAU_PBCH : NLOOP = 14 : MFLOWMIN = 2.9 : ASEGSURF = 28 ,36 ,
WALL =PBCH_EXT : SURF= 37 : AREA= 494 : EXTERNAL : ORI=H_0_0 : FSKY=0 : MFLOW = INPUT 0.52*QM_EAU_PBCH : NLOOP = 14 : MFLOWMIN = 2.9 : ASEGSURF = 35 ,37 ,
WALL =MI4 : SURF= 41 : AREA= 58.2 : BOUNDARY=INPUT 1*T_AIR_EXT
WALL =MI4 : SURF= 42 : AREA= 21 : BOUNDARY=INPUT 1*T_AIR_EXT
WALL =ME1 : SURF= 9 : AREA= 1 : ADJACENT=EMB_HAUT : ADJ_SURF=11 : FRONT
WINDOW=TRANSPARENT : SURF= 12 : AREA= 2686 : ADJACENT=EMB_HAUT : ADJ_SURF=13 : FRONT : ORI=H_0_0
REGIME
GAIN = PERS_ISO02 : SCALE= INPUT 1*OCCUPATION_EMB : GEOPOS= 0
GAIN = ECL_EMB : SCALE= INPUT 1*AIRE_EMB : GEOPOS= 0
GAIN = EQ_EMB : SCALE= INPUT 1*AIRE_EMB : GEOPOS= 0
INFILTRATION= INF_EMB
VENTILATION = VENT_EMB
ADJACENT_UPPER= EMB_HAUT : COUPL= INPUT 1*QM_AIR_COUPHB
CAPACITANCE = 13996.8 : VOLUME= 11664 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e EMBARQUEMENT / A i r n o d e EMB_HAUT
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
AIRNODE EMB_HAUT
WALL =MI2 : SURF= 43 : AREA= 264.2 : ADJACENT=DEBARQUEMENT : ADJ_SURF=44 : BACK
WALL =ME1 : SURF= 45 : AREA= 0.1 : ADJACENT=DEBARQUEMENT : ADJ_SURF=46 : BACK
WINDOW=VE1 : SURF= 47 : AREA= 75.6 : ADJACENT=DEBARQUEMENT : ADJ_SURF=48 : BACK : ORI=S_0_90
WALL =ME1 : SURF= 49 : AREA= 0.1 : ADJACENT=DEBARQUEMENT : ADJ_SURF=50 : BACK
WINDOW=VE1 : SURF= 51 : AREA= 75.6 : ADJACENT=DEBARQUEMENT : ADJ_SURF=52 : BACK : ORI=N_180_90
WALL =PH : SURF= 53 : AREA= 1924.5 : EXTERNAL : ORI=E_270_7 : FSKY=0.996
WALL =CBR_MUR_PH : SURF= 8 : LENGTH= 80 : EXTERNAL : ORI=E_270_7 : FSKY=0.996
WALL =ME1 : SURF= 11 : AREA= 1 : ADJACENT=EMBARQUEMENT : ADJ_SURF=9 : BACK
WINDOW=TRANSPARENT : SURF= 13 : AREA= 2686 : ADJACENT=EMBARQUEMENT : ADJ_SURF=12 : BACK : ORI=H_0_0
REGIME
INFILTRATION= INF_EMBH
ADJACENT_LOWER= EMBARQUEMENT : COUPL= INPUT 1*QM_AIR_COUPBH
CAPACITANCE = 6753.6 : VOLUME= 5628 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e DEBARQUEMENT / A i r n o d e DEBARQUEMENT
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE DEBARQUEMENT
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL
AIRNODE DEBARQUEMENT
WALL =ME1 : SURF= 5 : AREA= 0.18 : EXTERNAL : ORI=W_90_90 : FSKY=0.5
WINDOW=VE1 : SURF= 6 : AREA= 120.2 : EXTERNAL : ORI=W_90_90 : FSKY=0.5
WALL =ME2 : SURF= 7 : AREA= 257.5 : EXTERNAL : ORI=W_90_90 : FSKY=0.5
WALL =ME1 : SURF= 20 : AREA= 0.15 : EXTERNAL : ORI=N_180_90 : FSKY=0.5
WINDOW=VE1 : SURF= 21 : AREA= 22.6 : EXTERNAL : ORI=N_180_90 : FSKY=0.5
WALL =ME1 : SURF= 22 : AREA= 0.15 : EXTERNAL : ORI=S_0_90 : FSKY=0.5
WINDOW=VE1 : SURF= 23 : AREA= 22.6 : EXTERNAL : ORI=S_0_90 : FSKY=0.5
WALL =PI : SURF= 24 : AREA= 569.6 : ADJACENT=EMBARQUEMENT : ADJ_SURF=25 : FRONT
WALL =PH : SURF= 26 : AREA= 762.56 : EXTERNAL : ORI=E_270_7 : FSKY=0.996
WALL =CBR_MUR_PH : SURF= 32 : LENGTH= 80 : EXTERNAL : ORI=W_90_90 : FSKY=0.5
WALL =CBR_MUR_PI : SURF= 33 : LENGTH= 80 : EXTERNAL : ORI=W_90_90 : FSKY=0.5
WALL =MI4 : SURF= 38 : AREA= 13.05 : BOUNDARY=INPUT 1*T_AIR_EXT
