As I mentioned in an earlier post, I was thinking about backflows or
something similar, except that am using large vertical openings for my
windows and interior doors. AFAIK, and I could easily be wrong, they are
supposed to allow air in and out at the same timestep. But the rest of
your explanation makes a lot of sense to me. When I get some time for
that, I will look at some detailed flow outputs and see what is exactly
happening in the stack and windows...
Thanks for your help.
Francisco Rodríguez Pérez-Curiel
TECNALIA-Construcción
Parque Tecnológico, Edificio 700. E-48160 Derio (Bizkaia) (SPAIN)
Tel. +34 94 607 33 00, Fax. +34 94 607 33 49
francisco.rodriguez at tecnalia.com,
www.tecnalia.com
**************** AVISO LEGAL **************** DISCLAIMER
******************
Este mensaje es personal y confidencial y su uso no autorizado está
prohibido legalmente. Si usted no es el destinatario, proceda a borrarlo,
sin reenviarlo ni conservarlo.
This message is personal and confidential, unauthorised use is legally
prohibited. If you are not the intended recipient, delete it without
resending or backing it.
**************************************************************************************
David BRADLEY <d.bradley at tess-inc.com>
27/09/2010 16:21
Para
Mariëlle Nuchelmans <M.Nuchelmans at chri.nl>
cc
"frodriguezpc at labein.es" <frodriguezpc at labein.es>,
"trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>
Asunto
Re: [TRNSYS-users] digging into trnflow convergence problems
Francisco,
I believe that TRNFlow's "horizontal opening" models allow flow only in
one direction at a given time step. I would guess that what happens in
your simulation is that when the zone is hotter than ambient, the building
wants to exhaust air and that when the building is colder than ambient it
doesn't (maybe it even backflows). Since air and go only one direction at
a timestep, the model tries to exhaust air but enough goes out during a
timestep that the building decides that no, it should intake air and tries
that. But it intakes enough air that the building controls decide no, it
should exhaust...and round and round, never converging.
I believe that TRNFlow has something called a "relaxation solver" built
in (controlled from the TRNSYS control cards) that tries to cope with this
problem by first relaxing, then tightening the solution tolerances to come
up with a stable solution. A trick that is possible when using CONTAM
(type97) is to use a short timestep (1 minute max) and delay the zone
temperatures that are being passed to the airflow model but I don't think
that's possible with TRNFlow. There is some research being done on how
best to provide a path up and a path down for airflow in a bulk airflow
model such as CONTAM or TRNFlow (COMIS) but as it is a cooperative
agreement and not funded, there isn't a timeline on it.
Regards,
David
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
__________________________________________________________________________________________________________
Imprime solo lo imprescindible, recuerda tu compromiso con el MEDIO AMBIENTE
Behar beharrezkoa baino ez imprimatu, gogoratu zure INGURUGIROArekiko konpromezua
Before printing think about the ENVIRONMENT
__________________________________________________________________________________________________________
Este mensaje se dirige exclusivamente a su destinatario y puede contener informacion privilegiada o confidencial. Si no es vd. el destinatario indicado, queda notificado de que la utilizacion, divulgacion o copia sin autorizacion esta prohibida en virtud de la legislacion vigente. Si ha recibido este mensaje por error, le rogamos que nos lo comunique inmediatamente por esta misma via y proceda a su destruccion.
Mezu honek eta erantsita dituen agiriek (baldin baditu) isilpeko informazioa izan dezakete. Hori dela eta, hutsegite baten ondorioz jasotzen duenak jakin beza bertan dagoen informazioa ezkutukoa dela eta legeak galarazi egiten duela berori baimenik gabe erabiltzea.
This message is intended exclusively for its addressee and may contain information that is CONFIDENTIAL and protected by professional privilege. If you are not the intended recipient you are hereby notified that any dissemination, copy or disclosure of this communication is strictly prohibited by law. If this message has been received in error, please immediately notify us via e-mail and delete it.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100927/852ee144/attachment-0001.htm>
More information about the TRNSYS-users
mailing list