[TRNSYS-users] Solar thermal collectors
David BRADLEY
d.bradley at tess-inc.com
Mon Dec 12 09:36:22 PST 2011
Lee,
No, the collector is a fixed surface based on the value of parameter
7 in Type109. Please note that in the more recent versions of TRNSYS,
Type109 has been replaced by Type15. The collector model takes into
account "incidence angle modifiers." That is to say that the optical
properties of the collector cover change depending on the direction of
the beam radiation. You therefore pass the incidence angle and the
collector slope from the weather reading processing component to the
solar collector component.
Just to be sure that there isn't an error in the example that you are
looking at, the Type109 output "angle of incidence for surface" is
connected to the collector input "incidence angle" and the Type109
output "slope of surface" is connected to the solar collector input
"collector slope"
Kind regards,
David
On 12/11/2011 10:24, hankiat lee wrote:
>
> hi,
>
> I'm testing out at which angle the solar thermal collector is set,
> which will have the most useful energy output.
>
> When i looking at the connection in the hot water system example in
> trnsys. i notice that the angle of incidence for tilted surface and
> slope of tilted surface from the Type 109 weather are connected to the
> solar thermal collector incidence angle and collector slope.
>
> Does it mean that the solar thermal collector is automated to follow
> the direction of the sun during daytime?
>
> Thank You
>
> Lee Han Kiat
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111212/ef787fd7/attachment-0001.htm>
More information about the TRNSYS-users
mailing list