WALL =MI4 : SURF= 39 : AREA= 14.14 : BOUNDARY=INPUT 1*T_AIR_EXT
WALL =PI : SURF= 40 : AREA= 192.97 : BOUNDARY=INPUT 1*T_AIR_LT
WALL =MI2 : SURF= 44 : AREA= 264.2 : ADJACENT=EMB_HAUT : ADJ_SURF=43 : FRONT
WALL =ME1 : SURF= 46 : AREA= 0.1 : ADJACENT=EMB_HAUT : ADJ_SURF=45 : FRONT
WINDOW=VE1 : SURF= 48 : AREA= 75.6 : ADJACENT=EMB_HAUT : ADJ_SURF=47 : FRONT : ORI=S_0_90
WALL =ME1 : SURF= 50 : AREA= 0.1 : ADJACENT=EMB_HAUT : ADJ_SURF=49 : FRONT
WINDOW=VE1 : SURF= 52 : AREA= 75.6 : ADJACENT=EMB_HAUT : ADJ_SURF=51 : FRONT : ORI=N_180_90
REGIME
GAIN = PERS_ISO05 : SCALE= INPUT 1*OCCUPATION_DEB : GEOPOS= 0
GAIN = ECL_DEB : SCALE= INPUT 1*AIRE_DEB : GEOPOS= 0
GAIN = EQ_DEB : SCALE= INPUT 1*AIRE_DEB : GEOPOS= 0
INFILTRATION= INF_DEB
VENTILATION = VENT_DEB
COOLING = PCL_FR
HEATING = PCL_CH
CAPACITANCE = 3886.8 : VOLUME= 3239 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O u t p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
OUTPUTS
TRANSFER : TIMEBASE=1.000
DEFAULT
AIRNODES = EMBARQUEMENT
NTYPES = 5 : QVENT - sensible ventilation energy gain of airnode
= 4 : QINF - sensible infiltration energy gain of airnode
= 58 : SURF = 28, 35, 36, 37, : TOFL - fluid outlet temperature of active layer
= 59 : SURF = 28, 35, 36, 37, : QALFL - energy input by fluid of active layer
= 7 : QGCONV - internal convective gains of airnode
= 13 : QGRAD - defined internal radiative gain of airnode (Rad, gains are distributed over zones!)
= 12 : QSOLTR - total shortwave solar radiation transmitted through external windows of airnode (but not kept 100 % in airnode)
= 74 : QTSPAS - total solar radiation passing (trans+abs) the glass surface of external windows of airnode
= 75 : QTSABS - total solar radiation absorbed at all inside surfaces of airnode
= 9 : RELHUM - relativ humidity of airnode air
AIRNODES = DEBARQUEMENT
NTYPES = 4 : QINF - sensible infiltration energy gain of airnode
= 30 : QHEAT - sensible heating demand of airnode (positive values)
= 31 : QCOOL - sensible cooling demand of airnode (positive values)
= 5 : QVENT - sensible ventilation energy gain of airnode
= 7 : QGCONV - internal convective gains of airnode
= 12 : QSOLTR - total shortwave solar radiation transmitted through external windows of airnode (but not kept 100 % in airnode)
= 13 : QGRAD - defined internal radiative gain of airnode (Rad, gains are distributed over zones!)
= 74 : QTSPAS - total solar radiation passing (trans+abs) the glass surface of external windows of airnode
= 75 : QTSABS - total solar radiation absorbed at all inside surfaces of airnode
= 9 : RELHUM - relativ humidity of airnode air
AIRNODES = EMB_HAUT
NTYPES = 6 : QCOUP - sensible coupling energy gain of airnode
= 12 : QSOLTR - total shortwave solar radiation transmitted through external windows of airnode (but not kept 100 % in airnode)
= 13 : QGRAD - defined internal radiative gain of airnode (Rad, gains are distributed over zones!)
