[TRNSYS-users] Surface radiation model in TYPE 56
David BRADLEY
d.bradley at tess-inc.com
Mon Jan 31 08:17:38 PST 2011
Kuniaki,
Type56 takes the total and beam solar radiation values as inputs.
This allows you to use whatever sky model (or even measured data) that
you want. It is the weather processing component (Type15, Type99, or
Type16 in Trnsys17, Type15, Type109, of Type16 in Trnsys16) that allows
you to set the diffuse sky radiation calculation method. You can select
between an isotropic sky model or 4 different anisotropic sky models
(Hay and Davies, Reindl, Perez 1988, or Perez 1999)
Kind regards,
David
On 1/30/2011 20:55, 三原 邦彰 wrote:
> Dear all,
>
> What is the computational method of the total radiation on tilted surface incidented external wall and window etc in TYPE56 ?
> Is the anisotropic model used ?
>
> Best Regards
>
> Kajima. corp.
> Kuniaki Mihara
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
--
***************************