[TRNSYS-users] Type 655: flowrate problem
    Jeff Thornton 
    thornton at tess-inc.com
       
    Fri Jan 21 11:17:45 PST 2011
    
    
  
<The problem I  am encountering is that the Type 655 treats the input
"chilled water flowrate" as a temperature, and therefore you can only
choose units like C, F or K. >
I just opened Type 655 in TRNSYS 16 and TRNSYS 17 and it's set to flow
rate in both instances.  So somehow it got set to a temperature in your
version.  To fix it, simply open the proforma for Type 655 (right click on
the icon in the assembly panel and choose Proforma or double click on the
icon in the Direct Access tool).  Then find the input for the chilled
water flow rate (Variables Tab, Inputs Tab) and set the dimension back to
"Flow Rate" and the units to kg/hr.
Jeff
Jeff Thornton
President - TESS, LLC
22 North Carroll Street - Suite 370
Madison WI 53703 USA
Phone: 608-274-2577
Fax: 608-278-1475
E-mail: thornton at tess-inc.com
Web: www.tess-inc.com
    
    
More information about the TRNSYS-users
mailing list