[TRNSYS-users] convection approach in TRNSYS 17
David BRADLEY
d.bradley at tess-inc.com
Mon Dec 12 08:23:55 PST 2011
Leen,
My understanding is that the big change came between v15 and v16. In
v15, you had Type80 to calculate the internal convection coefficient and
you could couple Type56's surface temperature output to Type80's inputs,
then connect Type80's outputs back to a userdefined Type56 input for the
convection coefficient.
With the release of v16 (and still in v17) the correlation was built
into Type56 directly so a user has only to select "internal calculation"
instead of the usual "constant," "schedule," or "input" for the inside
convection coefficient. The correlation parameters can be adjusted using
the "properties" button in the TRNBuild project window.
Best,
David
On 12/10/2011 16:21, leen peeters wrote:
> Dear all,
> can anyone tell me whether the approach for modelling internal
> convection has been changed from TRNSYS 16 to TRNSYS 17?
> Thanks,
> Leen
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111212/da5716f8/attachment-0001.htm>
More information about the TRNSYS-users
mailing list