[TRNSYS-users] Heating and Hot water - Storage tank
David BRADLEY
d.bradley at tess-inc.com
Fri Apr 15 11:57:36 PDT 2011
Thomas,
If you have access to the TESS Libraries you can use Type534, which
allows you just about as many input/output combinations as you might
want (and then a few more). If you want to continue using Type4, you
will probably have to use a flow mixer and a flow diverter (both modes
of Type11) to mix two of your flows together before they go into the
tank and then separate them once they come back out. You would probably
mix the space and water heating system returns and of course this does
not give you the option of having those returns go into two different
places in the tank.
Best,
David
On 4/15/2011 04:22, Thomas CALMET wrote:
> Hello,
> I am working on self-efficient house, I want to simulate a storage
> tank with 3 inputs and 3 outputs.
> - One system for solar panel (1 input; 1 output)
> - One system for heating system (1 input; 1 output)
> - One system for hot water (1 input; 1 output)
> Actually I use "Type 4", we can had node but they are not output/input.
> Maybe you have a solution.
>
> Thanks anyway.
>
> Thomas
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
--
***************************