[TRNSYS-users] Psychrometrics error
Fred Betz
fbetz at aeieng.com
Fri Oct 22 07:00:48 PDT 2010
Marie-esther,
This error is created because the conditions your cooling tower is experiencing are outside the psychrometric chart. In this case the air is supersaturated.
Use Type33 to correct any inconsistencies in the weather file before passing the data on to the cooling tower.
Type 33 is located under: Physical Phenomena/Thermodynamic Properties/Psychrometrics
Fred
Fred Betz PhD., LEED AP
Sustainable Systems Analyst
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI 53719
P: 608.236.1175 | F: 608.238.2614
fbetz at aeieng.com<mailto:fbetz at aeieng.com> | www.aeieng.com<http://www.aeieng.com/>
From: marie-esther guillerm [mailto:marie-esther2b at hotmail.fr]
Sent: Friday, October 22, 2010 8:08 AM
To: trnsys-users at cae.wisc.edu
Subject: [TRNSYS-users] (no subject)
Hi,
I'm modelling a absorption cycle with type 107, type 51b, type 1b , type 60c and type 56a and I have a problem with the colling tower ;
actually the error message is : problem with the features of moist air the utility routine PSYCHOMETRICS, which calculates the thermodynamic properties of moist air, has been called with a wet bulb temperature above the maximum wet bulb temperature for the given pressure.
I tried to make calculations but nothing is working.
thank you very much to heping me if you can
Marie-esther
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101022/308df3cb/attachment-0005.htm>
More information about the TRNSYS-users
mailing list