[TRNSYS-users] questionable QINF

David BRADLEY d.bradley at tess-inc.com
Wed Feb 9 10:03:07 PST 2011


Wang,
  I would recommend that you send your project to your TRNSYS 
distributor for direct assistance. You have set your infiltration rates 
in TRNBuild as constant values (independent of windspeed and direction) 
for all three of your zones. However, your simulation couples the Type56 
thermal model with TRNFlow. In most circumstances, TRNFlow would 
calculate the infiltration rate and it may be that the constant values 
that you are specifying (and then switching off) are actually being 
ignored because of the TRNFlow integration. I am afraid I do not have 
TRNFlow installed so I cannot check.
Regards,
  David


On 2/9/2011 09:20, 王洋 wrote:
> Dear all,
>
>
> I got the result of  QINF which are the same when the infiltration is 
> on or off. I think TNRSYS's results are questionable. Why I turn off 
> the infiltration, is there still having QINF?
>
> And  when the walls are massless or massive, the result of  QINF which 
> are the same, it's 190.73 kJ all the time not only turning on the 
> infiltration but also turning off it; not only massless but also massive.
>
> Please see the ATTACHED and explain them! Thanks! These programs are 
> turning on the INFILTRATION, you can turn off the INFILTRATION. The 
> both results of TYPE 46 linking to QINF are 190.73 kJ one day.
> But I calculated QINF one day by hand, the result is more than 190.73 
> kJ. Q=CairM(Tindoor-Toutdoor)=1.
> 004*( 52*24*1.2)*(20-10)=14976 kJ, where Cair=1.004 kJ/kgK, 
> M=V*Dair=52 m3/h*24h*1.2 kg/m3
>
> I think my calculation is right. I think TNRSYS's results are 
> questionable.
>
> Many thanks!
>
> Br.
>
> wang
>
>
>
>
> 2011/2/9 <trnsys-users-request at cae.wisc.edu 
> <mailto:trnsys-users-request at cae.wisc.edu>>
>
>     Send TRNSYS-users mailing list submissions to
>     trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>
>     To subscribe or unsubscribe via the World Wide Web, visit
>     https://mailman.cae.wisc.edu/listinfo/trnsys-users
>     or, via email, send a message with subject or body 'help' to
>     trnsys-users-request at cae.wisc.edu
>     <mailto:trnsys-users-request at cae.wisc.edu>
>
>     You can reach the person managing the list at
>     trnsys-users-owner at cae.wisc.edu
>     <mailto:trnsys-users-owner at cae.wisc.edu>
>
>     When replying, please edit your Subject line so it is more specific
>     than "Re: Contents of TRNSYS-users digest..."
>
>     Today's Topics:
>
>       1. Re: Collectors in Series (Matt Duffy)
>       2. 64 Bit Fortran Compiler and Multi-Thread CPU's (Aaron Danenberg)
>       3. Re: TESS library examples two types couldn't run (Matt Duffy)
>       4. TRNFLOW'S large openig and Ventilation in TRNBUILD (??)
>
>
>     ---------- 已转发邮件 ----------
>     From: "Matt Duffy" <duffy at tess-inc.com <mailto:duffy at tess-inc.com>>
>     To: "Sancho,Fernando" <fernando.sancho at sonnenwaermeag.de
>     <mailto:fernando.sancho at sonnenwaermeag.de>>,
>     trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>     Date: Wed, 9 Feb 2011 08:20:20 -0600 (CST)
>     Subject: Re: [TRNSYS-users] Collectors in Series
>     Fernando,
>
>     You are correct on the flowrates - the collectors in series need to be
>     scaled down accordingly. I just did a simple simulation with two
>     in series
>     using Type1 and compared it to 1 with the same total area in
>     parallel and
>     got nominal results (greater outlet temperatures in series, the useful
>     energy gain is very similar, yet slightly greater losses in
>     series). I can
>     send you the project upon your request.
