[TRNSYS-users] Monthly/Yearly Schedules
Mohamed Ayman
ayman.mohamed at aalto.fi
Thu Jul 14 06:54:42 PDT 2011
Hi Rebecca
To enter seasonally or monthly schedules use external schedules as type 14 and coupling with another Type 14 also to define the time you want.
for example:
the occupancy schedule as this from 0 to hour 24 for Jan to March as 50% ( or any detail through day )that is Type14 called as (OCC_JAN_March) and from 0 to 24 for April to Dec. an 100 % ( or any detail through day ) that is Type14 called as (OCC_April_Dec)
then use other types 14 to define the period as
1- from 0 to 2160 ( the period of Jan to March) as 1 and from 2160 to 8760 ( the period of Aprilto Dec )as 0 define that as ( time_Jan_March)
2- from 0 to 2160 ( the period of Jan to March) as 0 and from 2160 to 8760 ( the period of Aprilto Dec )as 1 define that as ( time_April_Dec)
then use Equation to define Occ = Occ_jan_March * time_Jan_March +OCC_April_Dec*time_April_Dec
--
Regards
Ayman Mohamed
________________________________
From: trnsys-users-bounces at cae.wisc.edu [trnsys-users-bounces at cae.wisc.edu] on behalf of Rebecca Ward [rmw61 at cam.ac.uk]
Sent: Thursday, July 14, 2011 12:20 PM
To: trnsys-users at cae.wisc.edu
Subject: [TRNSYS-users] Monthly/Yearly Schedules
Hi,
I’m modelling a building using Type56 and the occupancy schedules vary through the year (it’s a college building and students are there for 3-month blocks, with vacations in between). Is there any way of including this as a schedule? The only way I can think of doing it at the moment is to do separate runs for each period of time, but how would I take the output of one run and use it as the starting conditions for the next run?
Thanks for any advice you can give,
Rebecca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110714/682dcf4f/attachment-0005.htm>
More information about the TRNSYS-users
mailing list