= 7 : QGCONV - internal convective gains of airnode
= 4 : QINF - sensible infiltration energy gain of airnode
= 9 : RELHUM - relativ humidity of airnode air
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* E n d
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
END
_EXTENSION_WINPOOL_START_
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS 15 WINDOW LIB
Desc : LowSHGC,Ar, silber1.3 38/30
Window ID : 3002
Tilt : 90.0
Glazings : 2
Frame : 11 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1219.2 mm
Total Width : 914.4 mm
Glass Height: 1079.5 mm
Glass Width : 774.7 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Argon 16.0 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.226 0.227 0.223 0.218 0.211 0.199 0.173 0.125 0.056 0.000 0.186
Abs1 0.520 0.525 0.530 0.532 0.529 0.525 0.521 0.496 0.373 0.001 0.509
Abs2 0.045 0.046 0.046 0.047 0.048 0.048 0.046 0.040 0.028 0.000 0.045
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.209 0.202 0.201 0.203 0.212 0.228 0.259 0.338 0.543 0.999 0.251
Rbsol 0.226 0.221 0.219 0.220 0.227 0.242 0.281 0.375 0.575 1.000 0.271
Tvis 0.383 0.385 0.380 0.373 0.363 0.344 0.301 0.219 0.102 0.000 0.320
Rfvis 0.167 0.160 0.158 0.161 0.171 0.189 0.224 0.310 0.526 0.999 0.214
Rbvis 0.150 0.144 0.143 0.147 0.160 0.188 0.249 0.387 0.646 1.000 0.226
SHGC 0.298 0.300 0.297 0.293 0.286 0.274 0.246 0.192 0.104 0.000 0.257
SC: 0.30
Layer ID# 9025 9026 0 0 0 0
Tir 0.000 0.000 0 0 0 0
Emis F 0.840 0.838 0 0 0 0
Emis B 0.110 0.838 0 0 0 0
Thickness(mm) 4.0 6.0 0 0 0 0
Cond(W/m2-C ) 225.0 150.0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.24 7.60 1.47 1.47 1.22 1.22 1.26 1.26 1.37 1.37
0 6.71 25.47 3.21 7.62 1.55 1.55 1.26 1.26 1.30 1.30 1.43 1.43
783 0.00 12.25 3.71 6.92 1.32 1.32 1.40 1.40 1.55 1.55 1.70 1.70
783 6.71 25.47 3.47 6.63 1.46 1.46 1.35 1.35 1.45 1.45 1.64 1.64
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS 14.2 WINDOW LIB
Desc : No glazing = open
Window ID : 10001
Tilt : 90.0
Glazings : 1
Frame : 11 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1219.2 mm
Total Width : 914.4 mm
Glass Height: 1079.5 mm
Glass Width : 774.7 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 0 0 0 0 0 0 0 0 0
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.999
Abs1 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.001 0.000 0.001
Abs2 0 0 0 0 0 0 0 0 0 0 0
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Rbsol 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Tvis 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.999
Rfvis 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Rbvis 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
SHGC 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.000 1.000
SC: 1.0
Layer ID# 9052 0 0 0 0 0
Tir 0.000 0 0 0 0 0
Emis F 1.000 0 0 0 0 0
Emis B 1.000 0 0 0 0 0
Thickness(mm) 0.001 0 0 0 0 0
Cond(W/m2-C ) 999.0 0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.42 8.23 5.27 5.27 4.95 4.95 4.94 4.94 5.53 5.53
0 6.71 25.47 3.33 8.29 6.26 6.26 5.73 5.73 5.68 5.68 6.46 6.46
783 0.00 12.25 3.49 8.17 5.25 5.25 4.58 4.58 5.24 5.24 5.66 5.66
783 6.71 25.47 3.37 8.27 6.25 6.25 5.53 5.53 5.95 5.95 6.57 6.57