>
>     Best regards,
>
>     Matt Duffy
>
>
>     ----- Original Message -----
>     From: "Sancho,Fernando" <fernando.sancho at sonnenwaermeag.de
>     <mailto:fernando.sancho at sonnenwaermeag.de>>
>     Sent: Tue, February 8, 2011 4:17
>     Subject:[TRNSYS-users]  Collectors in Series
>
>
>     Thanks Matt, hello Felix
>
>     I'm still doing some proving. Maybe we  should just change the
>     flow rate
>     "manually".For two collectors in series it would be the same as
>     for just
>     one,  in
>     this case is clear that we are getting another results.
>
>     100 m2 in parallel, flow rate 10000 l/h
>     25m2+25m2+25m2+25m2 flow rate 2500 l/h
>
>
>
>
>     Mit freundlichen Grüßen
>
>
>     Fernando Sancho Márquez
>     PHÖNIX SonnenWärme AG
>
>     ____________________________________________
>     PHÖNIX Sonnenwärme AG
>     Ostendstr. 1
>     D-12459 Berlin
>
>
>
>
>     _______________________________________________
>     TRNSYS-users mailing list
>     TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>     https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>     ----- End of original message -----
>
>
>
>
>     ---------- 已转发邮件 ----------
>     From: "Aaron Danenberg" <danenberg at hartford.edu
>     <mailto:danenberg at hartford.edu>>
>     To: <trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>>
>     Date: Wed, 9 Feb 2011 09:24:41 -0500
>     Subject: [TRNSYS-users] 64 Bit Fortran Compiler and Multi-Thread CPU's
>
>     Does anyone have experience with a 64 Bit Fortran Compiler?  I
>     have installed Compaq Visual Fortran Professional Edition for Win
>     32 x86 Systems V6.6.  It is not stable on the three 64 bit systems
>     I have installed it on.  I must attempt to load the program
>     multiple times.  Usually when I load the program it instantly
>     quits.  I would like to take advantage of my 64 bit system and
>     recompile TRNSYS with a 64 Bit compiler.  On the TESS website and
>     in the forums there is a brief note on this subject.  However the
>     link that is provided to an Intel site with a 64 bit compiler is
>     broken.  I have googled 654 bit compliers with little success.  I
>     have very limited experience with Fortran, so I may not be using
>     the best search terms.
>
>     Also I am running a second generation I7 Quad core with two
>     threads per core.  When I run a simulation in the Studio only one
>     thread per core is being used.  Is there a way to set the Studio
>     to run on all 8 threads?  I set the priority to High (Real Time
>     Setting Could not be Applied), and I set the affinity to all 8
>     threads.  Thanks!
>
>     Aaron Danenberg
>
>     Mechanical Engineering Graduate Student
>
>     University of Hartford
>
>
>
>     ---------- 已转发邮件 ----------
>     From: "Matt Duffy" <duffy at tess-inc.com <mailto:duffy at tess-inc.com>>
>     To: "CZ" <zh.chelsea at gmail.com <mailto:zh.chelsea at gmail.com>>
>     Date: Wed, 9 Feb 2011 08:26:41 -0600 (CST)
>     Subject: Re: [TRNSYS-users] TESS library examples two types
>     couldn't run
>
>     Dear Chelsea,
>
>     You are going to need to determine what the types are errors are
>     that you are receiving when you try to run the simulation, or
>     elaborate on why they cannot run. When you run your *.tpf
>     simulation, there are a few files that are created: the deck file
>     (*.dck, the TRNSYS input file), the log file (*.log), and the
>     listing file (*.lst). The log and the listing file should have the
>     information about your errors. Or, there is an icon on the lower
>     left side of the Simulation Studio, called the "Result File"; you
>     may also click on that to access the log information.
>
>     I would recommend upgrading to TRNSYS v17 and TESS Libraries 17 as
>     there are many new, useful additions including the slab-on-grade
>     component with the Google Sketchup plugin, new radiant slab
>     models, and the basement model as well.
