[TRNSYS-users] heat flux through a wall

David BRADLEY d.bradley at tess-inc.com
Mon Dec 19 10:04:50 PST 2011


Nils,
I think that if you use the combination of QCOMO and QCOMI, you can get 
at the energy transfer through the wall. QCOMO is the energy from 
outside the wall into the wall surface. QCOMI is the same for the inner 
surface. The difference between the two should be the amount of energy 
either stored by or given up by the wall.
Best,
David


On 12/16/2011 07:29, Nils Nikolai wrote:
> Dear TrnSYS users,
>
> i have the same question as Pablo. I am not sure how i can actually 
> get the heat flux through a wall. Is there an answer to this question?
>
> Thanks in Advance,
> Nils
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com




More information about the TRNSYS-users mailing list