*** END OF LIBRARY ***
***************************************************************************************************
*WinID Description Design U-Value g-value T-sol Rf-sol T-vis
***************************************************************************************************
3002 LowSHGC,Ar, silber1.3 38/30 4/16/6 1.3 0.298 0.226 0.209 0.383
10001 No glazing = open 0.001 5.68 1 1 0 1
_EXTENSION_WINPOOL_END_
_EXTENSION_BuildingGeometry_START_
_EXTENSION_BuildingGeometry_END_
_EXTENSION_ExternalShadingGeometry_START_
_EXTENSION_ExternalShadingGeometry_END_
_EXTENSION_GeoPositionGeometry_START_
_EXTENSION_GeoPositionGeometry_END_
***** WALL TRANSFERFUNCTION CALCULATIONS *****
---------- WALL TYPE ME1 ----------
THERMAL CONDUCTANCE, U= 1538.46153 kJ/h m2K; U-Wert= 5.80248 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.5384615E+03 1.5384615E+03 1.5384615E+03 1.0000000E+00
SUM 1.5384615E+03 1.5384615E+03 1.5384615E+03 1.0000000E+00
---------- WALL TYPE ME2 ----------
THERMAL CONDUCTANCE, U= 1.40706 kJ/h m2K; U-Wert= 0.36650 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.3632320E+01 1.1369885E+00 1.0265639E+01 1.0000000E+00
1 -1.2225318E+01 2.7006440E-01 -8.8586109E+00 -4.3908298E-06
2 5.2932947E-05 1.7942332E-06 2.6958827E-05
SUM 1.4070547E+00 1.4070547E+00 1.4070547E+00 9.9999561E-01
---------- WALL TYPE MI2 ----------
THERMAL CONDUCTANCE, U= 7.76978 kJ/h m2K; U-Wert= 1.57895 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 2.2356831E+01 1.1054900E+00 1.2164296E+02 1.0000000E+00
1 -1.8674251E+01 4.1390734E+00 -1.3032643E+02 -2.3504007E-01
2 2.4004123E+00 7.8042099E-01 1.4992060E+01 1.1022870E-02
3 -5.3773957E-02 4.2342213E-03 -2.7936444E-01 -3.6434496E-08
4 1.0014868E-07 1.5465853E-08 9.1024771E-07
SUM 6.0292186E+00 6.0292186E+00 6.0292186E+00 7.7598277E-01
---------- WALL TYPE PH ----------
THERMAL CONDUCTANCE, U= 1.03838 kJ/h m2K; U-Wert= 0.27496 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.3384754E+01 7.3548931E-01 1.0010966E+01 1.0000000E+00
1 -1.2356085E+01 3.0197159E-01 -8.9793077E+00 -7.4126580E-04
2 8.9461936E-03 1.5364332E-04 5.9558120E-03
SUM 1.0376145E+00 1.0376145E+00 1.0376145E+00 9.9925873E-01
---------- WALL TYPE PI ----------
THERMAL CONDUCTANCE, U= 41.40000 kJ/h m2K; U-Wert= 3.89171 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.5906556E+02 2.1194617E+00 1.5906556E+02 1.0000000E+00
1 -1.6634166E+02 1.5282965E+01 -1.6634166E+02 -4.6055785E-01
2 3.0760911E+01 5.4311412E+00 3.0760911E+01 1.4392246E-02
3 -5.5652735E-01 9.4873864E-02 -5.5652735E-01 -6.6897974E-06
4 1.8477227E-04 2.4858252E-05 1.8477227E-04
SUM 2.2928467E+01 2.2928467E+01 2.2928467E+01 5.5382771E-01
---------- WALL TYPE CBR_MUR_PB ----------
THERMAL CONDUCTANCE, U= 1.36986 kJ/h m2K; U-Wert= 0.35740 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.3698630E+00 1.3698630E+00 1.3698630E+00 1.0000000E+00
SUM 1.3698630E+00 1.3698630E+00 1.3698630E+00 1.0000000E+00
---------- WALL TYPE CBR_MUR_PI ----------
THERMAL CONDUCTANCE, U= 2.08333 kJ/h m2K; U-Wert= 0.52687 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 2.0833334E+00 2.0833334E+00 2.0833334E+00 1.0000000E+00
SUM 2.0833334E+00 2.0833334E+00 2.0833334E+00 1.0000000E+00
---------- WALL TYPE CBR_MUR_PH ----------