>
>     Best regards,
>
>     Matt Duffy
>
>     *----- Original Message -----*
>     *From:* "CZ" <zh.chelsea at gmail.com <mailto:zh.chelsea at gmail.com>>
>     *Sent:* Mon, February 7, 2011 16:36
>     *Subject:* Re: [TRNSYS-users] TESS library examples two types
>     couldn't run
>
>     Hello, Matt:
>
>     Thank you for your reply.
>     But currently I'm using the TRNSYS version16.01.0003. I tried Type
>     705 and Type 712 in my computer, and also in another computer
>     which is also same TRNSYS version and Windows 7, both of them
>     couldn't run, and Type 705.lst file even doesn't exist.
>     So do you think this is the TESS version problem, do I need to
>     update the TESS library?
>
>     Thank you,
>     Chelsea
>
>     On Thu, Feb 3, 2011 at 7:04 AM, Matt Duffy <duffy at tess-inc.com> wrote:
>
>         Dear Chelsea,
>
>         I was able to run those without any problems in TRNSYS 16.1.
>         Please check the listing (*.lst) or log (*.log) file for more
>         information about your errors.
>
>         Those components are from the previous TESS Libraries 2.x. I
>         strongly suggest contacting your local TRNSYS distributor to
>         obtain the upgrade to TESS Libraries 17.01 and TRNSYS 17.00.0019.
>
>         Best regards,
>
>         Matt Duffy
>
>
>         *----- Original Message -----*
>         *From:* "CZ" <zh.chelsea at gmail.com <mailto:zh.chelsea at gmail.com>>
>         *Sent:* Wed, February 2, 2011 20:21
>         *Subject:* [TRNSYS-users] TESS library examples two types
>         couldn't run
>         Could you please try TESS models/studio projects/ground
>         coupling library/Type 705 and Type 712?
>         They are radiant slab with embedded pipes.
>         These two examples can not run in my computer, and my computer
>         has Windows 7.
>
>         Thank you,
>         Chelsea
>
>         ------------------------------------------------------------------------
>
>         _______________________________________________
>         TRNSYS-users mailing list
>         TRNSYS-users at cae.wisc.edu
>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
>
>     ---------- 已转发邮件 ----------
>     From: 王洋 <wanghongyang1767 at gmail.com
>     <mailto:wanghongyang1767 at gmail.com>>
>     To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>     Date: Wed, 9 Feb 2011 16:13:55 +0100
>     Subject: [TRNSYS-users] TRNFLOW'S large openig and Ventilation in
>     TRNBUILD
>     Dear all,
>     I have a queation about TRNFLOW'S large openig and Ventilation in
>     TRNBUILD:
>
>      If I defined TRNFLOW'S large openig and Ventilation in TRNBUILD,
>     How can both of them work? Can they both have influences on each
>     other? What does the QVENT include? Only Ventilation in TRNBUILD
>     or both of them? What does the FLVSZ include? Only TRNFLOW'S large
>     openig's Ventilation?
>
>     Many thanks!
>
>     br.
>
>     wang
>
>
>
>     2011/2/9 <trnsys-users-request at cae.wisc.edu
>     <mailto:trnsys-users-request at cae.wisc.edu>>
>
>         Send TRNSYS-users mailing list submissions to
>         trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>
>         To subscribe or unsubscribe via the World Wide Web, visit
>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
>         or, via email, send a message with subject or body 'help' to
>         trnsys-users-request at cae.wisc.edu
>         <mailto:trnsys-users-request at cae.wisc.edu>
>
>         You can reach the person managing the list at
>         trnsys-users-owner at cae.wisc.edu
>         <mailto:trnsys-users-owner at cae.wisc.edu>
>
>         When replying, please edit your Subject line so it is more
>         specific
>         than "Re: Contents of TRNSYS-users digest..."
