[TRNSYS-users] Ground Convection coefficient
David BRADLEY
d.bradley at tess-inc.com
Wed Apr 13 12:16:16 PDT 2011
As noted in TRNBuild (where you set the back side convection
coefficient), a value smaller than 0.001 is used to indicate direct
contact between a BOUNDARY wall and a temperature. A large value (such
as 999) is used with other wall categories (ADJACENT, EXTERNAL, etc.) to
indicate good thermal contact.
Best,
David