THERMAL CONDUCTANCE, U= 2.17391 kJ/h m2K; U-Wert= 0.54765 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 2.1739130E+00 2.1739130E+00 2.1739130E+00 1.0000000E+00
SUM 2.1739130E+00 2.1739130E+00 2.1739130E+00 1.0000000E+00
---------- WALL TYPE PBCH_W1 ----------
THERMAL CONDUCTANCE, U= 78.85714 kJ/h m2K; U-Wert= 4.63710 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.6052988E+02 3.9184295E+01 1.6052988E+02 1.0000000E+00
1 -8.6767996E+01 3.5665852E+01 -8.6767996E+01 -4.5576958E-02
2 1.5012093E+00 4.1294205E-01 1.5012093E+00 1.9657182E-07
3 -3.9643928E-06 7.2743142E-07 -3.9643928E-06
SUM 7.5263090E+01 7.5263090E+01 7.5263090E+01 9.5442324E-01
---------- WALL TYPE PBCH_W2 ----------
THERMAL CONDUCTANCE, U= 1.67563 kJ/h m2K; U-Wert= 0.43132 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.5906534E+02 2.9341467E-03 2.6584968E+01 1.0000000E+00
1 -2.4559482E+02 1.0603865E-01 -5.0318652E+01 -9.5761749E-01
2 9.2981164E+01 1.4963476E-01 2.7120402E+01 1.2507658E-01
3 -6.2026466E+00 2.0398141E-02 -3.1278092E+00 -8.2366695E-04
4 3.0215028E-02 2.1501686E-04 2.0336773E-02 1.0223236E-06
5 -3.2677334E-05 1.2310686E-07 -2.4738704E-05
SUM 2.7922083E-01 2.7922083E-01 2.7922083E-01 1.6663645E-01
---------- WALL TYPE PB ----------
THERMAL CONDUCTANCE, U= 1.64076 kJ/h m2K; U-Wert= 0.42299 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.5906534E+02 1.4195280E-05 1.5841244E+02 1.0000000E+00
1 -3.2903623E+02 8.4916727E-03 -3.3703267E+02 -1.4821907E+00
2 2.2207870E+02 6.0730238E-02 2.2505797E+02 6.2908374E-01
3 -5.5394988E+01 5.3279719E-02 -4.9949931E+01 -6.8077934E-02
4 3.4440663E+00 7.6946753E-03 3.6715735E+00 6.4913880E-04
5 -2.6579295E-02 1.6800007E-04 -2.9063356E-02 -1.9151904E-06
6 6.7201195E-05 4.8839073E-07 6.6598310E-05
7 -5.0458781E-08 1.4386333E-10 -4.3771117E-08
SUM 1.3037899E-01 1.3037899E-01 1.3037899E-01 7.9462349E-02
---------- WALL TYPE PB_EXT ----------
THERMAL CONDUCTANCE, U= 1.64076 kJ/h m2K; U-Wert= 0.42299 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.5906534E+02 1.4195280E-05 1.5841244E+02 1.0000000E+00
1 -3.2903623E+02 8.4916727E-03 -3.3703267E+02 -1.4821907E+00
2 2.2207870E+02 6.0730238E-02 2.2505797E+02 6.2908374E-01
3 -5.5394988E+01 5.3279719E-02 -4.9949931E+01 -6.8077934E-02
4 3.4440663E+00 7.6946753E-03 3.6715735E+00 6.4913880E-04
5 -2.6579295E-02 1.6800007E-04 -2.9063356E-02 -1.9151904E-06
6 6.7201195E-05 4.8839073E-07 6.6598310E-05
7 -5.0458781E-08 1.4386333E-10 -4.3771117E-08
SUM 1.3037899E-01 1.3037899E-01 1.3037899E-01 7.9462349E-02
---------- WALL TYPE PBCH_EXT_W1 ----------
THERMAL CONDUCTANCE, U= 78.85714 kJ/h m2K; U-Wert= 4.63710 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.6052988E+02 3.9184295E+01 1.6052988E+02 1.0000000E+00
1 -8.6767996E+01 3.5665852E+01 -8.6767996E+01 -4.5576958E-02
2 1.5012093E+00 4.1294205E-01 1.5012093E+00 1.9657182E-07
3 -3.9643928E-06 7.2743142E-07 -3.9643928E-06
SUM 7.5263090E+01 7.5263090E+01 7.5263090E+01 9.5442324E-01
---------- WALL TYPE PBCH_EXT_W2 ----------
THERMAL CONDUCTANCE, U= 1.67563 kJ/h m2K; U-Wert= 0.43132 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.5906534E+02 2.9341467E-03 2.6584968E+01 1.0000000E+00
1 -2.4559482E+02 1.0603865E-01 -5.0318652E+01 -9.5761749E-01
