[TRNSYS-users] TRNBLD - active layer - Thickness of adjacent layers
leen peeters
l.f.r.peeters at gmail.com
Tue Dec 13 11:08:11 PST 2011
Johannes,
I know they violate one another. As I cannot access the code of type 56, I
cannot check the implementation. We are currently working on finding out
where the limits of the model are ...
The model is based on an EMPA model, but there are no international
publications I found that really discuss the implementation of the active
layer model.
It is a numerical derivation, so emperics are not the cause. I will get
back to you once I figured out more.
Leen
On Tue, Dec 13, 2011 at 1:29 PM, Schrade, Johannes <
Johannes.Schrade at ibp.fraunhofer.de> wrote:
> Dear Leen, dear TRNSYS users,****
>
> ** **
>
> Thanks for your quick reply.****
>
> However, I’m not really satisfied with your suggestion, as I want to
> understand the reason behind it.****
>
> If you are right, I violated the requirement “outside diameter over pipe
> distance < 0.2”. But, this requirement is completely independent from the
> layer thickness of the adjacent layer, isn’t it?****
>
> On the other side, if both adjacent layers must be conform to the minimum
> thickness of 0.3 times pipe spacing, I would have caused a violation of
> this requirement by setting the pipe spacing to 24 cm and the layer
> thickness to 8mm. But for this, I didn’t receive any warning.****
>
> Last but not least, there are oppositional specifications for the required
> ratio between thickness of adjacent layer(s) and pipe spacing in the TRNBLD
> user manual. On page 5-186 the ratio should be greater than 0.3, on page
> 5-187 the ratio should be equal or smaller than 0.3 and on page 5-59 the
> ratio should be equal or greater than 0.3. So, nearly all possibilities are
> mentioned. I’m a bit confused.****
>
> ** **
>
> Looking forward to some light into the dark,****
>
> ** **
>
> Kind regards,****
>
> Johannes Schrade****
>
> ** **
>
> ** **
>
> ** **
>
> *Johannes Schrade*
> Abteilung Wärmetechnik****
>
> Fraunhofer-Institut für Bauphysik
> Nobelstr. 12
> 70569 Stuttgart****
>
> johannes.schrade at ibp.fraunhofer.de
> Telefon 0711 / 970-3416
> Telefax 0711 / 970-3399
> www.ibp.fraunhofer.de/wt/****
>
> *Johannes Schrade*
> Department Heat Technology ****
>
> Fraunhofer Institute for Building Physics
> Nobelstr. 12
> 70569 Stuttgart, Germany****
>
> johannes.schrade at ibp.fraunhofer.de
> Phone +49 711 / 970-3416
> Fax +49 711 / 970-3399
> www.ibp.fraunhofer.de/wt/****
>
> ** **
>
> *Von:* leen peeters [mailto:l.f.r.peeters at gmail.com]
> *Gesendet:* Montag, 12. Dezember 2011 22:09
> *An:* Schrade, Johannes
> *Cc:* trnsys-users at cae.wisc.edu
> *Betreff:* Re: [TRNSYS-users] TRNBLD - active layer - Thickness of
> adjacent layers****
>
> ** **
>
> Johannes,****
>
> ****
>
> as soon as you decrease the distance between the pipes, you come closer to
> the limits set regarding the modeling of the heat transfer in the direction
> of the water flow (direction z in the mathematical model). The stability of
> that model requires that you achieve a certain boundary condition, which is
> a.o. function of the thermal resistance of the water-pipe-inter pipe
> distance. In order to ensure these boundary conditions are satisfied the
> ratio of pipe outside diameter over pipe distance < 0.2 AND the ratios of
> layer thickness over pipe distance > 0.3. The 0.024-value you received for
> the minimum layer thickness comes from this limitation. I assume the extra
> measure is invoked once you come close to the 0.2-limit.****
>
> As soon as you take 0.1 for the pipe distance, you can again select 0.008
> m for layer thickness ...****
>
> Playing around with conductivity or capacity does not help, as the measure
> seems to be implemented through the above limits only ....****
>
> ****
>
> Leen
>
> ****
>
> On Mon, Dec 12, 2011 at 1:48 PM, Schrade, Johannes <
> Johannes.Schrade at ibp.fraunhofer.de> wrote:****
>
> Dear TRNSYS users,****
>
> ****
>
> I have some problems with the active layer module of TRNBLD, which I used
> for modeling a floor heating system.****
>
> The active layers, which should be displayed in the model, are defined as
> following:****
>
> ****
>
> Layer 1:****
>
> · Pipe spacing: 24 cm****
>
> · Pipe outside diameter: 16 mm****
>
> · Pipe wall thickness: 2 mm****
>
> ****
>
> Layer 2:****
>
> · Pipe spacing: 8 cm****
>
> · Pipe outside diameter: 16 mm****
>
> · Pipe wall thickness: 2 mm****
>
> ****
>
> By specifying the thicknesses of the layers adjacent to the active layers,
> the following curiosity appeared.****
>
> ****
>
> For case 1, I set the thickness of the layer above the active layer to 73
> mm, which is greater than 0.3 times the pipe spacing, and I set the layer
> below to 0.5 times the pipe outside diameter (requirements taken from
> manual TRNSYS 17, 5-187, table). This step had worked pretty good and the
> simulation was running without any problems.****
>
> In a second step, I revised the model and included the second active layer
> into the TRNBLD model. As the floor screed should be identical for both
> cases, I tried to define the thicknesses of the adjacent layers the same
> way as I did it in case 1. But when I tried to reduce the thickness of the
> adjacent layer below, the following warning appeared: “thickness must be in
> the range of 0.024 to 1.0”.****
>
> In order to understand this warning I had a closer look to the manual of
> TRNBLD. On page 5-58 (TRNSYS 17) I found a remark that both layers adjacent
> to the active layer must be greater than 0.3 times pipe spacing. This would
> explain, why the warning appears, but I do not understand, why the first
> case should be unproblematic, as the required minimum thickness in this
> case should be 72mm and why this is not mentioned in the mathematical
> description.****
>
> Does anyone has an idea, what could be the reason behind that, or might
> this be a known or unknown bug? If this requirement dependent on the pipe
> spacing should be really used for both layers, this would mean that
> extremely thick floor screeds of +15cm are necessary to model a floor
> heating system with a pipe spacing of 24 cm. This sounds absolutely
> unrealistic. ****
>
> ****
>
> Hoping for some help,****
>
> Kind regards,****
>
> ****
>
> Johannes Schrade****
>
> ****
>
> *Johannes Schrade*
> Abteilung Wärmetechnik****
>
> Fraunhofer-Institut für Bauphysik
> Nobelstr. 12
> 70569 Stuttgart****
>
> johannes.schrade at ibp.fraunhofer.de
> Telefon 0711 / 970-3416
> Telefax 0711 / 970-3399
> www.ibp.fraunhofer.de/wt/****
>
> *Johannes Schrade*
> Department Heat Technology ****
>
> Fraunhofer Institute for Building Physics
> Nobelstr. 12
> 70569 Stuttgart, Germany****
>
> johannes.schrade at ibp.fraunhofer.de
> Phone +49 711 / 970-3416
> Fax +49 711 / 970-3399
> www.ibp.fraunhofer.de/wt/****
>
> ****
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users****
>
> ** **
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111213/cbdca191/attachment-0001.htm>
More information about the TRNSYS-users
mailing list