[TRNSYS-users] infiltration rate
王洋
wanghongyang1767 at gmail.com
Mon Feb 21 23:29:12 PST 2011
Dear all,
I want to compare the test room infiltration rate of actual measurement with
by TRNSYS simulation. Maybe as you know, in the TRNFlow manual: there it is
explained that "As soon as TRNFLOW is turned on, (...) in the simulation the
defined infiltrations, ventilations and couplings will be replaced with the
calculated air flows."
I defined CO2% as 1000 ppm in TRNFlow, then I want to observe CO2%'s
reducing curve when infiltration rate is 0.5276 1/h (I measured the value in
the test room), so I defined the infiltration rate as 0.5276 1/h in
TRNBUILD. But when I used TRNFLOW, the defined infiltration rate as 0.5276
1/h in TRNBUILD was replaced. And 1000 ppm keeps constant.
Please tell me how to get the infiltration rate curve using TRNSYS/TRNFLOW
or how to explain this ?
Many thanks!
br
wang
在 2011年2月21日 下午10:58, <trnsys-users-request at cae.wisc.edu>写道:
> Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
> 1. infiltration rate (??)
> 2. Fw: error message in calling matlab from trnsys (Rekiya Suleiman)
> 3. Re: Fw: error message in calling matlab from trnsys
> (Mehdi Shahrestani)
>
>
> ---------- 已转发邮件 ----------
> From: 王洋 <wanghongyang1767 at gmail.com>
> To: trnsys-users at cae.wisc.edu
> Date: Mon, 21 Feb 2011 22:16:12 +0100
> Subject: [TRNSYS-users] infiltration rate
> Dear all,
>
>
> I want to compare the test room infiltration rate of actual measurement
> with by TRNSYS simulation. Maybe as you know, in the TRNFlow manual: there
> it is explained that "As soon as TRNFLOW is turned on, (...) in the
> simulation the defined infiltrations, ventilations and couplings will be
> replaced with the calculated air flows."
> I defined CO2% as 1000 ppm in TRNFlow, then I want to observe CO2%'s
> reducing curve when infiltration rate is 0.5276 1/h (I measured the value in
> the test room), so I defined the infiltration rate as 0.5276 1/h in
> TRNBUILD. But when I used TRNFLOW, the defined infiltration rate as 0.5276
> 1/h in TRNBUILD was replaced. And 1000 ppm keeps constant.
>
> Please tell me how to get the infiltration rate curve using
> TRNSYS/TRNFLOW or how to explain this ?
>
> Many thanks!
>
> br
>
> wang
>
>
>
> 在 2011年2月21日 下午12:07,王洋 <wanghongyang1767 at gmail.com>写道:
>
>> Dear all,
>>
>>
>> I want to compare the test room infiltration rate of actual measurement
>> with by TRNSYS simulation. Maybe as you know, in the TRNFlow manual: there
>> it is explained that "As soon as TRNFLOW is turned on, (...) in the
>> simulation the defined infiltrations, ventilations and couplings will be
>> replaced with the calculated air flows."
>> I defined CO2% as 1000 ppm in TRNFlow, then I want to observe CO2%'s
>> reducing curve when infiltration rate is 0.5276 1/h (I measured the value in
>> the test room), so I defined the infiltration rate as 0.5276 1/h in
>> TRNBUILD. But when I used TRNFLOW, the defined infiltration rate as 0.5276
>> 1/h in TRNBUILD was replaced. And 1000 ppm keeps constant.
>>
>> Please tell me how to get the infiltration rate curve using
>> TRNSYS/TRNFLOW or how to explain this ?
>>
>> Many thanks!
>>
>> br
>>
>> wang
>>
>> 2011/2/21 <trnsys-users-request at cae.wisc.edu>
>>
>>> Send TRNSYS-users mailing list submissions to
>>> trnsys-users at cae.wisc.edu
>>>
>>> To subscribe or unsubscribe via the World Wide Web, visit
>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>> or, via email, send a message with subject or body 'help' to
>>> trnsys-users-request at cae.wisc.edu
>>>
>>> You can reach the person managing the list at
>>> trnsys-users-owner at cae.wisc.edu
>>>
>>> When replying, please edit your Subject line so it is more specific
>>> than "Re: Contents of TRNSYS-users digest..."
>>>
>>> Today's Topics:
>>>
>>> 1. Problems with calling EES (Type66a) (Doms Joris)
>>> 2. wall definition (davide disco)
>>>
>>>
>>> ---------- 已转发邮件 ----------
>>> From: Doms Joris <joris.doms at vito.be>
>>> To: "trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>
>>> Date: Sun, 20 Feb 2011 22:43:08 +0100
>>> Subject: [TRNSYS-users] Problems with calling EES (Type66a)
>>> Dear TRNSYS users,
>>>
>>> When simulating an applied thermal system, I'm using EES for the hydronic
>>> part. I programmed the hydronic circuit in EES and coupled it with TRNSYS
>>> via Type 66a. This coupling works fine, but;
>>>
>>> The problem is that the simulation runs very slow. Every timestep that
>>> TRNSYS calls EES, the EES project is opened and closed. Is there a way to
>>> set some settings so EES isen't closed and reopened each time, this would
>>> minimize the solution time alot.