2 9.2981164E+01 1.4963476E-01 2.7120402E+01 1.2507658E-01
3 -6.2026466E+00 2.0398141E-02 -3.1278092E+00 -8.2366695E-04
4 3.0215028E-02 2.1501686E-04 2.0336773E-02 1.0223236E-06
5 -3.2677334E-05 1.2310686E-07 -2.4738704E-05
SUM 2.7922083E-01 2.7922083E-01 2.7922083E-01 1.6663645E-01
---------- WALL TYPE MI1 ----------
THERMAL CONDUCTANCE, U= 1.37528 kJ/h m2K; U-Wert= 0.35873 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.7662044E+00 4.3589481E-03 1.2000009E+02 1.0000000E+00
1 -2.0703182E+00 1.0010032E-01 -1.8720428E+02 -9.7380229E-01
2 5.6990028E-01 1.0534881E-01 7.2461139E+01 1.3412031E-01
3 -4.6649253E-02 9.5515003E-03 -5.0570661E+00 -7.8620134E-04
4 2.6392697E-04 4.1548363E-05 1.9516051E-02 3.7076854E-08
5 -1.2200798E-08 3.0559431E-09 -6.9719809E-07
SUM 2.1940113E-01 2.1940113E-01 2.1940113E-01 1.5953186E-01
---------- WALL TYPE MI4 ----------
THERMAL CONDUCTANCE, U= 2.88000 kJ/h m2K; U-Wert= 0.70423 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 3.0480000E+00 2.7960000E+00 3.0480000E+00 1.0000000E+00
1 -1.6800000E-01 8.4000000E-02 -1.6800000E-01
SUM 2.8800000E+00 2.8800000E+00 2.8800000E+00 1.0000000E+00
************* REQUIRED INPUTS *************
*:InpNR | Label | UNIT | INPUT DESCRIPTION | Old label
* | 1 | TAMB | C | AMBIENT TEMPERATURE | TAMB
* | 2 | RELHUMAMB | % | RELATIVE AMBIENT HUMIDITY | ARELHUM
* | 3 | TSKY | C | FIKTIVE SKY TEMPERATURE | TSKY
* | 4 | TSGRD | C | GROUND TEMPERATURE | TGRD
* | 5 | AZEN | degrees | SOLAR ZENITH ANGLE | AZEN
* | 6 | AAZM | degrees | SOLAR AZIMUTH ANGLE | AAZM
* | 7 | IT_N_180_90 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION N_180_90 | ITN_180_90
* | 8 | IT_S_0_90 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION S_0_90 | ITS_0_90
* | 9 | IT_E_270_90 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION E_270_90 | ITE_270_90
* | 10 | IT_W_90_90 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION W_90_90 | ITW_90_90
* | 11 | IT_E_270_7 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION E_270_7 | ITE_270_7
* | 12 | IT_H_0_0 | kJ/hr.m^2 | INCIDENT RADIATION FOR ORIENTATION H_0_0 | ITH_0_0
* | 13 | IB_N_180_90 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION N_180_90 | IBN_180_90
* | 14 | IB_S_0_90 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION S_0_90 | IBS_0_90
* | 15 | IB_E_270_90 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION E_270_90 | IBE_270_90
* | 16 | IB_W_90_90 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION W_90_90 | IBW_90_90
* | 17 | IB_E_270_7 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION E_270_7 | IBE_270_7
* | 18 | IB_H_0_0 | kJ/hr.m^2 | INCIDENT BEAM RADIATION FOR ORIENTATION H_0_0 | IBH_0_0
* | 19 | AI_N_180_90 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION N_180_90 | AIN_180_90
* | 20 | AI_S_0_90 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION S_0_90 | AIS_0_90
* | 21 | AI_E_270_90 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION E_270_90 | AIE_270_90
* | 22 | AI_W_90_90 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION W_90_90 | AIW_90_90
* | 23 | AI_E_270_7 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION E_270_7 | AIE_270_7
