[TRNSYS-users] digging into trnflow convergence problems

Mariëlle Nuchelmans M.Nuchelmans at chri.nl
Mon Sep 27 00:28:57 PDT 2010


You could try even smaller time-steps, I've models with timestep: 0,03125 (n=5), 0,015625 (n=6) and even 0.0078125 (n=7). It just takes a while before it's finished calculating.

Kind regards,

Mariëlle

Van: frodriguezpc at labein.es [mailto:frodriguezpc at labein.es]
Verzonden: maandag 27 september 2010 9:11
Aan: Mariëlle Nuchelmans
CC: trnsys-users at cae.wisc.edu
Onderwerp: Re: [TRNSYS-users] digging into trnflow convergence problems


Thanks Mariëlle,

I have unsuccessfully tried several timesteps, from 0.0125 of an hour, to 0,1 and even one hour, which are obviously too large. The only way I can get the simulation finished is to input very large limit velues for warning and errors...

I am curious about this thing with interior and exterior temperatures, and was wondering if some conclusions about stack performance could be extracted from this...

Thanks,

Francisco Rodríguez Pérez-Curiel

TECNALIA-Construcción
Parque Tecnológico, Edificio 700. E-48160 Derio (Bizkaia) (SPAIN)
Tel. +34 94 607 33 00,  Fax. +34 94 607 33 49
francisco.rodriguez at tecnalia.com,
www.tecnalia.com

**************** AVISO LEGAL  **************** DISCLAIMER ******************
Este mensaje es personal y confidencial y su uso no autorizado está prohibido legalmente. Si usted no es el destinatario, proceda a borrarlo, sin reenviarlo ni conservarlo.
This message is personal and confidential, unauthorised use is legally prohibited. If you are not the intended recipient, delete it without resending or backing it.
**************************************************************************************

Mariëlle Nuchelmans <M.Nuchelmans at chri.nl>

27/09/2010 08:08

Para

"frodriguezpc at labein.es" <frodriguezpc at labein.es>, "trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>

cc



Asunto

RE: [TRNSYS-users] digging into trnflow convergence problems










Maybe you have already tried it, but you can make your simulation time step smaller (in steps of 1/(2^n))

Kind regards,

Mariëlle

Van: frodriguezpc at labein.es [mailto:frodriguezpc at labein.es]
Verzonden: maandag 27 september 2010 6:24
Aan: trnsys-users at cae.wisc.edu
Onderwerp: [TRNSYS-users] digging into trnflow convergence problems


Dear all:

I am working on a trnflow simulation (an apartment with passive stack exhausts), and having some convergence problems. After looking at it I have found these problems occur whenever the outside temperature gets significantly higher than the interior temperature, as you can see in the attached image. Any suggestion on how to deal with this?

Thanks,

[cid:image001.gif at 01CB5E26.68D7EA60]

Francisco Rodríguez Pérez-Curiel

TECNALIA-Construcción
Parque Tecnológico, Edificio 700. E-48160 Derio (Bizkaia) (SPAIN)
Tel. +34 94 607 33 00,  Fax. +34 94 607 33 49
francisco.rodriguez at tecnalia.com,
www.tecnalia.com

**************** AVISO LEGAL  **************** DISCLAIMER ******************
Este mensaje es personal y confidencial y su uso no autorizado está prohibido legalmente. Si usted no es el destinatario, proceda a borrarlo, sin reenviarlo ni conservarlo.
This message is personal and confidential, unauthorised use is legally prohibited. If you are not the intended recipient, delete it without resending or backing it.
**************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100927/99baa1d9/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 42766 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100927/99baa1d9/attachment-0005.gif>


More information about the TRNSYS-users mailing list