[TRNSYS-users] Results for QSEN (NTYPES 2) do not appear after thesimulation.
Kersken, Matthias
Matthias.Kersken at ibp.fraunhofer.de
Thu Oct 14 00:06:31 PDT 2010
Dear Ganapathy!
Qsens does only apply if You're using the ideal heating Type within the building type, not if You're realizing the heating through a gain or an active layer.
Heating is defined negative in Qsens!!!
So be sure that the problem isn't that Your online-plotter is only showing the positive values.
With kind regards,
Matthias Kersken
---
Dipl.-Ing. Matthias Kersken
Wissenschaftlicher Mitarbeiter / Abteilung Energiesysteme
Fraunhofer-Institut für Bauphysik
Institutsteil Holzkirchen
Fraunhoferstraße 10
83626 Valley
eMail: Matthias.Kersken at ibp.fraunhofer.de
Telefon 08024 / 643-204
Telefax 08024 / 643-366
www.ibp.fraunhofer.de <http://www.ibp.fraunhofer.de/>
Dipl.-Ing. Matthias Kersken
Research Associate / Department Energy Systems
Fraunhofer Institute for Building Physics
Branch Holzkirchen
Fraunhoferstraße 10
D-83626 Valley
eMail: <mailto:Matthias.Kersken at ibp.fraunhofer.de> Matthias.Kersken at ibp.fraunhofer.de
Phone +49 8024 / 643-204
Fax +49 8024 / 643-366
<http://www.ibp.fraunhofer.de/> www.ibp.fraunhofer.de
---
_____
Von: GANAPATHY.IYER at Thermaxindia.com [mailto:GANAPATHY.IYER at Thermaxindia.com]
Gesendet: Mittwoch, 13. Oktober 2010 08:18
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Results for QSEN (NTYPES 2) do not appear after thesimulation.
Hi all,
I am trying to calculate the sensible and latent heat load in a simple building. But whenever I enable the outputs NTYPE2 i.e. QSEN for any airnodes, the result is always 0.
I used the Sun-Space example where I enabled the output for QSEN, but when I print the results, it always shows this value to be 0.
Has anyone used this successfully?
Some examples will be helpful
Regards
Ganapathy Iyer
THERMAX PUNE
================================================================================================================
DISCLAIMER :
The information in this email is confidential and may be legally
privileged.It is intended solely for the addressee. Access to this email by anyone else is unauthorized.If you are not the intended recipient, any disclosure, copying, distribution or any action taken or omitted to be taken in reliance on it, is prohibited and may be unlawful. When addressed to our clients any opinions or advice contained in this email are subject to the terms and conditions.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101014/58b2df0f/attachment-0001.htm>
More information about the TRNSYS-users
mailing list