* | 24 | AI_H_0_0 | degrees | ANGLE OF INCIDENCE FOR ORIENTATION H_0_0 | AIH_0_0
* | 25 | GRDREF | - | GROUND REFLECTION FOR SKY DIFFUSE RADIATION SHADING | GRDREF
* | 26 | EQUIPEMENT_EMB | any | INPUT | EQUIPEMENT
* | 27 | ECLAIRAGE_EMB | any | INPUT | ECLAIRAGE_
* | 28 | OCCUPATION_EMB | any | INPUT | OCCUPATION
* | 29 | OCCUPATION_DEB | any | INPUT | OCCUPATION
* | 30 | ECLAIRAGE_DEB | any | INPUT | ECLAIRAGE_
* | 31 | EQUIPEMENT_DEB | any | INPUT | EQUIPEMENT
* | 32 | AIRE_EMB | any | INPUT | AIRE_EMB
* | 33 | AIRE_DEB | any | INPUT | AIRE_DEB
* | 34 | INFILTRATION_EMB | any | INPUT | INFILTRATI
* | 35 | INFILTRATION_DEB | any | INPUT | INFILTRATI
* | 36 | QM_AIR_DEB | any | INPUT | QM_AIR_DEB
* | 37 | QM_AIR_EMB | any | INPUT | QM_AIR_EMB
* | 38 | T_SOUF_DEB | any | INPUT | T_SOUF_DEB
* | 39 | RH_SOUF_DEB | any | INPUT | RH_SOUF_DE
* | 40 | T_SOUF_EMB | any | INPUT | T_SOUF_EMB
* | 41 | RH_SOUF_EMB | any | INPUT | RH_SOUF_EM
* | 42 | QM_EAU_PBCH | any | INPUT | QM_EAU_PBC
* | 43 | T_EAU_E_PBCH | any | INPUT | T_EAU_E_PB
* | 44 | T_AIR_CONS_CH_DEB | any | INPUT | T_AIR_CONS
* | 45 | T_AIR_CONS_FR_DEB | any | INPUT | T_AIR_CONS
* | 46 | T_AIR_LT | any | INPUT | T_AIR_LT
* | 47 | T_AIR_EXT | any | INPUT | T_AIR_EXT
* | 48 | INFILTRATION_EMBH | any | INPUT | INFILTRATI
* | 49 | QM_AIR_COUPHB | any | INPUT | QM_AIR_COU
* | 50 | QM_AIR_COUPBH | any | INPUT | QM_AIR_COU
************* DESIRED OUTPUTS *************
*:OutNr | Label | Unit | ZNr | Airnode | SurfNr| OUTPUT DESCRIPTION | old label
* | 1 | TAIR_EMBARQUEMENT | C | 1 | EMBARQUEMENT | | air temperature of airnode | TAIR 1
* | 2 | TAIR_EMB_HAUT | C | 1 | EMB_HAUT | | air temperature of airnode | TAIR 1
* | 3 | TAIR_DEBARQUEMENT | C | 2 | DEBARQUEMENT | | air temperature of airnode | TAIR 2
* | 4 | QSENS_EMBARQUEMENT | kJ/hr | 1 | EMBARQUEMENT | | sens. energy demand of airnode, heating(-) ,cooling(+) | QSENS 1
* | 5 | QSENS_EMB_HAUT | kJ/hr | 1 | EMB_HAUT | | sens. energy demand of airnode, heating(-) ,cooling(+) | QSENS 1
* | 6 | QSENS_DEBARQUEMENT | kJ/hr | 2 | DEBARQUEMENT | | sens. energy demand of airnode, heating(-) ,cooling(+) | QSENS 2
* | 7 | QVENT_EMBARQUEMENT | kJ/hr | 1 | EMBARQUEMENT | | sens. ventilation energy gain of airnode | QVENT 1
* | 8 | QINF_EMBARQUEMENT | kJ/hr | 1 | EMBARQUEMENT | | sens. infiltration energy gain of airnode | QINF 1
* | 9 | TOFL_S28 | C | 1 | EMBARQUEMENT | 28 | fluid outlet temperature of active layer ->WALL=PBCH_W1:IDENTICAL BOUNDARY | TOFL 28
* | 10 | TOFL_S35 | C | 1 | EMBARQUEMENT | 35 | fluid outlet temperature of active layer ->WALL=PBCH_EXT_W1:ORI=H_0_0 | TOFL 35
* | 11 | TOFL_S36 | C | 1 | EMBARQUEMENT | 36 | fluid outlet temperature of active layer ->WALL=PBCH_W1:IDENTICAL BOUNDARY | TOFL 36
* | 12 | TOFL_S37 | C | 1 | EMBARQUEMENT | 37 | fluid outlet temperature of active layer ->WALL=PBCH_EXT_W1:ORI=H_0_0 | TOFL 37
* | 13 | QALFL_S28 | kJ/hr | 1 | EMBARQUEMENT | 28 | energy input by fluid of active layer ->WALL=PBCH_W1:IDENTICAL BOUNDARY | QALFL 28
* | 14 | QALFL_S35 | kJ/hr | 1 | EMBARQUEMENT | 35 | energy input by fluid of active layer ->WALL=PBCH_EXT_W1:ORI=H_0_0 | QALFL 35
* | 15 | QALFL_S36 | kJ/hr | 1 | EMBARQUEMENT | 36 | energy input by fluid of active layer ->WALL=PBCH_W1:IDENTICAL BOUNDARY | QALFL 36
