[TRNSYS-users] Question about initial surface temperature of Type557a
Matt Duffy
duffy at tess-inc.com
Wed Sep 8 05:58:25 PDT 2010
Dear Patrick,
I apologize for the delay as I am catching up to all of the emails. That
parameter for Type557, Initial Surface Temperature, along with the next
parameter, Initial thermal gradient, will set the temperature for the
outside the storage volume. Thus, these are important parameters that will
be setting the initial temperature of the soil outside the storage
boundary. As a rule of thumb, we generally set the 30th parameter, Initial
Surface Temperature, to the deep earth temperature while indicating no
temperature gradient for the 31st parameter.
Best regards,
Matt Duffy
----- Original Message -----
From: "xi chen" <climber027 at gmail.com>
Sent: Wed, September 1, 2010 6:47
Subject:[TRNSYS-users] Question about initial surface temperature of Type557a
Dear all:
I would like to ask a question about Type 557a. I wonder if I could
set the 30th parameter, which is "initial surface temperature", to the
undisturbed far deep soil temperature of the location. Actually, I
could not understand the exact function of this "initial surface
temperature.
Yours sincerely,
Patrick