[TRNSYS-users] TRNflow notice in theTRNSYs *.lst file
Marion Hiller
hiller at transsolar.com
Mon Apr 18 01:39:17 PDT 2011
Hi,
TRNFlow is integrated in the code of multi-zone building model Type 56
of TRNSYS.
However, in order to activate it you need to buy the an add-on model
separately.
You can simply ignore this message “Message : TRNFLOW multi zone air
flow model integrated”
.
Regards,
Marion
_____
Von: pseudomino at gmx.com [mailto:pseudomino at gmx.com]
Gesendet: Montag, 18. April 2011 09:58
An: TRNSYS-users at cae.wisc.edu
Betreff: [TRNSYS-users] Re : Re: Convection in a simple two storey zone
And what about this message I get in the List file ?
Message : TRNFLOW multi zone air flow model integrated
I use Trnsys17 and as far as I know there is no TRNFLOW installed.
----- Message d'origine -----
De : David BRADLEY
Envoyés : 15.04.11 20:47
À : pseudomino at gmx.com
Objet : Re: [TRNSYS-users] Convection in a simple two storey zone
The Type56 model by itself does not calculate any interzonal air flow
(ie the buoyancy of warmer air is not accounted for). Type56 allows
you to specify coupling airflow between zones. Calculation of the
coupling airflow must be done by integrating Type56's thermal
solution with TRNFlow, COMIS, or Type97 (Contam). The effect you are
seeing is only due to a change between the star-network (simple)
radiation model and the gebhardt factor (detailed) radiation model
now available in Type56.
Kind regards,
David
On 4/14/2011 09:46, pseudomino at gmx.com wrote:
Hi,
In Trnsys 17, I made a very simple test : two little air-nodes
superposed, forming part of a thermal zone.
There is only one windows facing south, at the first floor. I ditn't
made anything else.
Case 1 : Simple radiation model
Quite realistically, the second floor is warmer.
Case 2 : Detailed radiation model
The 2 air-nodes have their temperatures centered around the same
value and very near, except that the first floor has more extreme
temperature variations.
I want to illustrate the hot air elevation by a simple example, but
I'm not sure of the phenomenon that are taken into account.
Thank you !
_______________________________________________ TRNSYS-users
mailing list TRNSYS-users at cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110418/c1f1ef61/attachment.htm>
More information about the TRNSYS-users
mailing list