>
>         Today's Topics:
>
>           1. (no subject) (davide disco)
>           2. Re: TYPECK () (Farah Gammoh)
>           3. Type 15-2_Simulation start time (Felix Martin Beutefuehr,
>         BLV-TGE)
>           4. INTERNATIONAL TRNSYS DAY, COURSES & NETWORKING (Info
>         Aiguasol)
>
>
>         ---------- 已转发邮件 ----------
>         From: davide disco <chester_83 at hotmail.it
>         <mailto:chester_83 at hotmail.it>>
>         To: <trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>>
>         Date: Wed, 9 Feb 2011 01:23:50 +0100
>         Subject: [TRNSYS-users] (no subject)
>         Hello,
>         when I add a wall I have to specify the layers that make up
>         the wall, and for each new layer Trnsys requires three
>         quantities: conductivity, capacity and density.
>         Now, the capacity is expressed in KJ/(Kg K), but for the
>         layers of wall I have the thermal conductivity (expressed in
>         W/m²·K) instead of the capacity as required by the program.
>         There is a way to correlate this two quantities so that I can
>         enter the thermal conductivity instead of the capacity?
>
>         Thanks in advance
>
>
>         ---------- 已转发邮件 ----------
>         From: Farah Gammoh <farah.gammoh at mirroxx.com
>         <mailto:farah.gammoh at mirroxx.com>>
>         To: "TRNSYS-users at cae.wisc.edu
>         <mailto:TRNSYS-users at cae.wisc.edu>" <TRNSYS-users at cae.wisc.edu
>         <mailto:TRNSYS-users at cae.wisc.edu>>
>         Date: Wed, 09 Feb 2011 11:58:36 +0100
>         Subject: Re: [TRNSYS-users] TYPECK ()
>         Hello,
>         could someone please explain to me the last three parameters
>         of the typeck subroutine? what are the correct INPUT,
>         PARAMETER and DERIVATIVE parameters to pass on? do they refer
>         to the total number in the entire type?
>         thanks in advance
>         Farah
>         davide disco schrieb:
>
>             Hello,
>             when I add a wall I have to specify the layers that make
>             up the wall, and for each new layer Trnsys requires three
>             quantities: conductivity, capacity and density.
>             Now, the capacity is expressed in KJ/(Kg K), but for the
>             layers of wall I have the thermal conductivity (expressed
>             in W/m²·K) instead of the capacity as required by the program.
>             There is a way to correlate this two quantities so that I
>             can enter the thermal conductivity instead of the capacity?
>
>             Thanks in advance
>                                                      
>              ------------------------------------------------------------------------
>
>             _______________________________________________
>             TRNSYS-users mailing list
>             TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>             https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
>         -- 
>
>         Mirroxx Logo <image002.gif>
>
>
>
>
>
>         * *
>
>
>
>
>
>         Farah Gammoh
>         MSc. Energy Conversion and Management
>
>         Engineering
>
>
>
>         *Mirroxx GmbH*
>
>         *Emmy-Noether-Str. 2*
>
>         *79110 Freiburg*
>
>         *Germany*
>
>
>
>
>
>
>
>
>
>
>
>
>
>         T (++49) 761 - 767 111-0
>
>         F (++49) 761 - 767 111-99
>
>         farah.gammoh at mirroxx.com <mailto:farah.gammoh at mirroxx.com>
>         <mailto:farah.gammoh at mirroxx.com
>         <mailto:farah.gammoh at mirroxx.com>>
>
>         www.mirroxx.com <http://www.mirroxx.com> <http://www.mirroxx.com/>
>
>
>
>         *Register*
>
>         Amtsgericht Freiburg
>
>         HRB 703185
>
>
>
>
>
>
>         ---------- 已转发邮件 ----------
>         From: "Felix Martin Beutefuehr, BLV-TGE" <beutefuf at fh-trier.de
>         <mailto:beutefuf at fh-trier.de>>
>         To: trnsys-users at engr.wisc.edu <mailto:trnsys-users at engr.wisc.edu>
>         Date: Wed, 9 Feb 2011 12:00:50 +0100
>         Subject: [TRNSYS-users] Type 15-2_Simulation start time
>
>         Dear Trnsys users,
>
>         I am using Type 15-2 and i am using a simulation timestep of 3
>         min. If the
>         simulation start time is 0 hr, everything works out fine. But
>         once i change
>         the simulation starttime to 2000 hours i get the following error
>         massage_"unable to correctly read from the supplied data
>         file-please check
>         the file and re-run the simulation". This massage refers to
>         Type 15-2.
