In the 13 kg/m²h the m² are related to the wall/ceiling area and not to
the pipe-diameter.
For the conversion to kg/s You may not use the pipe-area (7.1e-5 m²) but
Your wall area.
With kind regards,
Matthias Kersken
---
Dipl.-Ing. Matthias Kersken
Wissenschaftlicher Mitarbeiter / Abteilung Energiesysteme
Fraunhofer-Institut für Bauphysik
Institutsteil Holzkirchen
Fraunhoferstraße 10
83626 Valley
eMail: Matthias.Kersken at ibp.fraunhofer.de
Telefon 08024 / 643-204
Telefax 08024 / 643-366
www.ibp.fraunhofer.de
Dipl.-Ing. Matthias Kersken
Research Associate / Department Energy Systems
Fraunhofer Institute for Building Physics
Branch Holzkirchen
Fraunhoferstraße 10
D-83626 Valley
eMail: <mailto:Matthias.Kersken at ibp.fraunhofer.de>
Matthias.Kersken at ibp.fraunhofer.de
Phone +49 8024 / 643-204
Fax +49 8024 / 643-366
<http://www.ibp.fraunhofer.de> www.ibp.fraunhofer.de
---
Von: Devin Rohan [mailto:dmrohan at gmail.com]
Gesendet: Sonntag, 12. Juni 2011 02:10
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] TRNSYS Active Layer Flowrate
The Type 56 manual suggests that the specific mass flow rate be greater than
13 kg/h-m^2. Say I wanted to convert this to mass flow rate in kg/s and the
fluid was flowing through a 3/8" (or 9.525 mm) inside diameter pipe. Here's
what I'm doing...
A_pipe= (pi*D^2)/4 = (pi*.009525^2)/4= 7.1256 E-5 m^2
13 kg/h-m^2 x (7.1256 E-5 m^2) x (h / 3600 sec) = 2.573 E-7 kg/s
This seems like an awfully low mass flow rate, since what I've seen in
literature for floor heating applications is around .05 kg/s. Am I missing
something here?
--
Devin M. Rohan
drohan at purdue.edu
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110614/53d439d3/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smime.p7s
Type: application/pkcs7-signature
Size: 7103 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110614/53d439d3/attachment-0001.bin>
More information about the TRNSYS-users
mailing list