* | 16 | QALFL_S37 | kJ/hr | 1 | EMBARQUEMENT | 37 | energy input by fluid of active layer ->WALL=PBCH_EXT_W1:ORI=H_0_0 | QALFL 37
* | 17 | QGCONV_EMBARQUEMENT | kJ/hr | 1 | EMBARQUEMENT | | internal convective gains of airnode | QGCONV 1
* | 18 | QGRAD_EMBARQUEMENT | kJ/hr | 1 | EMBARQUEMENT | | internal radiative gain | QGRAD 1
* | 19 | QSOLTR_EMBARQUEMENT | kJ/hr | 1 | EMBARQUEMENT | | total s-wave solar radiation through ext. windows of airnode (but not kept 100 % in airnode) | QSOLTR 1
* | 20 | QTSPAS_EMBARQUEMENT | kJ/hr | 1 | EMBARQUEMENT | | total solar rad. passing from outside surface of ext. windows | QTSPAS 1
* | 21 | QTSABS_EMBARQUEMENT | kJ/hr | 1 | EMBARQUEMENT | | total solar rad. absorbed at inside surfaces of airnode | QTSABS 1
* | 22 | RELHUM_EMBARQUEMENT | % | 1 | EMBARQUEMENT | | relativ humidity of airnode air | RELHUM 1
* | 23 | QINF_DEBARQUEMENT | kJ/hr | 2 | DEBARQUEMENT | | sens. infiltration energy gain of airnode | QINF 2
* | 24 | QHEAT_DEBARQUEMENT | kJ/hr | 2 | DEBARQUEMENT | | heating demand | QHEAT 2
* | 25 | QCOOL_DEBARQUEMENT | kJ/hr | 2 | DEBARQUEMENT | | cooling demand | QCOOL 2
* | 26 | QVENT_DEBARQUEMENT | kJ/hr | 2 | DEBARQUEMENT | | sens. ventilation energy gain of airnode | QVENT 2
* | 27 | QGCONV_DEBARQUEMENT | kJ/hr | 2 | DEBARQUEMENT | | internal convective gains of airnode | QGCONV 2
* | 28 | QSOLTR_DEBARQUEMENT | kJ/hr | 2 | DEBARQUEMENT | | total s-wave solar radiation through ext. windows of airnode (but not kept 100 % in airnode) | QSOLTR 2
* | 29 | QGRAD_DEBARQUEMENT | kJ/hr | 2 | DEBARQUEMENT | | internal radiative gain | QGRAD 2
* | 30 | QTSPAS_DEBARQUEMENT | kJ/hr | 2 | DEBARQUEMENT | | total solar rad. passing from outside surface of ext. windows | QTSPAS 2
* | 31 | QTSABS_DEBARQUEMENT | kJ/hr | 2 | DEBARQUEMENT | | total solar rad. absorbed at inside surfaces of airnode | QTSABS 2
* | 32 | RELHUM_DEBARQUEMENT | % | 2 | DEBARQUEMENT | | relativ humidity of airnode air | RELHUM 2
* | 33 | QCOUP_EMB_HAUT | kJ/hr | 1 | EMB_HAUT | | sens. coupling energy gain of airnode | QCOUP 1
* | 34 | QSOLTR_EMB_HAUT | kJ/hr | 1 | EMB_HAUT | | total s-wave solar radiation through ext. windows of airnode (but not kept 100 % in airnode) | QSOLTR 1
* | 35 | QGRAD_EMB_HAUT | kJ/hr | 1 | EMB_HAUT | | internal radiative gain | QGRAD 1
* | 36 | QGCONV_EMB_HAUT | kJ/hr | 1 | EMB_HAUT | | internal convective gains of airnode | QGCONV 1
* | 37 | QINF_EMB_HAUT | kJ/hr | 1 | EMB_HAUT | | sens. infiltration energy gain of airnode | QINF 1
* | 38 | RELHUM_EMB_HAUT | % | 1 | EMB_HAUT | | relativ humidity of airnode air | RELHUM 1
*** THERMAL CONDUCTANCE OF USED WALL TYPES ***
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
WALL ME1 U= 5.802 W/m2K
WALL ME2 U= 0.366 W/m2K
WALL MI2 U= 1.579 W/m2K
WALL PH U= 0.275 W/m2K
WALL PI U= 3.892 W/m2K
WALL CBR_MUR_PB U= 0.357 W/m2K
WALL CBR_MUR_PI U= 0.527 W/m2K
WALL CBR_MUR_PH U= 0.548 W/m2K
WALL PBCH_W1 U= 4.637 W/m2K
WALL PBCH_W2 U= 0.431 W/m2K
WALL PB U= 0.423 W/m2K
WALL PB_EXT U= 0.423 W/m2K
WALL PBCH_EXT_W1 U= 4.637 W/m2K
WALL PBCH_EXT_W2 U= 0.431 W/m2K
WALL MI1 U= 0.359 W/m2K
WALL MI4 U= 0.704 W/m2K
More information about the TRNSYS-users
mailing list