>>>
>>> Thanks on advance
>>>
>>> Joris Doms
>>>
>>> ------------------------------
>>> This e-mail, any attachments and the information it contains are
>>> confidential and meant only for the use of the addressee(s) only. Access to
>>> this e-mail by anyone other than the addressee(s) is unauthorized. If you
>>> are not the intended addressee (or responsible for delivery of the message
>>> to such person), you may not use, copy, distribute or deliver to anyone this
>>> message (or any part of its contents) or take any action in reliance on it.
>>> In such case, you should destroy this message and notify the sender
>>> immediately. If you have received this e-mail in error, please notify us
>>> immediately by e-mail or telephone and delete the e-mail from any computer.
>>> All reasonable precautions have been taken to ensure no viruses are
>>> present in this e-mail and its attachments. As our company cannot accept
>>> responsibility for any loss or damage arising from the use of this e-mail or
>>> attachments we recommend that you subject these to your virus checking
>>> procedures prior to use.
>>> ------------------------------
>>>
>>>
>>>
>>> ---------- 已转发邮件 ----------
>>> From: davide disco <chester_83 at hotmail.it>
>>> To: <trnsys-users at cae.wisc.edu>
>>> Date: Mon, 21 Feb 2011 11:57:59 +0100
>>> Subject: [TRNSYS-users] wall definition
>>> Dear all,
>>> when entering data in Trnbuild I have to describe the walls of the zone:
>>> if, looking at the plant of the building, the building has more than a wall
>>> south oriented for example (wall to the left in the plant) I should enter
>>> in Trnbuild each section of wall facing south or I should enter a unique
>>> wall that is the sum of all sections of wall facing south?
>>> Thanks in advace.
>>> Best regards
>>>
>>> _______________________________________________
>>> TRNSYS-users mailing list
>>> TRNSYS-users at cae.wisc.edu
>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>
>>>
>>
>
>
> ---------- 已转发邮件 ----------
> From: Rekiya Suleiman <omohu_s at yahoo.com>
> To: trnsys-users at cae.wisc.edu
> Date: Mon, 21 Feb 2011 13:32:19 -0800 (PST)
> Subject: [TRNSYS-users] Fw: error message in calling matlab from trnsys
> Dear trnsys users,
> Please I am still waiting for help on the forwarded problem, please help!
> Thanks
>
> Rekiyat
>
> ----- Forwarded Message ----
> *From:* Rekiya Suleiman <omohu_s at yahoo.com>
> *To:* trnsys-users at cae.wisc.edu
> *Sent:* Fri, February 18, 2011 8:03:40 PM
> *Subject:* error message in calling matlab from trnsys
>
> Hi,
> Please can anyone help, I'm still learning to use the trnsys program. I am
> trying to use Type155 to call a code written in matlab but I keep getting
> the error message 'undefined command/function 'trnInputs'". What can I do to
> get out of this.
>
> Rekiyat Suleiman
> Dept of Mechanical Engineering
> Ahmadu Bello University, Zaria
> Nigeria.
>
>
>
>
> ---------- 已转发邮件 ----------
> From: "Mehdi Shahrestani" <mahdishahrestani at yahoo.com>
> To: "'Rekiya Suleiman'" <omohu_s at yahoo.com>
> Date: Mon, 21 Feb 2011 21:58:25 -0000
> Subject: Re: [TRNSYS-users] Fw: error message in calling matlab from trnsys
>
> Dear Rekiyat
>
>
>
> Couple of months ago I had the same problem. It should be related to the
> type155 dll file which calls Matlab.
>
> This file some times is not compatible with your Matlab version.
>
> Anyway, I have this dll for Matlab 2009a if you have the same version it
> could solve the problem.
>
> Please let me know you matlab version.
>
>
>
> Regards
>
> Mehdi
>
>
>
>
>
>
> ------------------------------
>
> *From:* trnsys-users-bounces at cae.wisc.edu [mailto:
> trnsys-users-bounces at cae.wisc.edu] *On Behalf Of *Rekiya Suleiman
> *Sent:* 21 February 2011 21:32
> *To:* trnsys-users at cae.wisc.edu
> *Subject:* [TRNSYS-users] Fw: error message in calling matlab from trnsys
>
>
>
> Dear trnsys users,
>
> Please I am still waiting for help on the forwarded problem, please help!
>
> Thanks
>
>
>
> Rekiyat
>
>
>
> ----- Forwarded Message ----
> *From:* Rekiya Suleiman <omohu_s at yahoo.com>
> *To:* trnsys-users at cae.wisc.edu
> *Sent:* Fri, February 18, 2011 8:03:40 PM
> *Subject:* error message in calling matlab from trnsys
>
> Hi,
>
> Please can anyone help, I'm still learning to use the trnsys program. I am
> trying to use Type155 to call a code written in matlab but I keep getting
> the error message 'undefined command/function 'trnInputs'". What can I do to
> get out of this.
>
>
>
> Rekiyat Suleiman
>
> Dept of Mechanical Engineering
>
> Ahmadu Bello University, Zaria
>
> Nigeria.
>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110222/e9698f99/attachment-0005.htm>
More information about the TRNSYS-users
mailing list