[TRNSYS-users] Type 505 Geothermal Heat Pump Performance File
Matt Duffy
duffy at tess-inc.com
Wed Sep 8 05:58:52 PDT 2010
Aaron,
With this particular heat pump model with the two
data files, the first data file considers the entering liquid conditions, “.\Tess
Models\SampleCatalogData\GeothermalHeatPump\Samp_C.Dat”. The following data
file then considers the inlet air conditions and puts multiplication factors on
the performance as necessary. Not all heat pump manufacturers report data the
same way unfortunately, so if your specific data does not match the format of
the Type, you can either somehow manipulate the data in a spreadsheet. For
example, I had data for a AWHP that was specified in outlet conditions, but I
needed it with inlet conditions, so I calculated (Q=mc(dT)) the inlet
temperature with a curve fit of the data points. Another option iss to modify
the source code for that component, so it conforms to the data, or you could
simply use a Type42 (HVAC à
Conditioning Equipment) which is a
performance map data interpolator in your simulation.
Best regards,
Matt Duffy
----- Original Message -----
From: "Aaron Danenberg" >;ajdanenberg at gmail.com
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100908/ef678888/attachment-0005.htm>
More information about the TRNSYS-users
mailing list