>         If I then change the simulation time step to 1 hour and re run the
>         simulation, no error occurs.
>
>         So what can I do to if I want a simulation time step within
>         the range of 1-5
>         min?
>
>         Many thanks in advance
>
>         Felix
>
>         --
>         http://webmail.fh-trier.de
>
>
>
>
>         ---------- 已转发邮件 ----------
>         From: Info Aiguasol <infoaiguasol at aiguasol.coop
>         <mailto:infoaiguasol at aiguasol.coop>>
>         To: Info Aiguasol <infoaiguasol at aiguasol.coop
>         <mailto:infoaiguasol at aiguasol.coop>>
>         Date: Wed, 9 Feb 2011 12:29:15 +0100
>         Subject: [TRNSYS-users] INTERNATIONAL TRNSYS DAY, COURSES &
>         NETWORKING
>
>         tud02.png
>
>         Dear all,
>
>          We are glad to invite you to the,
>
>         *1st FOCUSED International TRNSYS Users’ Day
>         <http://aiguasol.coop/2011/01/energy-thinking-days/3/>*
>
>         that will take place in Barcelona the next *April 5^th *,
>         under the frame of the
>
>         *Energy Thinking days 2011
>         <http://aiguasol.coop/2011/01/energy-thinking-days/>*
>
>         As usual, TRNSYS users’ day wants to be a space for sharing
>         experiences in the use of our tool where to explain, ask and
>         exchange ideas, works, what to do and what not to. This time
>         two different things will be introduced. First of all, the
>         *presentation of new version of TRNSYS, 17^th *, with its main
>         new features, especially it’s Sketch up plug-in, with a demo.
>         And, also new, the idea of having a *technologically focused
>         workshop*: we ask you to present your *works on*
>
>         **
>
>         *solar thermal coupled with DHC, heat pumps and/or seasonal
>         storage,*
>
>         *and also DHC and seasonal storage by itself*.
>
>         The aim is to have a technical meeting focused on systems
>         simulation useful for the 44^th and 45^th  IEA Tasks work that
>         will have their meeting in Barcelona the same weeks. We hope
>         this effort will be useful for all.
>
>         	
>
>         **
>
>         /Benvolguts,/
>
>         / Ens plau convidar-vos al,/
>
>         */1st FOCUSED International TRNSYS Users’ Day
>         <http://aiguasol.coop/2011/01/energy-thinking-days/3/>/*
>
>         *//*/que tindrà lloc a Barcelona el proper *5 d’abril* sota el
>         paraigües dels/
>
>         */Energy Thinking days 2011
>         <http://aiguasol.coop/2011/01/energy-thinking-days/>/*
>
>         /Com de costum, el dia els usuaris de TRNSYS vol ser un espai
>         per compartir experiències en l'ús de la nostra eina, per
>         explicar, preguntar i intercanviar idees, treballs, què fer i
>         què no. Aquesta vegada dues coses noves. En primer lloc, la
>         *presentació de la nova versió de TRNSYS, la 17*, amb les
>          seves principals novetats, sobretot el plug-in d’Sketch-Up,
>         amb una demostració. I, també nou, la voluntat de ser *un
>         taller de tecnologia enfocada*: us demanem que presenteu els
>         vostres treballs sobre/
>
>         */solar tèrmica acoblada amb DHC, bombes de calor i/o
>         acumulació estacional/*
>
>         */i també, DHC i acumulació estacional en sí mateixos./*
>
>         /L’objectiu és aconseguir una trobada tècnica focalitzada en
>         simulació de sistemes que sigui d’utilitat per a les Tasks 44
>         i 45 de la IEA, que es trobaran a Barcelona la mateixa
>         setmana. Esperem que aquest esforç sigui útil per a tothom./
>
>         	
>
>         Estimados,
>
>         Nos complace invitaros al,
>
>         *1st FOCUSED International TRNSYS Users' Day
>         <http://aiguasol.coop/2011/01/energy-thinking-days/3/>*
