[TRNSYS-users] annual scheduling of interior shades
Adrien JEZEQUEL - ITF
a.jezequel at itf.biz
Wed Feb 2 23:24:39 PST 2011
Dear Simge,
As you say, you may use type56 inputs.
To define yearly schedule, you can :
* use an equation tool with comparator LT and GT. You will have to
write something like SHADING =
0.1995*(GT(TIME,8016)+LT(TIME,3624))+0.161*(GE(TIME,3624)*LE(TIME,8016))
* or use a forcing function define for a year
And connect your outputs to type56 inputs
Best regards
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz
/Afin de contribuer au respect de l'environnement, merci de n'imprimer
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/
Le 02/02/2011 23:25, simge andolsun a écrit :
> I would like to model a building with interior shades that have a
> varying shading ratio over the year. I need to set the shading ratio
> to 0.1955 from December 1st till May 31st. During the rest of the
> year, however, the shading ratio will be 0.161. Could you please
> describe how I can model this condition in TRNSYS? Should I use the
> "INPUT" option of the interior shading ratio in TRNBuild? If so, how
> should I input this yearly schedule into TRNSYS?
>
> Thanks in advance for your reply,
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110203/bc86b12a/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_signature.jpg
Type: image/jpeg
Size: 17526 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110203/bc86b12a/attachment-0005.jpg>
More information about the TRNSYS-users
mailing list