Jun-Won,
  There is an example of translating the transmission, absorption, and 
reflection into the TRNBuild variables ISHADE and REFLISHADE on page 
6-59 of the TRNBuild manual (volume 06 of the documentation set). Note 
that in order for the internal shading parameters to take effect, the 
value of the the window's 'internal shading factor' (which is defined at 
the zone level, not in the window type manager) must be set to some 
value other than zero.
Kind regards,
  David
On 7/5/2011 04:16, 박준원 wrote:
>
> Hi~~!!
>
> I am a Korean student. I am using TRNSYS Ver.16
>
> In TRNbuild, I wish to add a window with internal shading device.
>
> Blind properties(transmitance, absorptance, reflectance) 
> are calculated in simulation studio.
>
> These values are connected into the multizone building model(Type56b)
>
> And  In TRNbuild, the values(transmitance, absorptance, reflectance) 
> are input value using Window Type Manager.
>
> But I dont know where the values are entered at Window Type manager.
>
> Help me!
>
> Thank you, and I'm sorry for my poor English skill.
>
>
> Jun-Won Park
> The Master's Course
> Building Technology Reasearch Unit Laboratory Sungkyunkwan Univ.
> Department of Architectural Engineering ,
> Sungkyunkwan University
> 300 Chunchun, Jangan, Suwon, Kyunggi, SOUTH. KOREA
> 440-746
> Mobile. +82-10-4161-2184
> Tel: +82-31-299-4775
> Fax: +82-31-290-7570
> Email: flowrime at naver.com <mailto:flowrime at naver.com>
> Web: http://btu.skku.ac.kr/
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110705/f03169da/attachment-0005.htm>
    
    
More information about the TRNSYS-users
mailing list