>
>         que tendrá lugar en Barcelona el *próximo 5 de abril* bajo el
>         paraguas de los
>
>         *Energy Thinking days 2011
>         <http://aiguasol.coop/2011/01/energy-thinking-days/>*
>
>         Como de costumbre, el día los usuarios de TRNSYS quiere ser un
>         espacio para compartir experiencias en el uso de nuestra
>         herramienta, para explicar, preguntar e intercambiar ideas,
>         trabajos, qué hacer y qué no. Esta vez dos cosas nuevas. En
>         primer lugar, *la presentación de la nueva versión de TRNSYS,
>         la 17*, con sus principales novedades, sobre todo el plug-in
>         de Sketch-Up, con una demostración. Y, también nuevo, la
>         voluntad de ser *un taller de tecnología enfocada*: os pedimos
>         que presentéis vuestros trabajos sobre
>
>         *solar térmica acoplada con DHC, bombas de calor y / o
>         acumulación estacional *
>
>         *y también, DHC y acumulación estacional en sí mismos.*
>
>         El objetivo es conseguir un encuentro técnico focalizada en
>         simulación de sistemas que sea de utilidad para las Tasks 44 y
>         45 de la IEA, que se encontrarán en Barcelona la misma semana.
>         Esperamos que este esfuerzo sea útil para todos.
>
>         *Please send your abstracts before February 25^th . **info >
>         <http://aiguasol.coop/2011/01/energy-thinking-days/3/>*
>
>         	
>
>         */Sisplau, envieu els vostres resums abans del 25 de Febrer.
>         /*//*/info >
>         <http://aiguasol.coop/2011/01/energy-thinking-days/3/>/*
>
>         	
>
>         *Por favor, envía tus resúmenes antes del 25 de Febrero.
>         **info > <http://aiguasol.coop/2011/01/energy-thinking-days/3/>*
>
>         **
>
>         *Other Energy Thinking days’ events:*
>
>         > *ecoheat4eu DHC open workshop
>         <http://aiguasol.coop/2011/02/energy-thinking-days/2/>*
>
>         	
>
>         4 April
>
>         	
>
>         > *1st FOCUSED International TRNSYS Users’ Day
>         <http://aiguasol.coop/2011/02/energy-thinking-days/3/>*
>
>         	
>
>         5 April
>
>         	
>
>         >***IEA-SHC Task 45 Meeting <http://www.iea-shc.org/task45/>*
>
>         	
>
>         5,6 April
>
>         	
>
>         >***IEA-SHC Tasks’ Experts Open Workshop
>         <http://aiguasol.coop/2011/02/energy-thinking-days/4/>*
>
>         	
>
>         6 April
>
>         	
>
>         > *Curso iniciación a TRNSYS17 y simulación de edificios
>         <http://aiguasol.coop/wp-content/uploads/2011/02/Curso-iniciaci%C3%B3n-a-TRNSYS17+Simulaci%C3%B3n-de-Edificios.pdf>*
>
>         	
>
>         6,7,8 April
>
>         	
>
>         > *Curso de simulación de CSP con TRNSYS17.
>         <http://aiguasol.coop/wp-content/uploads/2011/02/Curso-de-simulaci%C3%B3n-de-CSP-con-TRNSYS17.pdf>*
>
>         	
>
>         6,7,8 April
>
>         	
>
>         >***IEA-SHC Task 44 Meeting <http://www.iea-shc.org/task44/>*
>
>         	
>
>         7,8 April
>
>         	
>
>
>         	
>         	
>         	
>
>         	
>         	
>         	
>         	
>
>         	
>         	
>         	
>         	
>         	
>         	
>
>
>         _______________________________________________
>         TRNSYS-users mailing list
>         TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
>     _______________________________________________
>     TRNSYS-users mailing list
>     TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>     https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110209/b7c83456/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 69206 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110209/b7c83456/attachment-0005.png>


More information about the TRNSYS-users mailing list