[TRNSYS-users] Problem to make a building model
    Aaron Danenberg 
    ajdanenberg at gmail.com
       
    Mon Jul 18 07:16:08 PDT 2011
    
    
  
Leona,
 
Did you create the user defined schedule "BUEROKZIMMER" (unless this
schedule is part of a non-English version of a TRNSYS library) in a
different building project?  I would manually edit the bui file in a text
editor.  I found it was quicker for some things compared to using TRNBUILD.
If you have used this schedule in a different simulation you can just copy
and paste the code into your current bui file.  After that I would save this
schedule in a user library.  Also did you or someone else create this
schedule on a different computer, the machine you are currently using have
may not have it loaded.  What I believe is happening is that you are calling
a schedule that is not saved in any user libraries in TRNSYS, or not stored
in the right place.  When you open the file in text editor you will need to
edit this section.
 
*  S c h e d u l e s
*---------------------------------------------------------------------------
----------------------------------------------------------------------------
-------------------------------------------------
SCHEDULE WORKDAY
HOURS =0.000 8.000 18.000 24.0
VALUES=0 1. 0 0 
SCHEDULE WEEKEND
HOURS =0.000 1.000 24.0
VALUES=0 0 0 
SCHEDULE WORKLIGHT
HOURS =0.000 8.000 18.000 24.0
VALUES=0 1. 0 0 
SCHEDULE USE
DAYS=1 2 3 4 5 6 7
HOURLY=WORKDAY WORKDAY WORKDAY WORKDAY WORKDAY WEEKEND WEEKEND
SCHEDULE LIGHT
DAYS=1 2 3 4 5 6 7
HOURLY=WORKLIGHT WORKLIGHT WORKLIGHT WORKLIGHT WORKLIGHT WEEKEND WEEKEND
 
Hope this helps.
 
Aaron Danenberg
 
From: 瞳瞳 [mailto:ilyt2000 at gmail.com] 
Sent: Monday, July 18, 2011 9:26 AM
To: trnsys-users at cae.wisc.edu
Subject: [TRNSYS-users] Problem to make a building model
 
Dear all,
 
I am trying to make a simple room model to caluate the cold load. Now i have
inputed all the data in the TRNBild and when i ran it, i got the information
: Scheduletype<BUEROKZIMMER> not found.  It is a daily schedule , and for
the office room. 
 
My questions are
1. How can i solve the TRNBild problem?
2. What is the next step? make it as a external file in Type 56? 
3. Which Types or componentes do  i need to run the calculation. Type 109?
Type 25? 
 
Thanks a lot for everyone who could explain me that. 
  
Best Regards
 
Leona